For those conducting energy audits and developing retrofit work scopes on low-rise residential, please share your experiences in this thread.  Successful methods, pitfalls and complete disasters are all fair game for sharing with the group.

Since there are distinct difference between high-rise and low-rise strategies, let's keep our discussion here only on low-rise. High-rise stories go here.




Views: 569

Replies to This Discussion

What method are folks using for infiltration testing adjacent apartments?  I had to hire two other auditors to measure air leakage in a middle unit.  Is there a better way?

Do you want to QUANTIFY" flow, or just assess it?? If you need actual flow numbers, well, that's really tough. The only way I know to do that is with multiple fans and guarded blower door testing. (Sounds like that's just what you are doing.). That only makes sense if you need a number really badly. And in anything other than townhomes, it gets pretty complicated pretty fast.


But you CAN set up a blower door in one unit with an Energy Conservatory APT unit, throw tubes under the doors of adjacent apartments, and do a multipoint test. That will at least show you the magnitude of cross-talk. (When the tested unit is at -50 Pa, Unit B is pulled to -6 Pa, Unit C is pulled to -8 Pa, and so on.) Get in touch with me off line and we can get into details...

Anybody using blower doors on low-rise multifamily, or have views about it?
Two fans is all you really need, even if you want specific numbers. But you will have to move one around quite a bit, especially when you start talking about multi-level buildings.

For a townhouse, you equalize adjacent units to the outdoors. To measure the leakage across one shared wall, equalize the pressure across it with the second fan. A simple subtraction will give you the leakage across that wall. Repeat that step as needed for adjacent units, as well as those above and below. Andrew, you brought in two other people, that obviously makes things a tad easier and faster, as you won't need to move that second fan around as much. Though you don't actually need extra auditors, just their equipment (or some more of your own).

Retrotec does offer an online course on large building testing. I'd be happy to talk more about it if you're interested. Send me a direct message, or email

I have had several discussion with several different knowledgeable people about this. I am just not sure that it's true that you can test your way around a middle-of-building unit with just two fans; at least not in wood-frame buildings. I am just not confident that there would be NO communication across corners and through floor assemblies.

Think about the center unit in an 18-unit building with three stories and three apartments on each side of a double-loaded hall. I don't know of anyone that has tested the center unit with a blower door simultaneously in every single unit on one side of the building AND with a fan de-pressurizing the hall. And then gone back with just two blower doors and tested their way around the center unit, one surface at a time. I think someone would have to do that at least a few times, and confirm that you get equivalent results, to be confident that you were on solid ground.

But I do know (because I've done it) that you CAN put a blower door in one window of our hypothetical center unit, and see the pressure change in units that are "in contact" with the target unit only at the corners. That tells me that the communication and leak paths are far more complicated than is obvious. It leads me to suspect that only simultaneous testing of every surface will get accurate results.


But then again, the other question is -- how badly do you need to know? In new construction, it's generally accepted that you just get each unit very, very tight. Don't worry about where the air comes from, just stop it. In existing units, never promise that you'll get the unit tight enough to stop that cigarette smoke migration, because you almost certainly won't succeed. And, if you want to save energy in existing buildings, what are you doing mucking around with surfaces that have no delta-t?


Damn, we still have a lot to learn....

You bring up and interesting discussion Don, and I suspect you're right, there could certainly be some communication across corners ect...


However, I would suggest in your example that the number of fans can still be reduced to a manageable number, say 3. On both the first and third floor, install a fan to de-pressurize the hall, open the doors to each unit, and you've now neutralized the leakage between the center unit and the floor above and below. Obviously the possible test scenarios and test setups is nearly endless depending on the exact building configuration. And yes, you ask a great question... and yes, we still have much to learn.

I've been doing some multifamily testing during the last few months and been looking at it from all these different angles.  In one building we did some testing of a middle unit (double loaded corridor) on the second floor.  We first did at total leakage test - 1 blower door, and then did a guarded test depressurizing all adjacent units and the hallway.  The results were very similar - less than 100 CFM difference.  My best guess is that the interstitial spaces are pretty well connected throughout the building.  Of course this is just anecdotal, but led me to test total leakage for all the units. 


I agree completely with Don that you don't have to worry about where the air comes from, just stop it.  As far as I'm concerned it's too complicated, too uncertain, and too expensive to test anything other than total leakage in this type of situation - especially new construction.  I just don't see the down side to doing the total leakage test and keeping my life simple.  Does anyone else?


For existing buildings, you have to consider a whole building blower door to get at the leakage to common areas and non-living spaces which can have a large impact on energy usage.  Again, I agree with Don - no need to muck around with surfaces that have no delta-t.  I have much less experience with existing construction however.


This is a great discussion and I look forward to hear and learning more from you more experienced folks out there.

Tom Holmes (AEA New York) appears not to be a member of this group, so he isn't here to brag about some VERY illustrative work he's done in New York state. He reported on it at ACI in San Francisco.


He actually did all the work needed to go through an existing eight-unit "garden" style building both ways; testing all eight units individually, then doing guarded tests on all units. His numbers showed that testing units one at a time gave CFM50 reading that were all too high. The error ranged from 15 to 30 percent, in units with "pre" infiltration values from about 1,500 to 2.300 CFM50. 


So that indicates (the same as the little bit of experimentation I've been able to do) that you probably do over-state the leakiness of units, by a significant amount, when testing them solo. Test like that would not be all that useful -- It wouldn't be hard to fool yourself into thinking there was a lot more room for improvement than the building actually offers. 


The one thing I don't know -- he reported also "post" blower door numbers, but only those coming from guarded blower door tests. I should ask him whether he repeated his individual unit tests after they did their air sealing. If the error stays about the same, then it might not matter so much. I doubt that it would though--If all the air sealing were focused on the thermal shell (not affecting the defective air barrier between units) then then the unit-to-unit leakage would be a much larger proportion of the total leakage, when testing just one unit at a time. That would fool you into believing you hadn't changed the building much -- even though the thermal shell could be MUCH tighter, and the post-sealing energy use could then drop significantly.


You might also fool yourself into thinking that the unit didn't need supplemental ventilation, when it might in fact be pretty darn tight. Tom got a one-bedroom unit down close to 600 CFM50 to outside -- pretty darn tight to depend solely on infiltration for a ventilation/moisture strategy!

Thanks for passing this information on Don.  Definitely different results than I got.  I was testing a 4 story, 66 unit double-loaded corridor building, so construction type may be the difference or just construction technique. I guess my conclusion is that we can't say for sure whether testing 1 unit at a time will always significantly overstate outdoor air infiltration.


For new construction, we only see buildings with mechanical ventilation, but I will definitely heed the warning that one could be fooled into not needing a ventilation strategy in an existing building.


The second phase of the building I tested is being built right now, and I will have access to test as much as I want before it is occupied.  Unfortunately, I'm limited by having to do any extra testing on a volunteer basis.  I wonder if there might be a source of funding for this testing out there somewhere.

So, the blower door class IS going to happen -- Thursday through noon Saturday, August 11 through 13, in Aurora, IL. The logistics of offering this as a Short Course got a little complicated, so it's being offered as a separate event by Insight Property Services. I think we will be able to include a test run of one of the "automated" testing platforms, where all the blower doors needed (8 to 12 or so) are all linked and operated from a central control station driven by a laptop. Get in touch with me for more info -- I should have all the details in a day or two.

It looks like Wisconsin is going to wade into doing blower door testing on low-rise MF buildings. We did a training last week on auditing small MFBs and ran a two-fan test on a 12 unit building. That demonstrated that the building was about as leaky (per ft2 of shell) as a single-family home where air sealing would be a good strategy.


The state office is going to "encourage" weatherization agencies to test 5-24 unit buildings "whenever possible." This could get interesting...


Latest Activity

Profile IconAdam Fiscsu, Jacob Hooper, Jaime Horne and 1 more joined Home Energy Pros Forum
2 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)

BPI Jobs Pages: 36 Openings in 17 States

Are you a BPI Certified Professional looking for a job in home performance or weatherization? Look…See More
5 hours ago
Fred Schreiber replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"$500 each.  Comes with DM2, umbilical cords and bag.  If you want a picture, let me know."
22 hours ago
Gary Hall posted a photo
Diane Deyerler posted a discussion

2018 Energy OutWest Conference

Still time to register. Don't miss out on this premier event!…See More
Profile IconJoe Vragolic, Natalie Sheely and A Plus Mold joined Home Energy Pros Forum
Efficiency First California's blog post was featured
Efficiency First California posted a blog post
Thomas Price commented on Bruce Sullivan's blog post Don’t Repair, Replace! Bring Zero Energy Homes to Those Who Need them Most
"That's an interesting perspective but it begs certain questions.  Yes, if we were to…"
Kevin Jacks replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I sent you a friend request so we can communicate directly."
Arn McIntyre replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Within the US and I would need to add shipping cost.  Where are you located?"
Dennis Heidner replied to Bruce Navin's discussion LED's interfering with Garage Door Openers
"I posted an explanation to Liam weeks ago.   Since different LED manufacturers may use…"
Armstrong SMith replied to Bruce Navin's discussion LED's interfering with Garage Door Openers
"No one replied! ."
Kevin Jacks replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Are you willing to ship?"
Kevin Jacks joined allen p tanner's group

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Walter Ahlgrim replied to Pamela Brown's discussion Condensation on an interior wall of a detached garage.
"Do not be fooled it is very common problem for cast iron wood working equipment to sweat and rust…"
David Eakin commented on Bruce Sullivan's blog post Solving Energy Poverty: Energy Efficient Homes for Those Who Need Them Most
"Most all residential buildings are built with a 50-year life cycle. If the building stock in…"
Profile IconTaylor Joseph Mckay and Karin Haerter joined Home Energy Pros Forum
Arn McIntyre replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Dave I am selling everything as one package"
Dave Ransom replied to Arn McIntyre's discussion Retrotec Door Fan For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"What's your price for the DM2?"


  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service