You said take wet bulb at unit not in the house am i right or did i miss understand the formula

Views: 5903

Replies to This Discussion

You take the Indoor Wet Bulb and the Outdoor Temp

Thank You
Can you explain this superheat formula like way do we times it by 3 and mines 80 and mines cond enterning ambient,.

Thanks Mike O

Target SH = [(3 x indoor wb) - 80 - ambient] / 2 (°F)

Usually, if you are charging an ac , the manufacturer gives you a superheat range they want the equipment to operate at  (usually 6-8 degrees)   The higher the wetbulb the more capacity/cooling will be diverted to removing moisture/humidity.  

The super heat will show if the TXV is operating correctly as well.  It is a great tool for diagnosis.  If you are an HVAC dealer, your equipment manufacturer rep will be happy to explain it all to you.

All the various scenarios are to involved to train someone here.  

Yikes -- Folks help me out. I am confused. As I recall, the target superheat for a fixed metering device (orifice/non-TXV) is dependent on the return plenum wet bulb (at the plenum, not in the house because what the air conditioner sees is what is in the return plenum, not necessarily the same as the wet bulb in the house) and the condenser air entering temperature.

I checked the formula given against the generic table (originally Carrier) and found the formula proposed is way off (not usable). I gets vastly the wrong answer under many scenarios. For example at 58 return plenum WB and 80 condenser air entering temperature it gives a target superheat of 34F, while the standard table gives a target of less than 5F.

Check out the linked table below from the California Title 24 Standards

On the other hand a TXV is a constant superheat valve -- so it should not change with different return plenum or outdoor conditions. For adjustable TXVs some experienced people (like Rick Chitwood) adjust it to 6 degrees F system superheat (system superheat is based on the temperature of the suction line as it enters the outdoor unit on split systems). For a TXV or EXV it is often not adjustable, but you should suspect a problem if it is high (approx15 F or above) or low (less than 3F).  

Attachments:

RSS

Discussion Forum

Manual S for Water Furnace Equipment

Started by Jeremy Begley. Last reply by Danny Gough Mar 23. 6 Replies

joining ducts

Started by Don Fugler. Last reply by Dara Bowser Nov 28, 2017. 21 Replies

HVAC integration – the past, the present, and the future

Started by Igor Mitbarg. Last reply by Lucifer Prescott Apr 11, 2017. 1 Reply

Latest Activity

John White posted a blog post
1 hour ago
Profile IconChristina Mathieson, Sophia Jones and Nancy Hawkins joined Home Energy Pros Forum
yesterday
Brett Little posted an event
Thumbnail

Duct Optimization and Performance - Free CE Webinar at Webinar Online

October 31, 2018 from 12pm to 1:15pm
Good indoor air starts with proper duct design and installation. In residential ventilation…See More
Friday
John Nicholas replied to Jerry Needham's discussion Blower door test for small apartment building
"Thank You, Colin!  Those are very good points and processes to do some Zone Pressure…"
Friday
Colin Genge replied to Jerry Needham's discussion Blower door test for small apartment building
"The way we'd normally do this is to mount one blower door in the hallway, then a duct tester…"
Friday
Scott Katznelson replied to Jerry Needham's discussion Blower door test for small apartment building
"Most of the work I do is retrofit of older buildings. Marriage wall leakage is often significant,…"
Thursday
John Nicholas replied to Jerry Needham's discussion Blower door test for small apartment building
"Scott Katznelson   In 2013,  I had my HERS Field Review completed on a multi-family…"
Thursday
Sean Lintow Sr replied to Jerry Needham's discussion Blower door test for small apartment building
"Sorry but LMAO - one blower door for that small of a space gives you an accurate number for the…"
Thursday
Chris Davis posted a blog post
Thursday
Scott Katznelson replied to Jerry Needham's discussion Blower door test for small apartment building
"The most accurate way to accomplish this is to have 4 blower doors running at the same time, one…"
Thursday
Brett Little posted a discussion

Tour 2 IL New Built Homes - 1 LEED Silver - 1 Zero Energy Ready

During the IL Green Built Home Tour, we looked at 2 homes right down the road from each other to…See More
Thursday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service