what made this chimney fall down?  

2 years after a 80% furnace was put in.  Over sized heating system after building sealed

Tags: a, chimney, flue, liner, stone, tile, with

Views: 385

Reply to This

Replies to This Discussion

Gravity?

With so little information, this is like a stump the chump from BPI.  A picture would be nice...

I would think it is likely that the furnace was over sized for the demand and short cycled.  The short cycling will not heat up the chimney enough to purge the condensation so the water is absorbed into the masonry.  Repeated cycles of freeze and thaw will cause the mortar and the bricks to fail.

It is oversized only if you have performed a load calc.  Otherwise who knows if it is right or wrong sized.  Even if it is the correct size, an 80 % furnace vented into a an unlined chimney will condence.  That will happen at a greater rate when the chimney is in a cold attic.  If the house was sealed, then the attic is colder yet and the condensate will condense at a faster rate.    

It is a classic.  The chimeny was probably failing before the air sealing and before the furnace was installed.  Assuming that there was a furnace there before.  The change in the house probably made the falure more rapid.  It will happen even if the furnace is correctly sized, under or oversized.  The system was just installed incorrectly.  

This extremly accurate opinion has been reached by taking a question with no facts provided to its logical conclusion.   If you can measure it, you can quantify it, if you can quantify it you can compare it to what is normal and  only then can you diagnose the issue and apply the correct remedy.

If you want a factual answer ---- provide facts 

Eric, if you provide a little more information, we can sleuth the answer for you.

-- Age of house?

-- what kind of chimney materials (Brick, stone, CMU, etc.)

-- Climate where this house is?

Chances are if it's an older house (70-100 + years), then the mortar was already failing.  We see these everywhere in the Bay Area, and the furnace has nothing to do with them.  There should be a flue liner, if this chimney connects to other sources, like a wood burning fireplace.

A natural gas furnace vent doesn't put any pressure on the chimney; the water from the combustion wouldn't affect the mortar unless the chimney was blocked and not venting properly -- but then you'd have CO problems, which you haven't indicated.

Pictures and more information would be helpful.

the house was build in Kansas City MO in 1903.   4710 Degrees days with about 65 days gets under 32'.  All stone with a 18"X18" clay liner  that had a 850,000 BTU boiler now just a 120,000 up flow 80% with that main floor now has a heat loss of just 42,000 BTU at 0' out side.  So the furnace is 3 times over sized and the flue should be 5" liner.  The stone chimney  heat up  about one foot each time its start up.   The dew point with flue gas is 255'  stone chimney does not get up to temp unless some one turns up the heat  or leaves the main door open.   The chimney stays wet and some time goes though the freese with lack of being in building.   After 2 year with a 80% furnace  the chimney started to fall.   The boiler had a 7" flame to light the burners and to keep the flue hot.   

   I did not see any reference to acidity in the condensate. The acidity will quickly damage the masonry joints. This is why liners and exhaust lines are nearly always acid resistant. This is why the condensate drains are neutralized with limestone prior to going down the drain. There were many problems in the early days of high efficiency boilers when the new boiler was just plugged in to the existing masonry chimney.

I see each day that acidity can rot masonry, so keep the flue gas above the dew point.   around 255' and above with natural gas will keep flue gas above dew point.   I have seen cast iron floor drain flake apart in one winter with a 90% boiler.

RSS

Forum Discussions

Mini split air conditioners and ceiling fans

Started by Beverly Lerch in General Forum. Last reply by Blake Reid 10 hours ago. 12 Replies

Think of the house as a really big duct

Started by Frank Spevak in HVAC. Last reply by Franco Oyuela yesterday. 1 Reply

What's the Most Profitable HVAC Job for Your Company?

Started by Wayne Melancon in HVAC. Last reply by Franco Oyuela yesterday. 4 Replies

Mini split installation location

Started by Jan Green in HVAC. Last reply by David Butler on Monday. 1 Reply

Latest Activity

Blake Reid replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Good opinions in these replies!  I'll just add a few: * Experiment.  It's your…"
10 hours ago
John White replied to Jerry Needham's discussion Condensation on ceiling and walls of master bedroom
"Condensation on ceiling occurs when the attic space above is poorly ventilated or insulated. The…"
21 hours ago
Joshua P Murphy is now a member of Home Energy Pros Forum
yesterday
Franco Oyuela replied to Frank Spevak's discussion Think of the house as a really big duct
"THANKS for the information. Ducted mini splits offer hidden benefits."
yesterday
Franco Oyuela replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"Get into commercial, it's more money!"
yesterday
David Byrnes's video was featured

Why One Room Is Hotter Than Others

Ever wonder if your air conditioner is working right because one room never gets a cool or warm as others? Do you need a bigger air conditioner to fix a room...
yesterday
Profile IconEric MacCallum, Adam Morgan and Caolan Hutchens joined Home Energy Pros Forum
Monday
David Butler replied to Jan Green's discussion Mini split installation location
"Really hard to advise without knowing the layout. But you're asking good questions. Any chance…"
Monday
Jan Green posted a discussion

Mini split installation location

Reaching out to the experts today to ask about location of installation of a mini split.  I'm a…See More
Monday
David Butler replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Among the various opinions expressed here, I offer a few 'truths'... Ceiling fans are…"
Monday
Walter Ahlgrim replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"This is one of thouse topic where you ask 10 people and get 12 different opinions. I will give you…"
Monday
Brett Little's event was featured
Thumbnail

Full Circle Urban Forestry: Introducing Urban Wood Opportunities - Free CE Webinar at Webinar Online

October 17, 2018 from 12pm to 1:15pm
Many common urban tree removal practices in the United States view felled urban trees as costly…See More
Monday
Beverly Lerch replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Now I am confused.  Everyone has a different opinion.  "
Monday
Joseph Novella replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Don't use the fans! They generate heat and mix the stratified high warm air with the low cool…"
Monday
John White replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"If you are using air conditioning, a ceiling fan will allow you to raise the thermostat setting…"
Monday
John White posted a blog post
Monday
Profile IconDana Launius and Susan Dee Cummins joined Home Energy Pros Forum
Sunday
Linda Wigington liked Don Fugler's discussion Depressurization/make-up air issues
Sunday
Profile IconCourteney Hazard, Erin Kelly, Megan Bailey and 3 more joined Home Energy Pros Forum
Friday
Kent Browning replied to Julie Saporito's discussion Tankless water heating and existing gas lines
"First the problems - increased CO due to poor combustion, flue condensation delayed ignition, etc.…"
Friday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service