Does anyone have any knowledge of installing fiberglass in the walls and foam insulating the attic to bring Air Handler into conditioned space. To reduce the condensation on air Handlers.
Building in Hot Humid Climate.

Views: 241

Reply to This

Replies to This Discussion

Short answer: spray about an inch to the roof deck and gable walls. Take specific note of any fire rated surfaces and know the foam will potentially lessen that rating.

Long answer is that you should think hard about air, ventilation and the requirements of envelope (cladding, moisture barrier, air barrier, thermal barrier. Insulating the roof deck will "hot deck" the shingles and shorten their life. Typically you would back vent the roof deck with a 1 inch airspace that connects the soffits to the ridge vent. This can be done in many ways, commonly with vent chutes. If that is done, you have the first function of cladding completed. Now what you install on the inside of the air space must be a moisture, air and thermal barrier. Spray foam is a good source of all of these. Something like icynene, polyurethane foam or polystyrene foam, give you an air barrier, thermal barrier and various moisture "perm" rating. Polystyrene can be a moisture stopper, which can be a problem. Next, we commonly add fiberglass to get the r-value up to the code or desired amount. Fiberglass is fine, just understand that you don't want the kraft paper to be on the inside of the assembly AND acting as the moisture barrier. Commonly they have perforated face insulation to allow "draining". 

I would point you to insulating the cooling equipment and duct before i would condition the attic. If you can insulate the cooling equipment to get the surface temperature above the dew point, you will probably mitigate the energy loss and moisture issues. Changing the attic has plenum rating implications, is the attic air part of the conditioned zone or inactive conditioned space? I think the fix of insulating the equipment is a better answer to the problem.  Conditioning the attic could have other benefits and other problems that don't exist yet. 

Good point about 'fire rating'...  Depending on attic configuration, exposed spray foam insulation must either have a thermal or ignition barrier (typically an intumescent coating), although a few foam products are rated as such.  However, I wouldn't be too concerned with impact on shingle life.

When the residential codes first allowed unvented attics (2006 IRC), some shingle manufacturers voided warranty if roof deck wasn't ventilated. However, subsequent research demonstrated that spray foam on underside of roof deck had less impact on shingle temperature than the color of the shingle! I'd be interested in knowing if any shingle manufacturers are still making an issue of this.

It's worth pointing out that the R-value of the foam must meet IRC Section R806.5 requirements. For example, IECC Climate Zones 4A & 4B must have at least R-15 air impermeable insulation on the roof deck. I believe Noah is in SE Texas (CZ-2A), in which case only R-5 air impermeable insulation is required.  Also, just to clarify, it typically takes at least 3.5 inches of open cell foam to qualify as an air barrier. An inch of closed cell foam may or may not be an air barrier depending on the specific product.

Lastly, constructing a hybrid assembly (e.g., foam + fiberglass on roof deck) is not straightforward. In particular, the fiberglass must be held in good contact with the foam without compression. Here's a discussion in Home Performance Forum archives on that topic: https://homeenergypros.org/hpforum-archive#/discussion/3667

Concur with Mick Lane's ending, fully insulating attic can have unattended consequences, and to go further, that can reduce shingle life, create mold, chemical contamination (bad foam job), reduce air flow creating 'sick house' syndrome, or even destroy roof structure.  Working w firemen they don't appreciate foamed houses smoke developed is a big problem.

Insulate the equipment and ducts if at all possible, I suggest ROCK WOOL, it is resistant to moisture damage and is stiff enough to maintain shape with relatively little attachment.

While in the attic, think about more ceiling insulation, enlarging or installing gable end vents.  I'd aim for 18 inches of insulation & 3 to 4 sf vent in ea gable end.  If DIY aim higher on insulation, it's real hard to fully fluff it & deeper it is more likely workers will manage to get some of it back in place when they are finished fixing wiring, lights, etc

Does the roof have a vented soffit and ridge vent?

Honestly research shows its best to create a sealed conditioned attic buy putting the insulation on the outside of the roof deck. So, continuous on the roof osb, w/ shingles or metal roofing on top insulation. 

That said we have a builder that puts 1" rigid foam in the rafter space (1" deep) to allow a vented roof deck. Then flash foam 1" closed cell foam, then net and blow the rest of the 2' rafters. Then drywall. He hasn't had any issues yet and no complaints.

On houses with trusses we have done R38 with closed cell foam. We also then conditioned the space with a dedicated supply and return. This seemed to me to be a waste of energy. I would have recommended just spray foaming the ceiling on the attic side 2". Closed Cell foam all duct work. then blown fiberglass to around an R60.

RSS

Forum

Air Sealing Manufactured Home

Started by John Lile in General Forum. Last reply by Darin Pleines 19 hours ago. 10 Replies

Solar ROI Calculator

Started by Kyle Baker in General Forum 21 hours ago. 0 Replies

Does Radiant Barrier Still Work 10 Years Later?

Started by Green Energy of San Antonio in General Forum. Last reply by Sean Wiens on Friday. 2 Replies

Best Exhaust Fans - your opinion?

Started by Eric Miller in General Forum. Last reply by Russell Pope on Thursday. 3 Replies

October 2 is Energy Efficiency Day

Started by Diane Chojnowski in General Forum on Thursday. 0 Replies

ERV recommendations

Started by David Wentling in General Forum. Last reply by Luke Langhals on Wednesday. 13 Replies

Baffles without soffit vents?

Started by Haley Keegan in Best Practices. Last reply by Eric Kjelshus Sep 9. 14 Replies

Off-Grid Applications?

Started by Kyle Baker in General Forum. Last reply by Paul Scheckel Sep 5. 2 Replies

Latest Activity

Profile IconKevin M Dugan, Daniel Haydon and Patty Hoffman joined Home Energy Pros Forum
18 hours ago
Darin Pleines replied to John Lile's discussion Air Sealing Manufactured Home
"In illinois WAP program we seal the belly material and lightly dense pack the cavity with loose…"
19 hours ago
Brian Robinson replied to John Lile's discussion Air Sealing Manufactured Home
"The first place to look when working on trailers / manufactured home is the…"
21 hours ago
tedkidd replied to John Lile's discussion Air Sealing Manufactured Home
"Spray foam the road barrier."
21 hours ago
Tom Wilson replied to John Lile's discussion Air Sealing Manufactured Home
"The good news is the linoleum IS the air/vapor barrier and unless it is put under 50 Pa negative…"
21 hours ago
Kyle Baker posted a discussion

Solar ROI Calculator

How do you know when you get a payback on installing a solar system? What ROI have you received…See More
21 hours ago
Robin Henry replied to John Lile's discussion Air Sealing Manufactured Home
"Sorry if I'm preaching to the choir but careful sealing up mobiles too tightly as they are…"
22 hours ago
Tom Wilson replied to John Lile's discussion Air Sealing Manufactured Home
"Typo corrections: This is the classic problem folks have been wrestling with forever with…"
22 hours ago
Ed Minch replied to John Lile's discussion Air Sealing Manufactured Home
"Many of the WAP programs have written extensively on sealing of these guys.  West Virginia in…"
22 hours ago
Tom Wilson replied to John Lile's discussion Air Sealing Manufactured Home
"This is the classic problem folks have been wrestling with forever with manufactured…"
22 hours ago
Rich Mialki Jr replied to John Lile's discussion Air Sealing Manufactured Home
"Does this really matter much?  Think of what the blower door is doing as opposed to natural…"
22 hours ago
Emily Ambrose's blog post was featured
yesterday

© 2019   Created by Building Performance Association   Powered by

Badges  |  Report an Issue  |  Terms of Service