Two-stage furnace, control at furnace or thermostat?

Got called in recently to address thermostat and comfort issues for a local builder we work with. In reconfiguring the thermostat (Ecobee Smart Si), I noticed that it was wired up as a single stage for heating, although the furnace (Carrier 59TP6) is a two-stage model - that is, furnace staging decisions are made at the furnace control board, not by the thermostat. I've tried contacting Carrier, but haven't found anyone who can explain the furnace control board logic w/ respect to staging.

In examining several other recently finished houses for this builder, I've seen the same thermostat wiring setup (had never thought to check it prior to the last month). I'd expect better comfort and efficiency when furnace staging was controlled by the thermostat, particularly a "smart" thermostat. Just wondering if anyone has any thoughts on this before I talk with the builder & HVAC subs about this.

Views: 920

Reply to This

Replies to This Discussion

I'm not sure about the Ecobee Smart Si (I couldn't immediately find the install manual) but this FAQ (http://bit.ly/2Cf2UsR) describes Ecobee's staging logic -- it's selectable based on either elapsed time or temperature 'droop'.

Most modern thermostats use a PID algorithm for staging -- essentially this looks at the rate and direction of the temperature change. This is especially important for supplemental heat staging on a heat pump, not so much for a furnace. With a furnace, premature upstaging could have a slight to moderate impact on comfort (depending on how badly the furnace is oversized) but will have little impact on efficiency.

I'm not familiar with that furnace's internal staging logic. You should be able to find the install manual via Google search. But since it doesn't know the zone temperature setpoint, it's almost certainly based on time, and may be selectable.

Without the option of PID staging, I would prefer 1F droop over a fixed time delay. If you confirm the Ecobee Si works as described in the FAQ, it could easily be wired to stage the furnace based on a 1F temperature difference.

Is the A/C single stage?

David's comment is spot on. I would always prefer thermostat staging control over furnace staging control. (I am assuming the thermostat is making and breaking the control call for heating - not communicating the temperature back to the furnace controls. This may be a bad assumption with communicating system. It is a good assumption with a standard red =24V / yellow = cooling / green =blower / white = 1st stage heat)

Unless the furnace controls know the temperature and set point, the only thing it can use to bring on second stage heat is run time of 1 stage heat. So it may turn on second stage just as the set point is reached (causing larger temperature swing) or wait a long time in first stage before bringing on second stage (delaying reaching set point). Either way, the customer is not getting the comfort they have paid extra for.

Thanks for the quick feedback, David. I did find the furnace install manual earlier; there's no detail (that I was able to find) on staging logic or adjusting staging timing. Glad to understand the typical thermostat staging in a bit more detail - I'll try to track down the manual for this model.

The A/C is single stage, so no accompanying concerns about humidity management w/ respect to staging.

I hate to be the one to bring this up, but two stage furnaces are quite capable of having lower installed efficiency than single stage furnaces with the same max input. This comes from two sources: 1) the fuel air mixture on low fire often has too much air. 2) the increased resident time of the conditioned air in the ducts increases duct losses.  

Similar issues exist for two speed ACs

Attachments:

Thanks, John. The HVAC installers have actually responded to incentives and moved ducts within the building envelope on the vast majority of the furnaces we see, so losses to unconditioned space are less of a concern for us. Thanks for bringing up the issue of fuel air mixture.

Set up for 1st stage to run at highest eff.   With my set up will run on 1st stage 93% of time.   Use a high end flue gas meter and set up for max eff.   

@Tray, the staging logic is described on pg 85 of the furnace installation manual. In particular, here's what it says:

"This furnace can operate as a two--stage furnace with a single-stage thermostat because the furnace control CPU includes a programmed adaptive sequence of controlled operation, which selects low-heat or high-heat operation. This selection is based upon the stored history of the length of previous gas-heating periods of the single--stage thermostat.

"The furnace will start up in either low-- or high--heat. If the furnace starts up in low--heat, the control CPU determines the low--heat on--time (from 0 to 16 minutes) which is permitted before switching to high-heat."

This is better than straight timing option in the Ecobee. I'm not sure if it's better than setting a 1F degree staging temperature differential (droop). At least with the latter, the homeowner can get their mind around what it's supposed to do.

As a side note, I find that most furnaces are seriously oversized. If you suspect that might be the case, you could recommend to the homeowner to disable the high stage (SW1, position 2 ON, W2 not connected). If low stage can handle the load, great. If not, SW1-2 simply needs to be flipped back to OFF to enable the furnace staging logic (or, alternatively, connect Ecobee W2 to furnace W2 and set thermostat for 2-stage ops, leaving SW1-2 ON).

If ducts are in unconditioned space, I agree with John that low stage ops imposes an efficiency hit (low velocity in a duct system sized for cooling capacity increases conducted losses). Operating at high stage becomes a trade-off between efficiency and comfort. On the other hand, if ducts are in conditioned space, it's simple enough to have the tech verify optimal mixture in low stage, as suggested by Eric. Have your cake and eat it, too.

We use reverse staging on ecobee.

Generally, the best comfort, energy savings, iaq, etc are achieved by doing what you can to avoid having the equipment ever shut off.

We suspect among other things, start/stop losses are significant.

If the enclosure or duct really suck this approach can have surprising failures, so make sure you are significantly fixing things when using this approach.

Ted -- The startup losses on modern furnaces are much smaller than the old days. I would suggest a modification to your statement to: "if the ducts are normal and in unconditioned space then the losses exceed the gains from long run times". 

There are two papers by Krishnamoorthy, Modera, and Harrington tthat tested the effect of longer air residence time in (standard insulation standard surface area and minimal leaks) ducts in the attic. The results for a variable speed air conditioner showed a delivery effectiveness dropping from .73 at 100% flow and capacity to .40 at 40% flow and capacity when the attic temperature was 115F. The increased loss was significant even at 84F attic temperature.  

I was playing with a 2 stage carrier furnace last week.  The staging is not bad on the condensing boilers.  They camp out at low fire until the return air temp drops or they get past 5 minutes of run time.  I am fine with them doing it this way.  As long as the thing isn't way oversized, it should be fine.

I installed/configured a couple Honeywell VisionPro 8k models recently in a commercial facility. It has governing ability for 4 stages of heat and 2 of cool. It triggers out from 1st stage when sensing 90% capacity of the furnace.  

RSS

Forum Discussions

Overheating garage

Started by Chris Bellanca in Best Practices 1 hour ago. 0 Replies

GSHP for domestic hot water

Started by David Holtzclaw in General Forum. Last reply by David Holtzclaw 4 hours ago. 3 Replies

Log home roof insulation

Started by Bob Reuther in Best Practices. Last reply by Daniel Baur-McGuire yesterday. 8 Replies

Latest Activity

Chris Bellanca posted a discussion

Overheating garage

Hi all, I'm looking for potential solutions to a problem at a client's house.  The south facing 2…See More
1 hour ago
Landon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Brand new retrotec blower door system $3000

Hi, I’ve got a brand new blower door system from retrotec that I got 2 months ago, and never got…See More
1 hour ago
John Redmond posted discussions
1 hour ago
David Holtzclaw replied to David Holtzclaw's discussion GSHP for domestic hot water
"Thanks John & Bill. Bill your experience is one reason why I wanted a larger heat pump with…"
4 hours ago
John White posted photos
13 hours ago
Diane Chojnowski posted events
yesterday
Rob commented on Bob Krell's group Healthy Indoors (IAQ)
"Hello, Has anyone tried custom filtering of window AC units? Specifically concerned with…"
yesterday
Michael Dunseith's 2 photos were featured
yesterday
Franco Oyuela commented on Perry Ning's blog post Warnings About Portable Air Conditioners
"Here are the top five benefits of owning a portable air conditioner: 1. Low Price – All…"
yesterday
Daniel Baur-McGuire commented on Kurt Shafer's status
"Whole house fans are a scam if you use air conditioning. Seriously "
yesterday
Daniel Baur-McGuire commented on Michael Dunseith's photo
Thumbnail

NYC DEPT OF BUILDINGS TR8 ENVELOPE TESTING

"Looks fun. How did you connect all the fans together or did you adjust the flows manually? The…"
yesterday
Daniel Baur-McGuire replied to Bob Reuther's discussion log home roof insulation
"I would look to stop air from penetrating the ceiling. I would guess hot air is able to rise…"
yesterday
Jay Lillien posted a blog post

How Changing Temps Affect Your Home’s Windows

In Colorado, there’s a time-honored saying:“If you don’t like the weather, just wait a few minutes……See More
Tuesday
Matt Peiris replied to H.O. Electric's discussion Stop Drinking Bottled Water! in the group News & Announcements
"Cities like Los Angeles now use chlorine AND chloramine to treat their water. While chlorine can be…"
Tuesday
Matt Peiris joined Diane Chojnowski's group
Thumbnail

News & Announcements

Share your news and announcements with the community in this group.To post news or an announcement,…See More
Tuesday
Michael Dunseith posted photos
Tuesday
Ron Jones added a discussion to the group Job Board
Thumbnail

Residential Construction Superintendent for Net Zero Energy Homes: Northern California

At Acre Designs (acre.co), we're bringing Net Zero Energy homes into the 21st century, and we're…See More
Monday
Kim added a discussion to the group Job Board
Thumbnail

Job Opening - New Construction Specialist - Philadelphia or Pittsburgh, PA Location

New Construction SpecialistAre you looking for a collaborative work environment, colleagues who are…See More
Monday
Profile IconSteve, Todd Crawford and Evangeline Spence joined Home Energy Pros Forum
Monday
Steve liked Alex Jonson's discussion Constant Airflow Regulator
Monday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service