This furnace was installed two years ago in a conditioned basement.  The ductwork is a thin flexible plastic like that of a clothes dryer (but with a 6" diameter).   This is the second one that I've seen in the past year (Oregon).   Is this up to code?

 

Views: 302

Replies to This Discussion

The plastic would need to be rated for the temps the furnace delivers.  Is there a tag on the plastic?  The maufacturer would have the specs as to temp and application.  It isnt pretty but it is functional.  The specs on the plastic will give you the information you need but you might have to call the manufacturer.  I personally would be very suspect about it.   Have you performed a Temp Rise on the furnace?
This is crap work and should be redone, but is allowed by code.
I agree that the quality of work on this radial system can be called into question. But I a, very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...
I agree that the quality of work on this radial system can be called into question. But I am very surprised to hear this would meet code. Based on the 2009 IECC, that ductwork being in unconditioned space should have a minimum R-value. Here is MA and RI, inspectors hold the contractor to this spec, R-8 outside the building envelope and R-6 for inside - in a basement like this for example. This may be a place to start regarding this particular job, looks pretty recent...

RSS

Discussion Forum

HVAC integration – the past, the present, and the future

Started by Igor Mitbarg. Last reply by Lucifer Prescott Apr 11. 1 Reply

Target superheat formula

Started by Miguel Orduno. Last reply by John Proctor Feb 18, 2015. 6 Replies

Now for Something Different

Started by John Porterfield. Last reply by John Porterfield Jan 12, 2015. 2 Replies

Latest Activity

Profile IconCharles Buell, Robert Cowell, Alice Quinn and 1 more joined Home Energy Pros Forum
4 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Sean Lintow proposed rails and clips (re: first comment in this discussion), but in the context of…"
12 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"I missed where the suggestion for rails came in. The plywood would not need any rails. 4+ inches is…"
17 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"I'm a little confused about the necessity and purpose of using support rails if working on…"
17 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"If you insulate master bedroom and family room from below, you definitely need more R-value than…"
17 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Brad, I was only talking about using EPS between the ridges, if necessary, to conform to bolts.…"
17 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"It kind of depends on the PIC. Not all insulation is made the same. Here in VT (and all of New…"
17 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Filling those shallow valleys with rigid foam not only prevents primary foam panels from…"
18 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service