Trying to find %age energy saving from variety of upgrades in 10K sf multifamily house

I'm trying to figure out %age of energy savings from a variety of upgrades in a 10,000 sf building that has had deferred maintenance and a disfunctional heating system.

I'm using Energy Pro software and trying to figure out what the air flow reduction will be after adding insulation where there is none. The windows are mostly w/o hardware to keep them shut. The forced air system is nonfunctional mostly as there is no way for air to get back to the return air grill (it goes out the windows).

As it is now, the building has de facto electric heat as the forced air hardly functions. Because of this the 30 residents mostly use electric heater. I surmise that after a high quality insulation job and actually sealing the house and HVAC system that there will be little need for electric heat in mild Berkeley, CA.

 

How can I estimate air flow/leakage after the improvements? I got a stunning 27,000 CFM with my blower door in this big leaky 3 story, 10,000 sf house. I know I'm going to improve it drastically if I can sell the job.

 

Also, some of the energy improvements are really deferred maintenance rather than an energy upgrade. The historic steel windows have probably been semi-functional for many decades.

This is a bit more complicated than what I'm used to.

I've gotten bids from a variety of subs to do a quality energy upgrade and need to justify/show improvements and NPV to get a subsidy.

Thanks for any help,

George

Views: 176

Replies to This Discussion

Hello George,

If it were me, I would use the monthly electric bills to determine the average kW for each month's consumption by dividing the monthly kWh by the number of days in the billing period and dividing by 24 hours per day.  I would then determine the average monthly temperature for each monthly read and then plot the average kW verses the average temperature for each month.  The resulting slope of the line during the winter shows the total heat loss for the building that includes ventilation, conduction and existing infiltration.  Calculate the slope of the building's actual heat loss line.  Compare this actual heat loss coefficient to the total predicted heat loss coefficient (kW/F) for the building that includes the condution heat losses, ventilation air and an expected air infiltration rate if the building were properly sealed (0.75 ACH?).  You can then calculate the contribution that the excessive infiltration is having on the building's total heat loss by subtracting the predicted building's total heat loss from the the slope of the actual building's heat loss.

New Infiltration Heat Loss, kW/F = [Expected ACH after air sealing] /hr x [Volume of Home] ft3 x 0.24 BTU/lb F x 0.075 lb/ft3 / 3413 BTU/kW-Hr.

 

Conduction Heat Loss, kW/F = [Wall U-Value] BTU/Hr/Ft2/F x [Wall Area] Ft2 / 3413 BTU/kW-Hr

 

Ventilation Heat Loss , kW/Ft = [Ventilation CFM] Ft3/Min x 0.25 BTU/lb F x 0.075 lb/ft3 x 60 min/Hr / 3413 BTU/kW-Hr

 

The predicted energy savings is simply the difference between the slope of the actual heat loss line and the slope of the predicted heat loss.

Savings Potential, kW/F = Actual kW/F - (New Infiltration Heat Loss + ventilation Heat Loss + Ventilation Heat Loss)

Hi George,

You don't happen to have a spreadsheet handy for those calculations do you? :-)

Here is a spreadsheet that I have for identifying savings using monthly bills and average monthly temperatures.

We documented actual energy savings using this method during our "Reduce Your Use" contest that we conducted here at Chelan County Public Utility District.

 

Jim White

Sr. Energy Conservation Engineer

Attachments:

O.K., forget all of the Engineer jokes! Thank you very much Jim. Engineers rule!

RSS

Discussion Forum

Energy 2D and 3D

Started by James White. Last reply by James White Nov 6, 2014. 1 Reply

Transient Heat Transfer Analysis

Started by James White. Last reply by James White Dec 10, 2013. 5 Replies

How about simulation in the multifamily context?

Started by Evan Mills. Last reply by Don Hynek Jan 23, 2012. 6 Replies

Latest Activity

Liam Smith replied to Bruce Navin's discussion LED's interfering with Garage Door Openers
"Door openers operate with the remote control on radio frequencies, just like a remote-controlled…"
6 hours ago
John Nicholas replied to Jignesh's discussion Efficiency of furnace
"Any of the various energy modeling programs would give you a starting place. Model the ducts in…"
16 hours ago
John Nicholas replied to Jignesh's discussion Efficiency of furnace
"That is why gravity systems are much less popular then 50 years ago.   It could easily be…"
16 hours ago
Jim Baerg replied to Jignesh's discussion Efficiency of furnace
"This is a great discussion.  I'd like to ask a question about the distribution…"
17 hours ago
Michael R. Johnson posted a status
"Diane, Thank you for the welcome, I appreciate it. I look forward to contributing to the conversation. Michael"
19 hours ago
Gary Hall is now a member of Home Energy Pros Forum
yesterday
Brad Cook replied to Jim Conlon's discussion Insulation Blower Recommendations?
"Most rental machines will not put out the minimum required pressure for dense-packing. There are…"
yesterday
Brad Cook replied to Jim Conlon's discussion Insulation Blower Recommendations?
"We have been using the Intec Force II for almost 10 years. It only takes about 1 1/2 bags at a…"
yesterday
Eric Kjelshus replied to Jim Conlon's discussion Insulation Blower Recommendations?
"Most generator are more efficiency at 240 volt.   Its  about the total watts more…"
yesterday
Eric Kjelshus replied to Jignesh's discussion Best brands for furnace
"Its more about the install and air flow than the box brand,  Most brands about the same if you…"
yesterday
Eric Kjelshus replied to Jignesh's discussion Efficiency of furnace
"OK lets say you have a gravity air system with a 80% burn on heat exchanger with out the 8"…"
yesterday
John Nicholas replied to Jignesh's discussion Efficiency of furnace
"System Efficiency is great.  Not much use, if you don't intend to fix the various…"
Thursday
John Nicholas replied to Jignesh's discussion Efficiency of furnace
"Furnaces and all HVAC Equipment is rated by AHRI.  You can get the certification as to the…"
Thursday
Jacob Corvidae replied to Diane Chojnowski's discussion Support Mike Rogers in the group News & Announcements
"Hey Mike! We're all routing for you! Don't hesitate to ask for help.  Jacob"
Thursday
Jacob Corvidae joined Diane Chojnowski's group
Thumbnail

News & Announcements

Share your news and announcements with the community in this group.To post news or an announcement,…See More
Thursday
Diane Chojnowski added a discussion to the group News & Announcements
Thursday
Profile IconJeannette Moore, David Carson, Jesse Smith and 3 more joined Home Energy Pros Forum
Thursday
Home Energy Magazine's blog post was featured

How We Turned Our House into a Giant Foam Box, Part I — Wall Insulation By Wen Lee

Chris Stratton and Wen Lee are a husband-and-wife team living in the Los Angeles area who are DIY…See More
Wednesday
Home Energy Magazine posted a blog post

How We Turned Our House into a Giant Foam Box, Part I — Wall Insulation By Wen Lee

Chris Stratton and Wen Lee are a husband-and-wife team living in the Los Angeles area who are DIY…See More
Wednesday
Chris Stratton replied to Chris Stratton's discussion Technical question about mini split heat pump line set maximum length
"Hi Chris, Thanks again for your help. Update: the system is now up and running. Chris"
Wednesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service