Hello All,

I have installed few Zehnder systems and I am not sure if my rep is giving me the info I need or the info that helps me buy more foam piping from him. The large ducting (7" Comfopipe) coming off the unit  at the 4 ports for supply (fresh and to house), exhaust to exterior and from interior). Which are most critical to be insulated piping. If my supply from the ERV is running through a conditioned space, would a sheet metal duct without insulation gain condensation? Would the exhaust from my interior space require insulation? Since the comfotube is not insulated it seems like the additional cost for 39" runs at $77 is not the best cost option.

There are a lot of situations where I have extended internal runs from the ERV to the silencers/manifolds in order to keep my Comfotube runs under the recommended 35'. In a current install I have about 25' horizontal to a 12' vertical of 2 runs of Comfotube. That is not cheap and if I can do these types of runs in sheet metal with sealed seams and no insulation, there is a big cost savings to my client.

The supply and exhaust from the exterior I am more comfortable using the Comfopipe to ensure I don't get condensation.

Any thoughts?

Thanks

Alan

Views: 158

Reply to This

Replies to This Discussion

Good questions. I would say that on the "house" side, which is connected to the inlets and outlets in the living space, there should be no need for insulated ducting, if the duct runs are in conditioned space. But the ducts connected to the outside could certainly have condensation during the heating season. A house at 70F and 40% RH has a dewpoint temperature around 45F. I'm guessing your outside temperatures are often below that?Check out a psych chart for other temp/RH combinations. The duct surface will be cold, likely below the house air dew point temperature, voila, condensation. I would consider insulated ducting for the runs connected to outside inlets/outlets, but none for the others. As for using the expensive comfotube product, it is a choice, with pro's and con's. I think that well-executed rigid sheet metal ducts would perform very well, if you insulate and seal them appropriately. Cheers.

Also, if it's exceptionally cold outside, you could have a supply air temp into the living space that is below the dew point. For example, if it were 70F inside and -30F outside and you have a sensible efficiency of 70% (Zehnder is higher, I think), then your supply air would be 40F (70-100*(1-0.7)), also below the house air dew point. Also notable, some condensation is NOT death, as long as it dries out reasonably quickly, etc. If it happens for 6 hours of the year in 1 of 5 years, don't sweat it.   

It's a good question and certainly saving ComfoPipe is a good thing. The ComfoPipe is Insulated R-7 and non-conductive. I wish it were available somewhere else. Flexible Insulated spiral duct sadly will sweat like tin on some days unless installed perfectly. Which is nearly impossible.

A double wall tin pipe with insulation between is available, and more expensive than ComfoPipe. Non conductive R-6+ is what you want to penetrate the walls of a performance building. The ComfoPipe attaches to the AirBarrier. Use this pipe from unit through wall. It handles the Cold Side of the ERV/HRV. Cold Pipes in Warm Spaces-> Insulate it.  Connections from the ERV/HRV should be 8' +/- to the exterior air to aid efficiency of ERVs/HRVs.

Also note the ComfoTube; which is the 3" white flexible rigid duct that fits in 2x4 walls is also non-conductive. It's like fiber-optics for the internet, but for precise fresh air and exhaust. Very worth the money especially to deliver fresh air to the far rooms in buildings with precision.

ComfoTube is insulated, but like R-8 flex duct insulation it may not have enough R-value for some situations. The other big problem with ComfoTube is it isn't large enough for the airflows in a lot of systems. Based on Lifebreath duct design software runs, I use 8" steel for the outside connections and keep them close to 8', and use 8" for the inside duct runs for the first few Y's or long runs. I have never used ComfoTube on any Zehnder install, just putting a 7x8 3-piece increaser right on the connections and going steel as far as necessary to 6" American-style diffusers. These systems commissioned nicely.

In one house with some very restrictive structural limitations I had to use 3" Zehnder flex to go through steel I-beams a long way from the CA-350. So I ran 8" steel up to the beam, put on a 8x10 increaser and 10" cap with 4) 3" holes cut in it, then cannibalized a Zehnder flex manifold for the four flex connectors I put on the end of the cap. This gave me an inline 4-tube manifold that fit inside the joist bay for almost no cost. I had to do this with a 6" cap for a two-flex run to a high flow register. At the duct boots I belled back up to 6" round for standard HRV diffusers like the rest of the house. This commissioned properly.

By the way, the only thing I use American flex duct for is insulating steel duct; You can tape the inner liner onto the steel duct and pull the insulation and outer liner over the steel. Discard the inner liner. But we probably want more than R-8 unless the ducts are inside the thermal and pressure envelope, and the outer liner will deteriorate from UV, even in an attic with roof vent light. American flex duct is a temporary duct system in most locations.

@Alan, I see you're located coastal California so there's no chance for any condensation on any supply runs inside the thermal envelope, so uninsulated metal pipe is fine for all house side ducts -- supply and exhaust. Brennan's example is spot on for cold climates.

The fresh air duct from outside to ERV needs to be insulated to prevent condensation in cold weather, but only the section exposed to house humidity, i.e., from the thermal boundary to the unit.

I'm probably the odd man out when it comes to insulating the exhaust line from the ERV to the outside. I don't see the need for insulating that duct run, especially in your climate.  With an enthalpy core, the outside exhaust line could potentially sweat on the INSIDE surface in cold weather as it passes through unconditioned space (depends on inside-outside dew point differential and outside temperature), which is why installation instructions typically specify a slight slope to the outside.

In summary, the only ERV duct that must be insulated in your relatively mild climate is the fresh air intake duct, but only the section that passes through conditioned space.

Thanks for your feedback and information. I will be making adjustments in the future when I am running in conditioned space.

RSS

Latest Activity

Rick Barker is now a member of Home Energy Pros Forum
17 hours ago
David Keefe's video was featured

A Climate Report From The Field - Keefe

"A Climate Report from the Field" by David Keefe. Part of a TED-inspired evening session at the HPC Home Performance Conference, Philadelphia PA, April 25, 2018
18 hours ago
Bob Krell's video was featured

Carbon Monoxide Webinar with Bill Spohn - Healthy Indoors Show- Special Live Edition 4-16-18

Guest Bill Spohn, of Tru Tech Tools, joins host Bob Krell, to discuss Carbon Monoxide (CO) in the indoor environment. This show is a recording of a live webinar event on April 16, 2018.
18 hours ago
David Keefe posted a video

A Climate Report From The Field - Keefe

"A Climate Report from the Field" by David Keefe. Part of a TED-inspired evening session at the HPC Home Performance Conference, Philadelphia PA, April 25, 2018
18 hours ago
John White posted a blog post

What to Expect from a New HVAC Unit Installation Cost

The cost of installing an HVAC unit, such as an air conditioner installation in Laguna Hills, will…See More
yesterday
Kelly Vaughn posted a blog post

How Cities Can Ensure Better Rentals for Everyone

By Alisa PetersenWhile much of RMI’s research and analysis on home energy performance has focused…See More
yesterday
Brett Little posted an event

Resilient Design in an Age of Climate Change - Free CE Webinar at Webinar Online

May 30, 2018 from 12pm to 1:15pm
A changing climate, sea level rise, drought, and a wide range of stresses in the world are…See More
yesterday
John Oxford posted a blog post

Make 2018 The Year You Fear No Power Outage

Get A Back-Up Generator For Your Home’s “Mission Critical” Power Needs…See More
yesterday
Diane Chojnowski posted a discussion

California's new solar roof mandate

There's an interesting article in GreenTech Media about California's new solar roof…See More
yesterday
Ron Jones joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
yesterday
Ron Jones joined Diane Chojnowski's group
Thumbnail

News & Announcements

Share your news and announcements with the community in this group.To post news or an announcement,…See More
yesterday
Ron Jones joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
yesterday
Don Fugler added a discussion to the group Kitchen Ventilation
Thumbnail

Choosing a range hood

There is so much information - how do you find what you need?With the references listed in Tom…See More
yesterday
Ron Jones joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
yesterday
Mike faurot replied to Jerry Halls's discussion Retrotec Blower Door & DucTester For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Please send me a contact number to 772-528-2076. I would like to discuss a pup if you still have…"
yesterday
Don Fugler liked Tom Phillips's discussion Kitchen Ventilation Resources
yesterday
Mike faurot replied to Jerry Halls's discussion Retrotec Blower Door & DucTester For Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Please send me a contact number to 772-528-2076. I would like to discuss a pup if you still have…"
yesterday
Mike faurot joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Bob Krell posted videos
Monday
Profile IconRon Jones, universal services and Mike faurot joined Home Energy Pros Forum
Monday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service