Anyone ever hear of a window, or unit of insulated glass, as having different winter and summer U values? 

 

This wasn't on an NFRC sticker.  It was on a glass manufacturer's spec sheet. 

 

They listed it like this:

 

Winter - Air / Argon  0.35 / 0.31

Summer - Air / Argon 0.32 / 0.28

 

Our program requires a U value of 0.30 to receive an incentive rebate.  So obviously, homeowners and contractors want to average the summer and winter Argon fill U values to come up with an average of 0.295 and call it good.

 

I think it is just a piece of insulated glass that they want to have installed/retrofitted into their existing wood windows, and get an incentive for that. 

 

Views: 6364

Attachments:

Reply to This

Replies to This Discussion

The winter U-value is what is shown on the NFRC labels, and should be used for code compliance and incentive programs. It is calculated at -18C (about 0F) outside, and 21 C (about 70F), and a roughly 15 mph wind speed. The summer U-value is calculated with conditions where it is warm outside and hardly any wind. This means that the U-value will be a bit better, but it is not a representative condition for heat losss. The Solar Heat Gain Coefficient (SHGC) is more important during periods with solar gain. So think U-value for heating, and SHGC for cooling.

Christian
WIndows and Daylighting Group
Lawrence Berkeley National Laboratory
Adam:

Currently in communication with this gentleman:

Andre Anders, PhD
Leader, Plasma Applications Group
Lawrence Berkeley National Laboratory
1 Cyclotron Road, MS 53, Berkeley, California 94720, USA
Tel. 510-486-6745, Fax 510-486-4374

He's circulating the information among his associates and will be in touch following the holiday. Will probably find it's way Christian at LBNL, who has responded since last I checked in.

BTW, Christian's advice to use the winter number is probably not what you wanted to hear regarding the available incentive. If 0.30 U is a common cut off # for incentives, I would expect manufacturers to work to that figure, although in a manufacturing environment, such changes may be a challenge. Perhaps a bit of latitude from incentive providers is in order...who is going to notice a U difference of 0.01 ?

Thanks for surfacing this mystery.
Steve, Adam,

Andre forwarded your question to me, that is why I responded here. Many manufacturers have products that meet U=0.30, since that was the cut-off for the IRS tax credit.

If you are looking for even better windows, you can take a look at this website, where you can find listing of manufacturers that meet U=0.22 and less.
http://www.windowsvolumepurchase.org/

Christian
Thank you for the replies! Our program does require NFRC stickers, so this guy is going to be out of luck anyways.

But I was curious about the different winter and summer U values anyways. Thanks for the response and clairificaiton!

Adam

RSS

Forum Discussions

Mini split installation location

Started by Jan Green in HVAC. Last reply by David Butler 22 hours ago. 13 Replies

Think of the house as a really big duct

Started by Frank Spevak in HVAC. Last reply by John White on Friday. 2 Replies

Mini split air conditioners and ceiling fans

Started by Beverly Lerch in General Forum. Last reply by Beverly Lerch on Thursday. 13 Replies

Condensation on ceiling and walls of master bedroom

Started by Jerry Needham in General Forum. Last reply by John Nicholas on Thursday. 10 Replies

Latest Activity

Profile IconDavid R Young, Chris Joiner, mosan and 1 more joined Home Energy Pros Forum
3 hours ago
Home Performance Coalition liked Hannah Finch's blog post Announcing National Energy Geek Day [October 6]
4 hours ago
Tom Phillips replied to Don Fugler's discussion Choosing a range hood in the group Kitchen Ventilation
"thx, Don. See slides 16-17 BTW, it is a modeling study , based lab data and assumed outdoor PM2.5…"
8 hours ago
Matt Wright added a discussion to the group Job Board
Thumbnail

Home Performance Expert in Frisco, CO

Deeper Green ConsultingHome Performance ExpertJob Description:Deeper Green Consulting is seeking a…See More
9 hours ago
Home Performance Coalition shared Barbara Smith's video on Twitter
9 hours ago
Shine Facility Services posted a photo
9 hours ago
Don Fugler replied to Don Fugler's discussion Choosing a range hood in the group Kitchen Ventilation
"There is a scientific paper that Tom Phillips cited where the researchers are looking at the…"
10 hours ago
David Byrnes's video was featured

Should the Attic Floor Insulation Be Removed When Doing Spray Foam?

Spray foam insulation contractors and homeowners alike have debated this questions over many years and since spray foam first gained popularity
13 hours ago
John White posted a blog post
18 hours ago
David Butler replied to Jan Green's discussion Mini split installation location
"I'm not sure if I'm making myself clear. You don't want to 'squeeze' the…"
22 hours ago
Jim Gunshinan posted a blog post

More "Buzz" from ACEEE Summer Study—Grow Homes

Joe Clark and Martha Wudka of Evergreen Economics did a study in which "getting into the weeds (or…See More
yesterday
Jan Green replied to Jan Green's discussion Mini split installation location
"I agre that the south wall would be shaded for the warmer summer months, but it won't look…"
yesterday
Jan Green replied to Jan Green's discussion Mini split installation location
"I'll check on electrical.  Good point.  "
yesterday
Jan Green replied to Jan Green's discussion Mini split installation location
"Thank you for that.  I wanted to put it on the west wall since there isn't much chance of…"
yesterday
David Butler replied to Jan Green's discussion Mini split installation location
"Hi Jan, actually, I said you'd be find putting it on the west wall since you wanted a larger…"
yesterday
Brett Little posted an event
Thumbnail

Using Pearl Certification to Bridge the gap between home energy and value - Free CE Webinar at Webinar Online

October 3, 2018 from 12pm to 1:15pm
In this webinar, “The Power of the Pearl Connection”, Pearl Certification’s Cynthia Adams, CEO and…See More
yesterday
Walter Ahlgrim replied to Jan Green's discussion Mini split installation location
"Being a Flip you must consider the install cost. At least get a bid for a PTAC unit like the ones…"
yesterday
Daniel Baur-McGuire replied to Jan Green's discussion Mini split installation location
"South Wall. It will have the highest load needed for cooling/heating. the shade from the tree could…"
yesterday
Glen Gallo replied to Jan Green's discussion Mini split installation location
"I would add where is the power coming from? the south wall proposed might have easier access for…"
yesterday
Todd Hensel is now a member of Home Energy Pros Forum
yesterday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service