I got this email from a QA program manager. Looking for feedback. Thanks

 

 

I have a question for you I'm hoping you can shed some light on.

How are we supposed to proceed with getting combustion and worst case depressurization numbers from an area that is inaccessible?

I just ran into this situation over at customer's home with a tankless water heater on his second floor.
The only option to get a flue gas sample is to set up an extension ladder in an alley which doesn't have clearances that are proper for an extension ladder.

Look forward to hearing how you would proceed on this.

Views: 64

Replies to This Discussion

 

You should be able to access the room where the water heater itself is located.  Otherwise if it is in some kind of sealed off space, then it probably doesn't meet code requirements.  So you should be able to do a worst case depressurization test on the CAZ.  Although since it is sealed combustion, it is probably not a big deal. 

 

I think a lot of programs will waive requirements to get a CO reading on the flue gases if the appliance is condensing and/or sealed combustion, and the flue vents out the roof and is not easily accessible. 

 

I'd agree w/ the previous post. When going for a worst case test, you only need to measure presssure difference in the CAZ WRT outside. I'm figuring you can get into the CAZ. If required, Measuring exhaust gas for CO and efficiency on a sealed appliance is done from the outside according to most, though several well known pro's will drill the PVC pipe and sample from there, then seal the pipe with fire rated caulk.   
Thanks folks. The culprit here is an older tankless that is not sealed combustion.

If the tankless water heater is not sealed combustion, then it could be either power vented (one PVC pipe), induced draft (inducer motor and metal pipe), or natural draft (with draft hood).  I am not comfortable drilling a PVC pipe to measure CO, but some will drill it and seal it with silicone caulk.  A metal pipe for an induced draft appliance can be drilled and plugged with a metal plug or taped with metal tape.  If it is natural draft, you can measure the CO by putting the probe down in the heat exchanger from the draft hood.

This is what we do:  The Standards are clear:  No air sealing, dense packing more than 15% of the shell area, duct sealing outside the thermal envelope, if you cannot complete the or combustion testing protocol.  So, if we cannot test all the appliances that might be affected by modified house pressures due to air sealing, than we don't recommend air sealing.  More accurately, we explain the issues on the work order and customer report.  If we get full access to the entire building, so we can create worst case conditions in all CAZ's, and we can test to the Standards, then we include air sealing on the work order (if apporpriate).   Also... yes, we've climbed ladders to take samples from flue gasses... but of course we prefer to drill and fill where allowed!

RSS

Discussion Forum

BPI is Hiring!

Started by Quinn Korzeniecki. Last reply by Diane Chojnowski Jun 29. 1 Reply

Latest Activity

Profile IconAvery T. Phillips, Sarah Burger, Troy Spindler and 2 more joined Home Energy Pros Forum
14 hours ago
David Butler replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"theoretically, let's say you perfectly isolate the HPWH from a heat source. The HPWH's…"
yesterday
David Butler replied to David Butler's discussion How would you insulate this roof?
"Interesting idea. Commercial roof on a slope! Typical density for roofing spray foam is 2.5 to 3.0…"
yesterday
Profile IconRandy Kinnison, Breanna Detwiler, Jeff Farlow and 7 more joined Home Energy Pros Forum
yesterday
Summer Redman added a discussion to the group Job Board
Thumbnail

Hiring 2 Training Specialists in Champaign-Urbana, Illinois

The Applied Research Institute (ARI) at the University of Illinois at Urbana-Champaign is seeking…See More
yesterday
Summer Redman joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
yesterday
Stacie Bagnasco replied to Evan Mills's discussion Dirty solar panels
"This is a great idea. I clicked on your discussion because it made me remember that I forgot to get…"
yesterday
Kirsten Richnavsky posted an event
Thumbnail

rCloud - The Future of Testing at Your Office or Home

October 18, 2017 from 2pm to 3pm
Integrating rCloud as an essential part of your RESNET QA process.Retrotec’s rCloud app is here,…See More
yesterday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service