You said take wet bulb at unit not in the house am i right or did i miss understand the formula

Views: 5840

Replies to This Discussion

You take the Indoor Wet Bulb and the Outdoor Temp

Thank You
Can you explain this superheat formula like way do we times it by 3 and mines 80 and mines cond enterning ambient,.

Thanks Mike O

Target SH = [(3 x indoor wb) - 80 - ambient] / 2 (°F)

Usually, if you are charging an ac , the manufacturer gives you a superheat range they want the equipment to operate at  (usually 6-8 degrees)   The higher the wetbulb the more capacity/cooling will be diverted to removing moisture/humidity.  

The super heat will show if the TXV is operating correctly as well.  It is a great tool for diagnosis.  If you are an HVAC dealer, your equipment manufacturer rep will be happy to explain it all to you.

All the various scenarios are to involved to train someone here.  

Yikes -- Folks help me out. I am confused. As I recall, the target superheat for a fixed metering device (orifice/non-TXV) is dependent on the return plenum wet bulb (at the plenum, not in the house because what the air conditioner sees is what is in the return plenum, not necessarily the same as the wet bulb in the house) and the condenser air entering temperature.

I checked the formula given against the generic table (originally Carrier) and found the formula proposed is way off (not usable). I gets vastly the wrong answer under many scenarios. For example at 58 return plenum WB and 80 condenser air entering temperature it gives a target superheat of 34F, while the standard table gives a target of less than 5F.

Check out the linked table below from the California Title 24 Standards

On the other hand a TXV is a constant superheat valve -- so it should not change with different return plenum or outdoor conditions. For adjustable TXVs some experienced people (like Rick Chitwood) adjust it to 6 degrees F system superheat (system superheat is based on the temperature of the suction line as it enters the outdoor unit on split systems). For a TXV or EXV it is often not adjustable, but you should suspect a problem if it is high (approx15 F or above) or low (less than 3F).  

Attachments:

RSS

Discussion Forum

Manual S for Water Furnace Equipment

Started by Jeremy Begley. Last reply by Danny Gough Mar 23. 6 Replies

joining ducts

Started by Don Fugler. Last reply by Dara Bowser Nov 28, 2017. 21 Replies

HVAC integration – the past, the present, and the future

Started by Igor Mitbarg. Last reply by Lucifer Prescott Apr 11, 2017. 1 Reply

Latest Activity

Franco Oyuela commented on David Byrnes's video
Thumbnail

Why One Room Is Hotter Than Others

"If the temperature difference between your bedroom and your living room feels like walking from a…"
2 hours ago
Franco Oyuela replied to Jan Green's discussion Mini split installation location
"First: Mini split are a great option. Second:vI agree with David that installing on the south…"
2 hours ago
Pearl Home Certification's blog post was featured
9 hours ago
John White replied to Frank Spevak's discussion Think of the house as a really big duct
"Thanks for sharing this helpful information. Want to read more on duct cleaning pros and cons.…"
15 hours ago
Jan Green replied to Jan Green's discussion Mini split installation location
"Thank you, thank you!  I appreciate your insights.  I agree with the idea that installing…"
yesterday
David Butler replied to Jan Green's discussion Mini split installation location
"Hi Jan, in a room like that with a relatively balanced aspect ratio, flat ceiling and not much…"
yesterday
Rick Blair joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
yesterday
Jan Green replied to Jan Green's discussion Mini split installation location
"This is a very rough diagram of the detached casita.  There are currently no windows in this…"
yesterday
Sean Wiens liked Jerry Needham's discussion Condensation on ceiling and walls of master bedroom
yesterday
Andrea Simmonsen liked David Byrnes's video
yesterday
Beverly Lerch replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Thanks.  A very reasonable, practical answer.  We have done our experimenting and ceiling…"
yesterday
Pearl Home Certification posted a blog post
yesterday
John Nicholas replied to Jerry Needham's discussion Condensation on ceiling and walls of master bedroom
"Jerry, ;Have you opened the cathedral ceiling?  "
yesterday
Blake Reid replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Good opinions in these replies!  I'll just add a few: * Experiment.  It's your…"
Wednesday
John White replied to Jerry Needham's discussion Condensation on ceiling and walls of master bedroom
"Condensation on ceiling occurs when the attic space above is poorly ventilated or insulated. The…"
Wednesday
Joshua P Murphy is now a member of Home Energy Pros Forum
Tuesday
Franco Oyuela replied to Frank Spevak's discussion Think of the house as a really big duct
"THANKS for the information. Ducted mini splits offer hidden benefits."
Tuesday
Franco Oyuela replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"Get into commercial, it's more money!"
Tuesday
David Byrnes's video was featured

Why One Room Is Hotter Than Others

Ever wonder if your air conditioner is working right because one room never gets a cool or warm as others? Do you need a bigger air conditioner to fix a room...
Tuesday
Profile IconEric MacCallum, Adam Morgan and Caolan Hutchens joined Home Energy Pros Forum
Monday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service