Looking for some help troubleshooting this furnace blower issue!

Carrier Model 58CTX070

Furnace is not delivering much air to supply grills and is shutting itself off every 10 minutes.

Why is it not moving enough air

Here are the results of my initial tests:

  • Tripping the Limit Switch
    • Error code = 33
    • After 5 minutes of heat.
    • Supply air temp climbs to 175 F
    • Temp rise is over 100 degrees at low setting
    • Design is 30-60 degrees for temp rise
    • After furnace cools, the limit switch appears to close again, and the furnace cycles back on, only to repeat process.
  • Low total static pressure.
    • 0.1 wc total. 
    • Very low airflow at the supply grills 
    • Ruling out duct obstructions because of low SP
  • Trpping the Limit Switch after 5 minutes of firing
    • Supply air temp climbs to 175 F
    • Temp rise is over 100 degrees at low setting
    • Design temp rise is 30-60 degrees
  • Blower speed does not seem to change in response to changing the speed tap wires.
    • No change in static pressure at supply
    • No change in air temp at supply
  • Took out blower and cleaned it thoroughly
    • No change in symptoms
    • Squirrel cage turns smoothly with zero noise or resistance

What's the problem? 

  • Burnt out motor windings? Is there a way to confirm/test this?
  • Bad capacitor?
  • Bad circuit board?

Thanks for any help!

Bachi Brunato

bachi brunato
making your home strong, healthy & agile
providing comfort & energy savings with a smart green approach!
bachi@ultimatehomeperformance.com
510-936-1212 
lic# 946742
lic# 740545
bpi# 5008123

Tags: Blower

Views: 3238

Attachments:

Reply to This

Replies to This Discussion

I'm thinking your static reading may be off, are you testing below or above the A-coil? Pressure drop across the coil alone should be more than .1". What is the amp draw on the motor? Does the motor seem to be "running hard", slow or OK? Do you have access to verify a clean A-coil?

No AC coil on this unit. Just a gas burner and heat exchanger.

Supply SP is 0.035 wc.

Return SP is 0.070 wc.

Amp draw on the motor:

   @ black wire: 7.2 and falling. Went down to 5.35 amps while I was watching.

   @ yellow wire: 4.07

   @ blue wire: 3.42

   @ red wire: 2.76

Motor seems to be running slow, smooth & quiet.

I just tested the run capacitor. Its only showing 0.5 MFD. See photo. Also, put an digital ohm meter on the capacitor. It did not rise up to a number like 200 and then fall back to OL. It just stayed at a very low number. 

I'd like to test the motor windings... Haven't figured out the procedure just yet. Must be a way to determine if they are burned or partially shorted.

I've installed a few systems, but I'm not an HVAC tech. I am curious and wanting to learn more about all this, so I'm motivated to figure it out. Researching motor winding test protocols now.

Attachments:

Looks like you found your problem, shorted capacitor.

I've heard that the capacitor and motor can go out at the same time.

Eg: a bad motor can damage the capacitor and a bad capacitor can damage the motor.

It's possible but unlikely for a motor to damage the capacitor. A bad cap can burn up a motor if not promptly replaced. Capacitors are under $15, buy one and put it in.

Typical 5UF Capacitor

replace the motor from a PSC  with an after market ECM  evergreen or like.  You may have to change braket or holder for the motor as the ECM take more tork and brake welds.   eff changes from 25-35% to 60-75%.  If the SP is to high (.91" WC or higher) the ECM  just over heats and burns the back up - heat kills-.    If you see the oil spots on bottom and the bearing are gone it likely over heated.  there is saw dust and some fiber around the brass oil bearing when the oil is gone 3-6 mo later so is the motor.  Eric Kjelshus HVAC   www.ericsenergy.com

Payback isn't there unless customer runs fan 24/7, has high utility rates or already has a bad PSC motor.

Just Ohm tested all the motor leads. They all look good. Problem seems to be limited to the capacitor only.

Ordered a 7.5 uf, 370A capacitor. 

Will post results when I get it installed.

I get 440 volt Capacitor,  now  with lack of size lack of  oil in new caps the leads over heat and burn out. new caps are just 1/5 the size of 25 yr ago.  

 If the end play is to much the OHM change when moving the shaft and still burn out .  with power off Take  your fingers and see how much play is on shaft more than 3/8" then plan on replacement.  www.ericsenergy.com

In a 240v circuit I 100% agree on the 440v caps. On a 120v circuit a 370v is plenty.

Turns out it was the capacitor.

Installed a new one and all systems are back on track.

Total static pressure is up to 0.46 wc now.

Temp rise is down to 51°F.

High limit switch is no longer tripping.

Blower motor is running smooth and strong.

$5 part.

Happy client.

Figured that would fix it :)

RSS

Forum Discussions

Why is Air Sealing Important?

Started by Cameron Home Insulation in General Forum 1 hour ago. 0 Replies

Greetings :)

Started by Dennis in General Forum. Last reply by Diane Chojnowski 16 hours ago. 2 Replies

Electro Magnetic Fields (EMF)

Started by Barry L NewDelman in General Forum. Last reply by Brad Cook 16 hours ago. 12 Replies

Zehnder Comfopipe vs. rigid pipe

Started by Alan Lehman in HVAC yesterday. 0 Replies

Follow the action at HPC 2018

Started by Diane Chojnowski in General Forum yesterday. 0 Replies

Latest Activity

Cameron Home Insulation posted a discussion

Why is Air Sealing Important?

Hello guys, Tell me, Why is Air Sealing Important? Share your views.Why is Air Sealing Important?See More
1 hour ago
Ryan T De La Rosa posted a blog post

Home Energy Savings In An Unlikely Place

When thinking of the best way to save mother nature, it's likely that the last thing on your mind…See More
8 hours ago
Taylor Joseph Mckay replied to Taylor Joseph Mckay's discussion Seeking to Purchase Blower Door in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"please shoot me an email taylor.joseph.mckay@gmail.com"
10 hours ago
Diane Chojnowski replied to Dennis's discussion Greetings :)
"Welcome Dennis! Great to have you join us! "
16 hours ago
Brad Cook replied to Barry L NewDelman's discussion Electro Magnetic Fields (EMF)
"Whoa! EMFs are everywhere, but they are not all equal. The characteristics of EMFs varies very much…"
16 hours ago
Ben Thompson replied to Taylor Joseph Mckay's discussion Seeking to Purchase Blower Door in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Taylor.  I have a Minneapolis Blower Door set up for sale. DG-700 manometer was factory…"
17 hours ago
Arn McIntyre replied to Taylor Joseph Mckay's discussion Seeking to Purchase Blower Door in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Taylor I have item described below for sale.  Pictures are posted in Equipment for…"
17 hours ago
Taylor Joseph Mckay added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Seeking to Purchase Blower Door

Hi, I'm getting into energy audits and am looking to save a few bucks on picking up a used blower…See More
18 hours ago
Taylor Joseph Mckay joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
18 hours ago
Sandra James replied to Barry L NewDelman's discussion Electro Magnetic Fields (EMF)
"I am quite interested in how EMF can cause health issues.  There is no question that too much…"
18 hours ago
Sandra James replied to Dennis's discussion Greetings :)
"Hello There, I am new as well. Hoping to learn new things through the course of this time on this…"
18 hours ago
Profile IconJames Sabal, Ethan Foley and Katelyn Haas Conrad joined Home Energy Pros Forum
19 hours ago
Alan Lehman posted a discussion

Zehnder Comfopipe vs. rigid pipe

Hello All,I have installed few Zehnder systems and I am not sure if my rep is giving me the info I…See More
yesterday
Diane Chojnowski posted a discussion
yesterday
Brett Little's 2 events were featured
yesterday
Profile IconSandra James, arthur wilson, Nolan and 4 more joined Home Energy Pros Forum
yesterday
Landon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

BRAND NEW: Fantastic Software for Retrotec

I purchased a new blower door system from retrotec and it came with the fantestic software.…See More
Monday
CEE posted a blog post
Monday
CEE's blog post was featured
Monday
Brett Little posted events
Saturday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service