what made this chimney fall down?  

2 years after a 80% furnace was put in.  Over sized heating system after building sealed

Tags: a, chimney, flue, liner, stone, tile, with

Views: 306

Reply to This

Replies to This Discussion

Gravity?

With so little information, this is like a stump the chump from BPI.  A picture would be nice...

I would think it is likely that the furnace was over sized for the demand and short cycled.  The short cycling will not heat up the chimney enough to purge the condensation so the water is absorbed into the masonry.  Repeated cycles of freeze and thaw will cause the mortar and the bricks to fail.

It is oversized only if you have performed a load calc.  Otherwise who knows if it is right or wrong sized.  Even if it is the correct size, an 80 % furnace vented into a an unlined chimney will condence.  That will happen at a greater rate when the chimney is in a cold attic.  If the house was sealed, then the attic is colder yet and the condensate will condense at a faster rate.    

It is a classic.  The chimeny was probably failing before the air sealing and before the furnace was installed.  Assuming that there was a furnace there before.  The change in the house probably made the falure more rapid.  It will happen even if the furnace is correctly sized, under or oversized.  The system was just installed incorrectly.  

This extremly accurate opinion has been reached by taking a question with no facts provided to its logical conclusion.   If you can measure it, you can quantify it, if you can quantify it you can compare it to what is normal and  only then can you diagnose the issue and apply the correct remedy.

If you want a factual answer ---- provide facts 

Eric, if you provide a little more information, we can sleuth the answer for you.

-- Age of house?

-- what kind of chimney materials (Brick, stone, CMU, etc.)

-- Climate where this house is?

Chances are if it's an older house (70-100 + years), then the mortar was already failing.  We see these everywhere in the Bay Area, and the furnace has nothing to do with them.  There should be a flue liner, if this chimney connects to other sources, like a wood burning fireplace.

A natural gas furnace vent doesn't put any pressure on the chimney; the water from the combustion wouldn't affect the mortar unless the chimney was blocked and not venting properly -- but then you'd have CO problems, which you haven't indicated.

Pictures and more information would be helpful.

the house was build in Kansas City MO in 1903.   4710 Degrees days with about 65 days gets under 32'.  All stone with a 18"X18" clay liner  that had a 850,000 BTU boiler now just a 120,000 up flow 80% with that main floor now has a heat loss of just 42,000 BTU at 0' out side.  So the furnace is 3 times over sized and the flue should be 5" liner.  The stone chimney  heat up  about one foot each time its start up.   The dew point with flue gas is 255'  stone chimney does not get up to temp unless some one turns up the heat  or leaves the main door open.   The chimney stays wet and some time goes though the freese with lack of being in building.   After 2 year with a 80% furnace  the chimney started to fall.   The boiler had a 7" flame to light the burners and to keep the flue hot.   

   I did not see any reference to acidity in the condensate. The acidity will quickly damage the masonry joints. This is why liners and exhaust lines are nearly always acid resistant. This is why the condensate drains are neutralized with limestone prior to going down the drain. There were many problems in the early days of high efficiency boilers when the new boiler was just plugged in to the existing masonry chimney.

I see each day that acidity can rot masonry, so keep the flue gas above the dew point.   around 255' and above with natural gas will keep flue gas above dew point.   I have seen cast iron floor drain flake apart in one winter with a 90% boiler.

RSS

Forum Discussions

Low Leakage home with cathedral ceiling

Started by Dav Camras in General Forum. Last reply by David Butler on Friday. 3 Replies

2005 EPAct tax credit

Started by Mandy Leazenby in General Forum. Last reply by Mandy Leazenby on Thursday. 2 Replies

ASHRAE 62.2 Help

Started by Melissa Baldridge in HVAC. Last reply by Melissa Baldridge Dec 1. 5 Replies

Latest Activity

Dan Phillips replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"I've had my Sense for over a year now.  If you have a driven person that wants to engage…"
1 minute ago
Scott Katznelson replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"I’ll be watching to see what people say... the only whole house monitor I’ve used was…"
49 minutes ago
Chris Woods liked Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
51 minutes ago
Chris Woods liked Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
51 minutes ago
Horace Douglas Hunt, Jr. replied to Travis Freethy's discussion Blower Door & Duct blaster for sale. in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"is this still for sale?"
yesterday
Jim Ballman is now a member of Home Energy Pros Forum
Saturday
Tim replied to Shawna Henderson's discussion Exterior Insulation for Deep Energy Retrofits
"Hey Shawna, Have you worked with thermal insulation coatings? They are normally a modified…"
Saturday
David Butler replied to Dav Camras's discussion Low Leakage home with cathedral ceiling
"With a vented cathedral ceiling, getting a tight envelope is difficult, but not impossible. Various…"
Friday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service