The L-shaped probe grew legs, so this was improvised with a straight metal tube. There seems to be a persistent notion that angling the probe toward the appliance (into the exhaust stream) is the correct technique, but wouldn't this result in interference from ram air pressure of the rising flue gases?

Tags: CAS, CAZ, analysis, combustion, draft, pitot, safety, spillage, tube

Views: 639

Reply to This

Replies to This Discussion

I'm guessing that is the short metal tube that comes with the DG.  If that is the case, go with perpendicular to the pipe.  Might want to trim some of the pipe insulation off as well before the job is completed.  The insulation looks a little close to the vent, based just on the pictures above (clearance to combustables).

Thanks Dan. Yes, it's the straight tube from the DG bag. Interestingly, Minneapolis sells what they call a "Static Pressure Probe" and distinguish it from a "Pitot Tube", which they don't sell. Both are right-angled metal probes, the difference being that pitot tubes measure ram air (or velocity) pressure through an opening in the tip that static pressure probes don't have.

The principle is familiar to the aviation geek in me (aircraft use a pitot tube to measure airspeed and a static pressure port with an aneroid barometer to measure altitude). After further discussion in our office and examination of one the aforementioned static pressure probes, angling the tip toward the appliance would, in fact, align the holes in the probe perpendicular to the exhaust stream for a true static pressure reading. In that context, the technique I hear people cite about pointing the probe into the stream makes sense, as does your recommendation to hold the straight metal tube perpendicular to the flue.

I think the tight clearance is a result of the photo angle here.

A pitot tube on an airplane is pointed forward because you want to measure air speed and if it points into the wind it measures, well, the speed of the air.

Draft in a heater is different - we aren't looking for MPH but Delta P.  These are 2 different things.  Both the pitot tube and the bent static probe have holes perpendicular to the air stream so are measuring the same thing.  The straight pitot tube in a heater flue should point straight in to measure the same thing that the bent static probe measures when either pointed toward or away from the air stream.  

Interesting that, in your pictures, the probe pointed into the airstream measures zero.

Yep - and the static pressure port is usually on the side of the fuselage, perpendicular to the airstream.

The reading pointed toward the airstream fluctuated between -0.2 and 0.2 or so. If we interpolate the "true" static pressure as about -2.0 (halfway between zero and -4.1), then the interference of the velocity air pressure directly entering the tube, which the manometer would interpret as positive, explains the zero reading.

Isn't there a measurement missing here?...

Yeah, it should have been taken perpendicular to the flue, as Dan pointed out.

Too cryptic, sorry.  

Shouldn't there be another tube and another pressure being measured?...

Hmm. I've understood the intent to be measuring the delta P of flue gases and the ambient air, but it's been quite a few moons since I've done combustion testing on a regular basis. What am I missing here?

Ted

Still too cryptic

Where is the 2nd hose measuring caz depressurization?

I see what you mean - but the title of the thread is:

Which is the valid draft test, noir which is the valid CAZ test

Is it a valid draft test without both numbers?

RSS

Latest Activity

Bob Krell replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Most of the moisture issues there can be attributed to failure to get the roof system completely…"
2 minutes ago
Bob Krell replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"You are correct about it being multi-family.  It is, in fact, an assisted-living facility, so…"
5 minutes ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Weatherization Pros: Only 9 Days Left to Apply for Free BPI Certification Exams!

Are you a weatherization professional? Don't miss your chance to get the costs of your new 2018 BPI…See More
12 minutes ago
Quinn Korzeniecki posted a discussion

Weatherization Pros: Get BPI Certification Exam Costs Covered!

Are you a weatherization professional? Don't miss your chance to get the costs of your new 2018 BPI…See More
14 minutes ago
Diane Chojnowski replied to David Butler's discussion Beginners Guide: Managing Subscriptions on Home Energy Pros
"Great guide David! Thanks! We send two weekly emails to keep members in the loop about new blogs,…"
1 hour ago
Summer Reyes's blog post was featured

Equipment We Use: Detecting Water With Infrared Cameras

You know water is somewhere on the property, you can smell the mildew, but can't determine the…See More
21 hours ago
Profile IconGlenn Hourahan and Joseph Frasier joined Home Energy Pros Forum
21 hours ago
Alfredo Baccari added a discussion to the group Job Board
Thumbnail

HERS or/and BPI Energy Inspector in SF Bay Area (SAN JOSE, CA).

ELEM3NTS is a leading energy efficient consulting company specializing in residential homes. We…See More
22 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service