I have an under-insulated roof above a "cathedral ceiling".  The shingles need to be replaced this year.  It occurred to me that this could be an opportunity to insulate from above.

Can it make sense to insulate above the plywood roof deck? Or to remove the plywood roof deck, add insulation, and re-install the plywood roof deck on top of that? 

Accessing the insulation from inside would require ripping down and re-installing a perfectly good ceiling.  I believe there's no more than 6-8 inches of fiberglass insulation in that ceiling, and in some places where there's an empty cavity, it appears the fiberglass has fallen out of position. 

The home is in Massachusetts.  I would love to hear from anyone on the theory and practice of doing this, and any real-world experience. 

Tags: Insulation, Retrofit, Roof

Views: 22168

Reply to This

Replies to This Discussion

Hi GW,

Is this a vented cathedral and if so where and how much venting?

What type of rafters are in there and how deep are they?

You suspect some of the insulation might have "fallen out of position", explain?  Did you look at this ceiling with an Infrared camera?

What problem/s are you addressing, ice dams, heat loss, or comfort?


Hi Bud,

The ceiling is not vented, so ice dams are occasionally a problem.  There are no soffits.

I'm not sure the depth of the rafters.  My best guess is 2 x 6". At one time, many years ago, it was probably an unheated room.

Insulation has fallen out of position over a closet and entranceway. There is empty, inaccessible space between the ceiling there and the roof.  I was able to see that when there was hole in the wall adjacent to it during an earlier renovation.  Snow melts very quickly above that area, and a little more slowly above the cathedral shaped ceiling.   The ceiling in the cathedral keeps the insulation above it in place.

As I say above, ice dams are occasionally an issue, but heat loss is the number one issue.  Comfort is not a problem, as the floors are radiant under a layer of 3/4" oak.

Hello Go.: you would only tear off plywood if it is rotted & needs replacement! The solution is to tear off the drywall, re-insulate if necessary, apply 2 inches of foam panel, and re dry wall. i've done this, so enjoy! t

I think it would be much less work to have this dealt with from above if that's possible. 

go. : right. ez way is to shoot foam using thermal detector. don't screw up venting. don't cause a "stephen girard" project like my builder did! you're right, t

I'm still not getting a good picture.  Are you talking about a flat ceiling at the top of the cathedral, the 6 to 8" of insulation.  And then 2x6 rafters which are only 5.5".

Here's what I'm looking for.  You should not have fiberglass insulation in an unvented cathedral ceiling, the rafters or attic for that matter.  Any air leakage or moisture migration will go straight to the bottom of the cold roof deck and cause damage.  If the space is truly unvented, then more information is needed to determine if there is a bigger problem already there.  In which case, now might be the best time to address the insulation and its installation.


The ceiling inside is at the same angle as the roof.  Sandwiched between the ceiling and the roof, and between the roof rafters, is a layer of insulation.  Those rafters are most likely 2 x 6. 

You are right... it is unvented, and I'm sure what you are describing is what's happening. 

From what you say, I will need to have venting added, though without soffits, I'm not sure how that might work.  If I were to have a ridge vent, moisture getting in there would not be vented out.  I suppose it might be possible to put soffit vents at the top of the wall, but I have never heard of that being done.


 Remove the shingles, drill a row of holes and use an 1 1/2 blowing tube to dense pack insulsafe fiberglass into the cavity, plug the holes add some foam board, add 1/2'" plywood over that and then reshingle with a light colored shingle. Hot roof, no air movement.

A minor note-'plywood' can be a used as a bit of a generic term for a number of products. I'd go with 5/8 OSB for the airsealing qualities. Every little bit helps.

Robert has it though I would lean more towards cellulose & don't forget to close off & seal the soffit vents

Scroll down about a 1/3 of the way & you will see that version with foam boards on the outside including a few best practices http://blog.sls-construction.com/2011/what-is-a-hot-roof 

One thing not listed there is make sure you install enough foam per code to eliminate condensation (806.4 in 2009 IRC) which looks like an R20 for you

Warm roofs only work if vapour is prevented from reaching the underside of the cold decking. Any gaps in the insulation or if it is porous will result in mould growth eventually if there is no ventilation. Plywood is a partial vapour stop so it is best located on the inside of the insulation. In the UK we fix insulation above the rafters using helical fixings and counter battens, and a breather membrane and battens under the roofing.

Insulating above the roof deck is the way to go in this case. I am completing a simular project on my house currently.

Remove the shingles, drill & fill the existing cavities with dense pack cellulose (3.5# cuft) or fiberglass. Air seal the plywood deck with tape (Siga, ProClima, ProtectoWrap, ect). If you do this it would be possible to use mineral wool above the deck, but not strictly according to the code.

Install a minumum of R-10 Rigid insulation (I seal the edges to each other with 1 part foam), more is better. Install 1/2" plywood, screwed to rafters below. (you could also add 2x4's flat for ventilation). Alternative is to buy nailbase (foam with 1/2" OSB on it). You can buy nailbase with a built in ventilation space. Venting the roofing would be preferable from several standpoints; reduce roofing temperature, and if (when it leaks it can dry out (and you can see it sooner)

Of course you will have to build up the trim on the edges (could use flashing depending).

On my house I left out the airspace, since I did not have the ability to add any more height due to another roof intersection. I also plan on painting the roof white.


Latest Activity

Landon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase

WANTED: Blower door complete set Retrotec or Minneapolis

Hi all,I'm looking for a blower door system complete, ready to go. Preferably used, unless you have…See More
7 hours ago
Landon joined allen p tanner's group

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
7 hours ago
ABAA posted an event

ABAA 2018 Conference and TradeShow at Salt Palace Convention Center

May 8, 2018 to May 9, 2018
7th Annual Air Barrier Association of America’s conference and trade show.May 8-9, 2018 at the Salt…See More
8 hours ago
Michael R. Johnson liked Bruce Sullivan's blog post Solving Energy Poverty: Energy Efficient Homes for Those Who Need Them Most
8 hours ago
Home Energy Magazine posted a blog post
10 hours ago
Diane Chojnowski posted a discussion

ACEEE Fact Sheet: The Impact of Federal Energy Efficiency Programs

Federal energy efficiency programs have played a key role in reducing energy use and saving…See More
11 hours ago
Profile IconLandon, Lloyd Elam, Jeremiah Doty and 3 more joined Home Energy Pros Forum
11 hours ago
Khaliquzzaman Katchi liked Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge
11 hours ago
Mick Lane replied to Steve Eberly's discussion Infrared camera recommendations for general contractor use
"The real question is what are you going to do with the camera.  Does it need to take pictures…"
12 hours ago
Lloyd Elam commented on Home Energy Magazine's blog post How We Turned Our House into a Giant Foam Box, Part I — Wall Insulation By Wen Lee
"Can't wait to see what your blower door number will be...."
12 hours ago
Danny Gough replied to Jeremy Begley's discussion Manual S for Water Furnace Equipment in the group HVAC
"Well said David Butler. One more thing I would add is if you have some flexibility with the loop…"
14 hours ago
Leslie Jackson posted a blog post
20 hours ago
Steve Eberly posted a discussion

Infrared camera recommendations for general contractor use

Hi, I believe I have searched and found little recent discussion on recommendations for IR…See More
22 hours ago
Jeremiah Doty commented on Jeremiah Doty's blog post A list of 7 important questions to ask potential Contractor's BEFORE hiring them!
"To read more of our helpful Blog's visit us at https://www.jandmservices.us/blog/"
Jeremiah Doty posted a blog post

A list of 7 important questions to ask potential Contractor's BEFORE hiring them!

A list of 7 important questions to ask a Contractor Before Hiring Them.1) First and foremost when…See More
Todd Williams liked Diane Deyerler's event Energy OutWest Conference
Khaliquzzaman Katchi replied to Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I am prepared to pay $200 and I will pay the shipping to Canada."
Brad Cook replied to Brad Cook's discussion When is a fuel history confidential and why?
"Personally, I just don't see what is so personal about how much fuel your home uses, in…"
Barbara Smith liked Diane Chojnowski's video
Al Tibbs replied to Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a DM2 Mark II in VERY GOOD to Excellent Condition. I will sell for $300."


  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service