Every single time I do an audit where the house has I joists instead of regular floor joists I see this issue. Either the insulation batts are installed with no tiger teeth at all and the batt is resting on the bottom of the joist or the installers DID use tiger teeth but those are in turn resting on the bottom of the I joist with the insulation on top. Even though I joists are still 16" OC the actual width between the wood members is greater than with typical floor joists. Tiger teeth are 16" wide and aren't long enough to properly support anything and in turn rest on the bottom of the I joist. Here in Colorado R19 is pretty standard and typical I joist heights are either 10 or 12". This results in an approximate 4 or 6" airgap above the batt and extremely ineffective or totally pointless insulation. What I'm getting at is what do most professionals recommend to remedy this? If tiger teeth aren't the right width then are people typically using twine and staples to get the R19 flush with the floor? Otherwise are people getting an additional R13 or 19 batt to fill the entire cavity and using twine and staples on the bottom of the joist to secure them in place? Does somebody manufacture oversized tiger teeth for this type of application that I'm unaware of?

Any input is appreciated as I see this all too often.

Views: 439

Reply to This

Replies to This Discussion

In order to make the air gap above the insulation work effectively, the framing must be airtight at the joist end as well as have a continuous air barrier, and preferably some continuous insulation below the joists. You are essentially creating a very tiny encapsulated crawlspace.

I believe this method would be the most cost-effective if the job conditions are reasonable.

@Stanley, your strategy for holding batts against the subfloor is interesting. Much better than wire insulation compressors! That 1/2 EPS you're using is relatively inexpensive and since you're not going for full encapsulation, it's not very time consuming. Also, your method would not be as impacted by interfering pipes and ducts since you're not going for an air barrier.

Regarding facing on batts... Virtually every type of batt is available without kraft facings, although a given SKU may not be stocked at a given location depending on demand. If I'm not mistaken, the IRC only requires vapor retarders in wall assemblies and only then in CZ 5-8 and Marine 4.

The issue with fire codes is that kraft paper facings (and even some foil facings on batts) do not meet the 'flame spread' and/or 'smoke developed' requirements of the IRC. In particular, Section R302.10.1 requires insulation facings to meet these requirements unless concealed and in contact with drywall or other surface separating cavities from living space.

I think the kraft facing would meet the requirements of "concealed" and "in contact" with "other surface" if the batts are supported to maintain contact. Not if there's a 5" air gap above them! Another reason to do something about these legacy installations.

RSS

Forum

How many BTU required to heat air

Started by Sean Wiens in HVAC. Last reply by Sean Wiens 18 hours ago. 22 Replies

Derating / Rating Old Insulation

Started by Haley Keegan in Weatherization. Last reply by Haley Keegan on Thursday. 4 Replies

Green Button Connect

Started by Rob Buchanan in General Forum. Last reply by Steve Schmidt Dec 9. 1 Reply

Installing High Efficiency Equipment....?

Started by Horace Douglas Hunt, Jr. in General Forum. Last reply by Horace Douglas Hunt, Jr. Dec 5. 5 Replies

Solar Panel Size?

Started by Kyle Baker in Best Practices Dec 2. 0 Replies

ACEEE 2019 State Energy Efficiency Scorecard

Started by Diane Chojnowski in General Forum. Last reply by Horace Douglas Hunt, Jr. Nov 29. 1 Reply

HVAC Contractors Expand Their Role in Home Performance

Started by Diane Chojnowski in General Forum. Last reply by Horace Douglas Hunt, Jr. Nov 29. 1 Reply

Latest Activity

Larry Weingarten posted a blog post

Clues a Water Heater Gives You

If only we would listen, water heaters would have a lot to tell…See More
5 hours ago
Profile IconJon R, Gavin Lyman and Wyatt Catron joined Home Energy Pros Forum
5 hours ago
Bob Deavson's blog post was featured

HCFC Refrigerant Ban: Everything Contractors Need to Know

As of January 1, 2020, HCFC refrigerant use will be severely limited in the United States. If you…See More
5 hours ago
Sean Wiens replied to Sean Wiens's discussion How many BTU required to heat air
"Thanks David - I knew HPWH definition, just was not sure why you wanted (and still don't) its…"
18 hours ago
David Butler replied to Sean Wiens's discussion How many BTU required to heat air
"The abbreviation HPWH refers to a domestic water heater, not an air-to-water space conditioning…"
23 hours ago
Sean Wiens replied to Sean Wiens's discussion How many BTU required to heat air
"Also one last point on the final benefit.  Although we do not have time of day energy rates,…"
yesterday
Sean Wiens replied to Sean Wiens's discussion How many BTU required to heat air
"You rest assured on one point - if I go ahead with hybrid, I will definitely be reporting on its…"
yesterday
Sean Wiens replied to Sean Wiens's discussion How many BTU required to heat air
"Are you meaning the space conditioning heat pump or domestic hot water on your bullet 1?  How…"
yesterday
Sean Wiens replied to Sean Wiens's discussion How many BTU required to heat air
"Thanks for follow up David, Valid comments.  The facet flow is high, I was basing on current…"
yesterday
Brad Cook replied to Sean Wiens's discussion How many BTU required to heat air
"I don't dive into numbers as well as David does because if you do analyze a situation only by…"
yesterday
David Butler replied to Sean Wiens's discussion How many BTU required to heat air
"Your consumption numbers seem rather high if not unrealistic, especially sink draws, which add up…"
yesterday
David Butler replied to Sean Wiens's discussion How many BTU required to heat air
"Sean wrote: "The only question is what will be the cost for the extra 4000K of heating needed…"
yesterday

© 2019   Created by Building Performance Association   Powered by

Badges  |  Report an Issue  |  Terms of Service