Gravity?

With so little information, this is like a stump the chump from BPI.  A picture would be nice...

I would think it is likely that the furnace was over sized for the demand and short cycled.  The short cycling will not heat up the chimney enough to purge the condensation so the water is absorbed into the masonry.  Repeated cycles of freeze and thaw will cause the mortar and the bricks to fail.

It is oversized only if you have performed a load calc.  Otherwise who knows if it is right or wrong sized.  Even if it is the correct size, an 80 % furnace vented into a an unlined chimney will condence.  That will happen at a greater rate when the chimney is in a cold attic.  If the house was sealed, then the attic is colder yet and the condensate will condense at a faster rate.    

It is a classic.  The chimeny was probably failing before the air sealing and before the furnace was installed.  Assuming that there was a furnace there before.  The change in the house probably made the falure more rapid.  It will happen even if the furnace is correctly sized, under or oversized.  The system was just installed incorrectly.  

This extremly accurate opinion has been reached by taking a question with no facts provided to its logical conclusion.   If you can measure it, you can quantify it, if you can quantify it you can compare it to what is normal and  only then can you diagnose the issue and apply the correct remedy.

If you want a factual answer ---- provide facts 

Eric, if you provide a little more information, we can sleuth the answer for you.

-- Age of house?

-- what kind of chimney materials (Brick, stone, CMU, etc.)

-- Climate where this house is?

Chances are if it's an older house (70-100 + years), then the mortar was already failing.  We see these everywhere in the Bay Area, and the furnace has nothing to do with them.  There should be a flue liner, if this chimney connects to other sources, like a wood burning fireplace.

A natural gas furnace vent doesn't put any pressure on the chimney; the water from the combustion wouldn't affect the mortar unless the chimney was blocked and not venting properly -- but then you'd have CO problems, which you haven't indicated.

Pictures and more information would be helpful.

the house was build in Kansas City MO in 1903.   4710 Degrees days with about 65 days gets under 32'.  All stone with a 18"X18" clay liner  that had a 850,000 BTU boiler now just a 120,000 up flow 80% with that main floor now has a heat loss of just 42,000 BTU at 0' out side.  So the furnace is 3 times over sized and the flue should be 5" liner.  The stone chimney  heat up  about one foot each time its start up.   The dew point with flue gas is 255'  stone chimney does not get up to temp unless some one turns up the heat  or leaves the main door open.   The chimney stays wet and some time goes though the freese with lack of being in building.   After 2 year with a 80% furnace  the chimney started to fall.   The boiler had a 7" flame to light the burners and to keep the flue hot.   

   I did not see any reference to acidity in the condensate. The acidity will quickly damage the masonry joints. This is why liners and exhaust lines are nearly always acid resistant. This is why the condensate drains are neutralized with limestone prior to going down the drain. There were many problems in the early days of high efficiency boilers when the new boiler was just plugged in to the existing masonry chimney.

I see each day that acidity can rot masonry, so keep the flue gas above the dew point.   around 255' and above with natural gas will keep flue gas above dew point.   I have seen cast iron floor drain flake apart in one winter with a 90% boiler.

RSS

Latest Activity

Shane S posted a photo
1 hour ago
Al Tibbs posted photos
9 hours ago
Al Tibbs commented on Eric Aune's photo
Thumbnail

IMG00173-20100805-1030

"Always remind customer to make sure to mark out location of piping before covering!! The infrared…"
9 hours ago
Al Tibbs commented on Eric Aune's photo
10 hours ago
Joe is now a member of Home Energy Pros Forum
16 hours ago
Liam Smith replied to Silas Inman's discussion Best Energy Myths
"Yes incandescent bulb are very heat productive. Instead of that use LED bulb which are energy…"
18 hours ago
Kelly Vaughn's blog post was featured

How Cities Can Ensure Better Rentals for Everyone

By Alisa PetersenWhile much of RMI’s research and analysis on home energy performance has focused…See More
18 hours ago
Brett Little's event was featured

Resilient Design in an Age of Climate Change - Free CE Webinar at Webinar Online

May 30, 2018 from 12pm to 1:15pm
A changing climate, sea level rise, drought, and a wide range of stresses in the world are…See More
18 hours ago
Cody Farmer liked Jim Gunshinan's blog post Highlights from the 2018 HPC National Home Performance Conference in Philadelphia
20 hours ago
Rick Barker is now a member of Home Energy Pros Forum
yesterday
David Keefe's video was featured

A Climate Report From The Field - Keefe

"A Climate Report from the Field" by David Keefe. Part of a TED-inspired evening session at the HPC Home Performance Conference, Philadelphia PA, April 25, 2018
yesterday
Bob Krell's video was featured

Carbon Monoxide Webinar with Bill Spohn - Healthy Indoors Show- Special Live Edition 4-16-18

Guest Bill Spohn, of Tru Tech Tools, joins host Bob Krell, to discuss Carbon Monoxide (CO) in the indoor environment. This show is a recording of a live webinar event on April 16, 2018.
yesterday
David Keefe posted a video

A Climate Report From The Field - Keefe

"A Climate Report from the Field" by David Keefe. Part of a TED-inspired evening session at the HPC Home Performance Conference, Philadelphia PA, April 25, 2018
yesterday
John White posted a blog post

What to Expect from a New HVAC Unit Installation Cost

The cost of installing an HVAC unit, such as an air conditioner installation in Laguna Hills, will…See More
Tuesday
Kelly Vaughn posted a blog post

How Cities Can Ensure Better Rentals for Everyone

By Alisa PetersenWhile much of RMI’s research and analysis on home energy performance has focused…See More
Monday
Brett Little posted an event

Resilient Design in an Age of Climate Change - Free CE Webinar at Webinar Online

May 30, 2018 from 12pm to 1:15pm
A changing climate, sea level rise, drought, and a wide range of stresses in the world are…See More
Monday
John Oxford posted a blog post

Make 2018 The Year You Fear No Power Outage

Get A Back-Up Generator For Your Home’s “Mission Critical” Power Needs…See More
Monday
Diane Chojnowski posted a discussion

California's new solar roof mandate

There's an interesting article in GreenTech Media about California's new solar roof…See More
Monday
Ron Jones joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
Monday
Ron Jones joined Diane Chojnowski's group
Thumbnail

News & Announcements

Share your news and announcements with the community in this group.To post news or an announcement,…See More
Monday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service