Technical question about mini split heat pump line set maximum length

Hello!

I'm installing a two-zone Mitsubishi mini split (in Pasadena, CA area, 1400 sf, single family detached, one-story home, if context is relevant). This is my first install, and I am trying to determine if extra refrigerant needs to be added based on the line set distance to each of the two indoor units. The outdoor unit is factory charged with R410A.

Outdoor Unit - MXZ-2C20NAHZ2

Indoor Unit 1 - PEAD-A12 (pipe length distance from outdoor unit: ~25 feet)

Indoor Unit 2 - MSZ-FH12NA (pipe length distance from outdoor unit: ~40 feet)

The manual (attached image) for the outdoor unit (MXZ-2C20NAHZ2) says "Max. pipe length per indoor unit for multi system" is 82 ft, and that refrigerant adjustment for longer lengths is 1.08 oz/5 ft. The manual for indoor unit 1 says maximum pipe length is 23 feet (before additional refrigerant is required). The manual for indoor unit 2 says maximum pipe length is 25 feet (before additional refrigerant is required). So...I'm trying to determine which number is applicable -- 82, 23, or 25? Does the system need additional charge?

I'll contact the manufacturer as well, but I thought I'd ask here in case anyone has installed one of these systems and already determined the answer to this question. Thanks for your help.

Views: 1035

Attachments:

Reply to This

Replies to This Discussion

Hi Chris!

  I just happened to come across your question after I posted my most recent blog - Mitsubishi Ductless happens to be my specialty (and full-time job)!

  That condenser is pre-charged for 98' of pipe.

  Each zone can be a max 82' from the condenser.

  Total pipe length would be 164' (82 x 2).

I think the confusion regarding the 23/25 comes in if you are installing these as single zone systems...always check the install manual for the condenser on mylinkdrive.com : http://meus1.mylinkdrive.com/item/MXZ-2C20NAHZ2-U1.html

Hope you have a successful install, and a Happy New Year!

Chris

Chris,

A million thanks! This is very helpful; thank you for sharing your expertise. I can post an update once I'm further along. I am tempted to ask more questions but will not abuse your generosity. :) Happy New Year to you as well!

Chris

Hi Chris,

Thanks again for your help. Update: the system is now up and running.

Chris

RSS

Latest Activity

Dannie Jackson's blog post was featured
5 hours ago
Profile IconEric Miller, David Giusti, Melinda Zytaruk and 2 more joined Home Energy Pros Forum
5 hours ago
Daniel Baur-McGuire replied to Tim Kendzia's discussion Cooling effect from solar panels
"I would argue that keeping the solar panels cool is more important as you will produce more power.…"
9 hours ago
Daniel Baur-McGuire replied to David Meiland's discussion Air gap above floor insulation--how big is the impact?
"Im specifically thinking of floors over garage. Builders here often use rigid insulation under the…"
10 hours ago
Robert DV replied to David Meiland's discussion Air gap above floor insulation--how big is the impact?
"Why Charles!   How do you really feel??"
10 hours ago
Robert DV replied to David Meiland's discussion Air gap above floor insulation--how big is the impact?
"David, Assuming the band / rim is sealed what benefit is there to direct contact with the sub…"
10 hours ago
Sean Lintow Sr replied to David Meiland's discussion Air gap above floor insulation--how big is the impact?
"2018 IECC --- just think, you do have 6 sided encapsulation unlike an attic which see's more…"
yesterday
Mick Lane replied to David Meiland's discussion Air gap above floor insulation--how big is the impact?
"There are a few things going on here. First, if you want an idea of the effectiveness of the…"
yesterday

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service