Hi again,

    This is a great place to learn, thank you all that have answered my questions. Here is the next one. I just completed an audit and they only have a heater that is ducted because they are in a beach community. It was very leaky, but leaky compared to what??? I have read through my BPI and can't find some kind of multiplier for heater duct leakage

Judi

Views: 50

Replies to This Discussion

Duct leakage is leakage. I always apply the 6 cfm per 100 sqft energy star leakage standard for the ducts that I work with. The main difference in heating and cooling is in expected air flow of the two system types which vary.

21.7 times the OUTPUT btu= cfm for heat  Example: 100,000 btu furnace input   80,000 btu furnace output. 80% efficient.

21.7 X 80=1736 cfm supply for heat. You have to go outside BPI for these formula's. Try national comfort institute. The 80 comes from dropping the zero's  from 80,000 btu

thank you both, ahhh I forgot my HERS stuff. Yes, when I saw 21.7 I remembered HERS. See somtimes a little nudge is all we need. I guess I couldn't think of putting HERS and BPI together. Thanks much appreciated.

Judi

RSS

Latest Activity

Lucyna de Barbaro liked David Eggleton's group 1000 Home Challenge
11 hours ago
Steven Lefler's photo was featured
12 hours ago
Brad Cook replied to Dav Camras's discussion Low Leakage home with cathedral ceiling
"It is all about the dewpoint. Think of the roof system as a big box. Air can circulate in, out and…"
14 hours ago
David Butler replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"@Dav, 240-volt circuits are dedicated to a single appliance so circuit monitoring with CT's…"
yesterday
Dav Camras replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"I have been thinking about putting it on my own home as you suggest, and was wondering which, if…"
yesterday
Profile IconGrady Harper, Christina Savage, gregory sutliff and 1 more joined Home Energy Pros Forum
yesterday
Doug Mullins added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door equipment for sale

I have 5 ea Retrotec 6000 blower door fans - $3500.00 ea1 3000 series fan with WiFi -…See More
yesterday
Jon Finewood joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service