RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 362

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Latest Activity

Dannie Jackson liked Allison A. Bailes III's group HVAC
8 hours ago
Dannie Jackson added a discussion to the group Energy Efficient Design
9 hours ago
Dannie Jackson liked Barry NewDelman's discussion Help your Clients save, THEN do what you do best
9 hours ago
Dannie Jackson replied to Barry NewDelman's discussion Whats the Consensus of this group Define "Energy Efficiency" in the group Energy Efficient Design
"Design wise I would say that energy efficiency is defined by the Btu / square foot.  This is…"
9 hours ago
Dannie Jackson joined Chris Laumer-Giddens's group
Thumbnail

Energy Efficient Design

Energy efficiency starts at the drafting table...How architects and designers can help buildings…See More
9 hours ago
Dannie Jackson liked Chris Laumer-Giddens's group Energy Efficient Design
10 hours ago
Dannie Jackson posted a blog post
11 hours ago
Dannie Jackson liked Home Performance Coalition's blog post Building a Market for High-Performing Homes
12 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service