You said take wet bulb at unit not in the house am i right or did i miss understand the formula

Views: 5040

Replies to This Discussion

You take the Indoor Wet Bulb and the Outdoor Temp

Thank You
Can you explain this superheat formula like way do we times it by 3 and mines 80 and mines cond enterning ambient,.

Thanks Mike O

Target SH = [(3 x indoor wb) - 80 - ambient] / 2 (°F)

Usually, if you are charging an ac , the manufacturer gives you a superheat range they want the equipment to operate at  (usually 6-8 degrees)   The higher the wetbulb the more capacity/cooling will be diverted to removing moisture/humidity.  

The super heat will show if the TXV is operating correctly as well.  It is a great tool for diagnosis.  If you are an HVAC dealer, your equipment manufacturer rep will be happy to explain it all to you.

All the various scenarios are to involved to train someone here.  

Yikes -- Folks help me out. I am confused. As I recall, the target superheat for a fixed metering device (orifice/non-TXV) is dependent on the return plenum wet bulb (at the plenum, not in the house because what the air conditioner sees is what is in the return plenum, not necessarily the same as the wet bulb in the house) and the condenser air entering temperature.

I checked the formula given against the generic table (originally Carrier) and found the formula proposed is way off (not usable). I gets vastly the wrong answer under many scenarios. For example at 58 return plenum WB and 80 condenser air entering temperature it gives a target superheat of 34F, while the standard table gives a target of less than 5F.

Check out the linked table below from the California Title 24 Standards

On the other hand a TXV is a constant superheat valve -- so it should not change with different return plenum or outdoor conditions. For adjustable TXVs some experienced people (like Rick Chitwood) adjust it to 6 degrees F system superheat (system superheat is based on the temperature of the suction line as it enters the outdoor unit on split systems). For a TXV or EXV it is often not adjustable, but you should suspect a problem if it is high (approx15 F or above) or low (less than 3F).  

Attachments:

RSS

Discussion Forum

joining ducts

Started by Don Fugler. Last reply by Dara Bowser 14 hours ago. 12 Replies

HVAC integration – the past, the present, and the future

Started by Igor Mitbarg. Last reply by Lucifer Prescott Apr 11. 1 Reply

Target superheat formula

Started by Miguel Orduno. Last reply by John Proctor Feb 18, 2015. 6 Replies

Latest Activity

Dara Bowser replied to Don Fugler's discussion joining ducts in the group HVAC
"Good to hear you have clean dryer ducts Don. The dryer duct issues that we run into are…"
14 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"David, If the IMC mandates metal dryer duct and prohibits metal screws, they must be accepting…"
15 hours ago
David Butler replied to Don Fugler's discussion joining ducts in the group HVAC
"I never checked that before. Checking now... Section M1502.4.2 of the International Residential…"
15 hours ago
Joseph Frasier is now a member of Home Energy Pros Forum
15 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"Brendan, Thanks for that response. Because of your warning, I just went down to the basement and…"
19 hours ago
Brendan Reid replied to Don Fugler's discussion joining ducts in the group HVAC
"Hi Don, Summary: DRYER VENT: screws bad idea, possibly prohibited by code. METAL DUCT: must be…"
20 hours ago
Profile IconBrendan Reid and David Butler joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
20 hours ago
Profile IconSean Wiens and David Butler joined Chris Laumer-Giddens's group
Thumbnail

Energy Efficient Design

Energy efficiency starts at the drafting table...How architects and designers can help buildings…See More
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service