Insulation touches underside of roof in home with no soffit or soffit venting.

I performed an assessment for a recent home buyer and the home inspector they hired when they purchased the home said the fiberglass insulation that is touching the roof where the roof slope meets the exterior wall may cause condensation issues and needs to be pulled away from the underside of the roof. The house was originally designed and constructed with no soffit, so there are no soffit vents. The top plate of the exterior wall meets the lower slope of the roof. To properly insulate the attic, I would think you would want the attic insulation covering the top plate. To ensure proper levels of insulation above the top plate, the insulation will be in contact with the lower area of roof slope. Since the attic does not have a soffit, I would think there is no issue with the fiberglass batt insulation being in contact with the underside of the sheathing? Since there is no soffit in the original design of the house the insulation does not limit the airflow ventilating the roof. The house does have gable and ridge vents for proper attic ventilation.

Is there an issue with fiberglass batts installed on the attic flat touching the underside of the lower slope of the roof if there is no soffit venting? 

Views: 518

Reply to This

Replies to This Discussion

Soffit vents can be used for intake, but they are not the only means of intake. If you have a vented roof and already have adequate intake venting, you don't need to add more. Additionally, not all roofs need to be vented - there are "hot roof" designs where the rafter bays are insulated and sealed up. For more inquiry on ventilation contact to HVAC services experts at White Mechanical to get all your answers.

I have inspected attics where some but not all of the 4x8 roof deck has been replaced.  I noted large amounts of black mold on deck panels that were not replaced.  On those replaced,  I noted black streaks or stains from the nail points penetrating the deck,  When the ambient temperature drops below the dew point inside the attic,  this is the first place you will get condensation.  

The amount of moisture in the attic and the dew point compared to the ambient temperature is a simple way to judge the balance of the various factors that contribute to damage from inadequate ventilation in an existing attic.

Too many people attribute ventilation benefits to attic ventilation that are myths.  The purpose of attic ventilation is to remove heat and moisture from the attic space above the insulation to avoid ice dams and condensation.  That is it.

Home inspectors have no training in many things we deal with and balk at anything non-standard or which they have not observed.

"Too many people attribute ventilation benefits to attic ventilation that are myths. " YES!

I've gone round and round with roofers who are almost religious with their belief in venting as a cure for all evils. 

The real issue is the connections between the attic and living space and the moisture that moves between them. I've actually seen attics with nominally zero venting be made much worse (moisture-wise) by adding venting - usually done to fix an ice dam problem.

RSS

Forum Discussions

Water heater ventilation question

Started by Luis Hernandez in General Forum. Last reply by Bradford E. White 1 hour ago. 11 Replies

Exterior green cladding

Started by Luis Hernandez in General Forum. Last reply by Dennis Heidner on Friday. 3 Replies

Faces & Places of HPC19

Started by Diane Chojnowski in General Forum Apr 5. 0 Replies

high rise humidity

Started by Steve Nations in HVAC. Last reply by Dennis Heidner Apr 3. 7 Replies

Follow the action at #HPC19

Started by Diane Chojnowski in General Forum Apr 2. 0 Replies

Unvented Roof Assembly

Started by Patrick Michaelyan in General Forum. Last reply by Wallacebastien Mar 30. 6 Replies

Technology and Customer Service

Started by Kelly Caplenas in General Forum. Last reply by Franco Oyuela Mar 25. 1 Reply

Latest Activity

Bradford E. White replied to Luis Hernandez's discussion Water heater ventilation question
"This has been a topic of discussion for 20 years now. It is true that appliance manufacturers often…"
1 hour ago
Wallacebastien replied to Rob Madden's discussion Determining Duct Leakage based solely on blower door and pressure pan testing
"Doors can sometimes not be tight, so you should watch out for it carefully. For example this can be…"
2 hours ago
John White posted a blog post

Air Conditioner Not Blowing Cold Air

Air conditioners must be tuned to experience better performance and enjoy the pollution-free cold…See More
5 hours ago
Franco Oyuela replied to Luis Hernandez's discussion Water heater ventilation question
"Common Water Heater Problems: Water Leaking From the TopWater Leaking From the BottomReader…"
14 hours ago
Jill Lindman posted events
17 hours ago
dale garren replied to Luis Hernandez's discussion Water heater ventilation question
"make sure the gas modulator / controller valve has propane orifices (jets), if it came from factory…"
17 hours ago
Home Energy Magazine posted a blog post
17 hours ago
Ken Summers replied to Luis Hernandez's discussion Water heater ventilation question
"I agree with Sean to bring in a technician that can do some diagnostics on it.  I would also…"
18 hours ago