Where to install the vapor barrier for a finished basement?

I have an audit customer that is in the process of finishing his basement. The basement foundation walls are poured concrete. He has installed a polyethylene vapor barrier over the concrete wall per his brother's instructions who is a builder. He plans to install unfaced insulation in the 2 by 4 stud walls that are 2 inches away from the concrete wall. He will be also installing drywall and heating the space with his existing HVAC unit. This is an all-electric two story home located in Ohio.

 

I'm already recommending he seal the entire rim joist with foam since they are leaking a lot of air. The rim joists are currently fitted with faced fiberglass batts. My thoughts are to advise him to also foam the entire basement wall but I'm not sure this is the correct or the best solution. If he decides to install fiberglass batt insulation in the 2 by 4 walls, where should the vapor barrier be installed? The poured cement basement walls are dry with good drainage outside so I'm thinking the vapor barrier should be installed between the drywall and insulation since the basement will be a conditioned space.

Views: 60476

Reply to This

Replies to This Discussion

I'm referencing Joe Lstiburk's "Cold Climates" You should not install poly on the walls in the assembly. It will cause the wall to retain moisture. The key is to let the walls dry to the inside or the outside. I would also not use fiberglass in the basement because it is hydrophilic. A water resistant insulation would be a better material to use. I recommend you get a copy of "Cold Climates" it covers all the different areas in a house and the best methods for building and insulating.
Thanks Chris for your feedback. I will get Joe Lstiburk's book so I can add it to my reference library. 
You're very welcome.

Also, review the work of the Pat Huelman and the folks of the Cold Climate Housing Center. Pat and his people have done a lot of work in this area. And he and Dick Stone do a lot of training -- Affordable Comfort, the Duluth EDC conference, etc.

 

I don't believe any of their work contradicts the info in the "Builder's Guide: Cold Climates" book. But they may well have info on the most recent "miracle" materials out there intended to "allow" building assemblies that will just never work. (Like this goofy idea that you can successfully put a functioning vapor barrier on the warm side of a below-grade concrete wall!) 

Thanks Don for making me aware of Pat Huelman group. I'll definetly review their findings.

Jim,

Your question and the subsequent responses got me thinking. 

I tell myself I should know the answer to this question but I found myself wavering a bit.

I have “Cold Climates” but it has been awhile since I have reviewed it and looked at this wall profile.

 

Out of curiosity I searched the web and here is what I found at an EPA site.

http://www.epa.gov/indoorairplus/technical/moisture/1_12.html

 

“An appropriate assembly for the inside of a basement wall consists of 1 in. of plastic foam board or closed-cell polyurethane spray foam followed by a stud wall with fiberglass insulation filling the cavities. This assembly is covered with moisture- and mold-resistant gypsum board covered by two coats of latex paint. The foam board serves two purposes: providing a capillary break between the foundation wall and the stud wall and keeping warm, humid basement air away from the earth-chilled foundation. It is good practice to put 1 in. of foam board beneath the sole plate of the stud wall and the basement floor and to leave a ½-in. gap between the basement floor and the bottom of the gypsum board. Doing so provides protection from minor floods and damp concrete floors.”

 

Clicking the link provides additional explanation and context for this strategy.

I wonder if this is consistent with the other resources mentioned. If not i would like to hear others thoughts.

You can find an excellent publication on this question at http://www.buildingscience.com/documents/reports/rr-1003-building-a....  The publication presents many solutions and rates them on several criteria.  They also conducted detailed thermal and moisture modeling.

I put 2" XPS on my basement walls as a temporary way to add some insulation before I got to the task of finishing the basement walls. I did not seal the joints between the sheets or the gaps at the top and bottom of the sheets.  I had lots of ice on the top of the foundation wall and ice at every joint and gap down to the soil line.  A well sealed vapor barrier at the foundation wall is absolutely critical to preventing moisture problems.

After seeing the moisture/ice problems first hand, I think I will insulate the stud walls with closed cell foam to assure that I have no air leaks.  This will cost more but the peace of mind is worth it.  I live in a very cold climate near Yellowstone National Park.  We have had many consecutive days of -20 to -30 F this winter.  I am sure this contributed the ice formation behind the XPS and on top of the foundation wall.

polyethylene vapor barrier is the most common that the contractors use. See this http://www.agmrenovations.com/safebasement/ incase you need any information

No first-hand experience, but that stuff looks like spray-on bulk water proofing material not moisture seal. And why are they spraying it on after the stud wall was erected and not before?

Since he's also in Ohio and has a great deal of experience, you might want to reach out to Nate Adams at Energy Smart Home Performance for his opinion.

RSS

Latest Activity

Profile IconSean Wiens and David Butler joined Chris Laumer-Giddens's group
Thumbnail

Energy Efficient Design

Energy efficiency starts at the drafting table...How architects and designers can help buildings…See More
7 hours ago
Profile IconSean Wiens and David Butler joined Mark Richardson's group
Thumbnail

Renewable Energy

This group will focus on the issues associated with incorporating renewable energy sources like…See More
8 hours ago
Al Tibbs posted photos
8 hours ago
Al Tibbs replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"In any case where there is visible mold present, I would begin with a thorough VISUAL assessment of…"
9 hours ago
Al Tibbs joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
9 hours ago
David Byrnes posted a blog post

Strategies for Hiring and Interviewing for Home Performance Professionals

Hire slow and fire fast.  It’s a phrase that experienced managers and human resources professionals…See More
10 hours ago
David Butler posted discussions
10 hours ago
David Butler replied to Don Fugler's discussion joining ducts in the group HVAC
"Static pressure drop through a straight length of pipe is a function of friction rate, and friction…"
15 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service