Hi All

Wanted to get the opinion of an expert.

Attached is a photo of a customer's window.... as you can see there is a large cold spot above the window... Here's my opinion..am I right?

The large horizontal cold spot is thermal bridging from the double 2x6 or 8 top plate.

DO you agree?  The customer's pain was condensation on the windows.  WIndows were well installed with minimum leakage. The house was very tight, which I believe is the problem..not this.

Tags: ir, windows

Views: 746

Replies to This Discussion

Master shows!

John, Thanks for the review in Home Energy 101.  Sometimes, as auditors, we get so enamored with the technology, we forget the basics.  Comments like this, keep my feet firmly on the ground, and improved my audit results.

 

 

Matthew, this is not thermal bridging or else it would look like the wall studs and the window header. This is a result of running the blower door in a tight house where air coming in at the soffitt vents is pulled into the building through penetrations in the drywall. Take the same shot before the blower door has been run and it will look a lot more normal.

This is not thermal bridging and it has nothing to do with the blower door.  This is the ceiling plane meeting the wall plane, and this is thin insulation at this area combined with possibley a slight breeze blowing or convection causing cold air to ride up under the first couple of inches of attic insulation.  The very dark spot every 2 feet corresponds to the roof trusses/rafters and the week insulation adjacent to them. In the mid-Atlantic we are required to install hurricane clips - metal clips that hold the trusses/rafter down to the top plates.  We see the conducted cold from the metal as a dark spot every 2 feet even if it is not connected between with a dark area.  The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates.

Ed Minch

Slight Breeze?  He said the bower door was running. 

Chad

As I said:

"The blower door would have caused the cold air to come down the wall/ceiling joint into the wall - but this is not the case, and thermal bridging would have made all the studs show as much as the top plates."

There is no connection of this area to the blower door through the attic.  The only possible connection is from the bottom of the wall at the baseboard or through receptacles, etc in the wall, then up through the wall to the open wall/ceiling joint where the cold areas are.  If this were happening, the cold would extend down as "icy fingers" into the wall below, but it is not.

Ed

RSS

Discussion Forum

Having some fun with our cameras

Started by Mike Pagozalski. Last reply by Mike Pagozalski Jul 31, 2017. 2 Replies

Expert Eye Needed

Started by Matthew P. Last reply by Ed Minch Nov 15, 2014. 17 Replies

Google Thermal View?

Started by Joshua Knittel. Last reply by tedkidd Jun 1, 2013. 4 Replies

Infrared Image - What is it?

Started by Fluke Thermal Imaging. Last reply by Dale Sherman Apr 26, 2012. 6 Replies

Latest Activity

Profile IconLauren Asplen and Danny Gough joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
6 hours ago
Franco Oyuela commented on John White's blog post What to Expect from a New HVAC Unit Installation Cost
"Is strongly advise against attempting to install any complex home comfort equipment on your own.…"
7 hours ago
CEE posted a blog post
8 hours ago
Lindsay Bachman liked David Keefe's video
8 hours ago
Julie Saporito's blog post was featured
9 hours ago
John C. Semmelhack liked Diane Chojnowski's discussion Everything you need to know about California's new solar roof mandate
10 hours ago
Profile IconJohn Walter and Eric Rabesa joined Home Energy Pros Forum
23 hours ago
William Collins posted a video

The Foam Sealants Kit " Bead or Spray"

Now you can apply foam sealant as a " bead " or a " spray " with the Foam Sealants Kit. When using a 16lb Canister of Black Sealant you can easily go from us...
yesterday
Profile IconSean Wiens and Armando Cobo joined Don Fugler's group
Thumbnail

Kitchen Ventilation

In many homes, cooking is the largest indoor source of air pollutants. Exposures can be higher in…See More
yesterday
Julie Saporito posted a blog post
yesterday
Brennan Less replied to Linda Wigington's discussion Good Eating with Reduced Cooking Emissions in the group Kitchen Ventilation
"Cook outside, as much as you can, and close your doors/windows while you do it ;) "
yesterday
Ethan Foley joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
yesterday
Shane S posted a photo
yesterday
Al Tibbs posted photos
Wednesday
Al Tibbs commented on Eric Aune's photo
Thumbnail

IMG00173-20100805-1030

"Always remind customer to make sure to mark out location of piping before covering!! The infrared…"
Wednesday
Al Tibbs commented on Eric Aune's photo
Wednesday
Joe is now a member of Home Energy Pros Forum
Wednesday
Liam Smith replied to Silas Inman's discussion Best Energy Myths
"Yes incandescent bulb are very heat productive. Instead of that use LED bulb which are energy…"
Wednesday
Kelly Vaughn's blog post was featured

How Cities Can Ensure Better Rentals for Everyone

By Alisa PetersenWhile much of RMI’s research and analysis on home energy performance has focused…See More
Wednesday
Brett Little's event was featured

Resilient Design in an Age of Climate Change - Free CE Webinar at Webinar Online

May 30, 2018 from 12pm to 1:15pm
A changing climate, sea level rise, drought, and a wide range of stresses in the world are…See More
Wednesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service