Looking for some help troubleshooting this furnace blower issue!

Carrier Model 58CTX070

Furnace is not delivering much air to supply grills and is shutting itself off every 10 minutes.

Why is it not moving enough air

Here are the results of my initial tests:

  • Tripping the Limit Switch
    • Error code = 33
    • After 5 minutes of heat.
    • Supply air temp climbs to 175 F
    • Temp rise is over 100 degrees at low setting
    • Design is 30-60 degrees for temp rise
    • After furnace cools, the limit switch appears to close again, and the furnace cycles back on, only to repeat process.
  • Low total static pressure.
    • 0.1 wc total. 
    • Very low airflow at the supply grills 
    • Ruling out duct obstructions because of low SP
  • Trpping the Limit Switch after 5 minutes of firing
    • Supply air temp climbs to 175 F
    • Temp rise is over 100 degrees at low setting
    • Design temp rise is 30-60 degrees
  • Blower speed does not seem to change in response to changing the speed tap wires.
    • No change in static pressure at supply
    • No change in air temp at supply
  • Took out blower and cleaned it thoroughly
    • No change in symptoms
    • Squirrel cage turns smoothly with zero noise or resistance

What's the problem? 

  • Burnt out motor windings? Is there a way to confirm/test this?
  • Bad capacitor?
  • Bad circuit board?

Thanks for any help!

Bachi Brunato

bachi brunato
making your home strong, healthy & agile
providing comfort & energy savings with a smart green approach!
bachi@ultimatehomeperformance.com
510-936-1212 
lic# 946742
lic# 740545
bpi# 5008123

Tags: Blower

Views: 3132

Attachments:

Reply to This

Replies to This Discussion

I'm thinking your static reading may be off, are you testing below or above the A-coil? Pressure drop across the coil alone should be more than .1". What is the amp draw on the motor? Does the motor seem to be "running hard", slow or OK? Do you have access to verify a clean A-coil?

No AC coil on this unit. Just a gas burner and heat exchanger.

Supply SP is 0.035 wc.

Return SP is 0.070 wc.

Amp draw on the motor:

   @ black wire: 7.2 and falling. Went down to 5.35 amps while I was watching.

   @ yellow wire: 4.07

   @ blue wire: 3.42

   @ red wire: 2.76

Motor seems to be running slow, smooth & quiet.

I just tested the run capacitor. Its only showing 0.5 MFD. See photo. Also, put an digital ohm meter on the capacitor. It did not rise up to a number like 200 and then fall back to OL. It just stayed at a very low number. 

I'd like to test the motor windings... Haven't figured out the procedure just yet. Must be a way to determine if they are burned or partially shorted.

I've installed a few systems, but I'm not an HVAC tech. I am curious and wanting to learn more about all this, so I'm motivated to figure it out. Researching motor winding test protocols now.

Attachments:

Looks like you found your problem, shorted capacitor.

I've heard that the capacitor and motor can go out at the same time.

Eg: a bad motor can damage the capacitor and a bad capacitor can damage the motor.

It's possible but unlikely for a motor to damage the capacitor. A bad cap can burn up a motor if not promptly replaced. Capacitors are under $15, buy one and put it in.

Typical 5UF Capacitor

replace the motor from a PSC  with an after market ECM  evergreen or like.  You may have to change braket or holder for the motor as the ECM take more tork and brake welds.   eff changes from 25-35% to 60-75%.  If the SP is to high (.91" WC or higher) the ECM  just over heats and burns the back up - heat kills-.    If you see the oil spots on bottom and the bearing are gone it likely over heated.  there is saw dust and some fiber around the brass oil bearing when the oil is gone 3-6 mo later so is the motor.  Eric Kjelshus HVAC   www.ericsenergy.com

Payback isn't there unless customer runs fan 24/7, has high utility rates or already has a bad PSC motor.

Just Ohm tested all the motor leads. They all look good. Problem seems to be limited to the capacitor only.

Ordered a 7.5 uf, 370A capacitor. 

Will post results when I get it installed.

I get 440 volt Capacitor,  now  with lack of size lack of  oil in new caps the leads over heat and burn out. new caps are just 1/5 the size of 25 yr ago.  

 If the end play is to much the OHM change when moving the shaft and still burn out .  with power off Take  your fingers and see how much play is on shaft more than 3/8" then plan on replacement.  www.ericsenergy.com

In a 240v circuit I 100% agree on the 440v caps. On a 120v circuit a 370v is plenty.

Turns out it was the capacitor.

Installed a new one and all systems are back on track.

Total static pressure is up to 0.46 wc now.

Temp rise is down to 51°F.

High limit switch is no longer tripping.

Blower motor is running smooth and strong.

$5 part.

Happy client.

Figured that would fix it :)

RSS

Latest Activity

Chris Dorsi posted an event
Thumbnail

2018 Habitat X Summer National Conference at Big Sky Montana

June 27, 2016 to June 29, 2016
The 2018 Habitat…See More
7 hours ago
Stuart Langley liked David Byrnes's blog post Strategies for Hiring and Interviewing for Home Performance Professionals
11 hours ago
Kevin Miller replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Visual inspection can only confirm the presence of mold, not the absence.   That said,…"
14 hours ago
Armand C Magnelli replied to Don Fugler's discussion joining ducts in the group HVAC
"I often suggest pop-rivets as an alternative to sheet metal screws for both clothes dryer duct work…"
14 hours ago
Kevin Miller replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Sampling would be primarily to verify 'Condition 1' or 'Normal Fungal Ecology'…"
15 hours ago
Daniel Cullen joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
15 hours ago
Daniel Cullen replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Can anyone tell me exactly HOW mold sampling impacts the mold remediation process or protocol? Why…"
15 hours ago
Daniel Cullen joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
15 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service