RemRate allows for a ground source heat pump and you can couple it to the domestic hot water system.  However I need to convert the Water Furnace's 5.0 COP to an equivalent EF.  Any ideas?????

Views: 358

Reply to This

Replies to This Discussion

One would be tempted to put in 500%, but refrain, the stated COP is just for the unit, not the HP system, which will include pumping power and other distribution losses.  Probably system COP closer to 3.

Hi Elizabeth -- If you look at the last page of this article (http://www.luntmarymor.com/condensing_heaters.pdf), you'll see a nice description of how EF is measured.  From this, and factoring in the additional consumption that Michael mentioned, you can probably come up with a reasonable approximation of the EF for your scenario.  The toughest part may be to figure out the standby losses, if the DHW is a tank-type system.

Note that in REM the EF is entered as a decimal, not a percentage -- and for a heat pump, the decimal will be larger than 1.0.

I was looking at REM/Rate and the GSHP only needs COP entered. It looks like you only need to model the type of water heater you are using for EF and also check desuperheater in the heat pump section if they are coupled.
Also to add the pump watts. Are you using the GSHP to supply 100% of the domestic hot water?
Thanks for the help.  Didn't want to reinvent the wheel if someone had already been down this path.

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler 8 hours ago. 2 Replies

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco 14 hours ago. 1 Reply

Fixing a water heater?

Started by John Shillito in Best Practices. Last reply by Eric Kjelshus on Friday. 21 Replies

Latest Activity

Profile IconAndrew McDowell, Randy Kinnison, Breanna Detwiler and 8 more joined Home Energy Pros Forum
5 hours ago
David Butler replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"theoretically, let's say you perfectly isolate the HPWH from a heat source. The HPWH's…"
7 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Interesting idea. Commercial roof on a slope! Typical density for roofing spray foam is 2.5 to 3.0…"
8 hours ago
Summer Redman added a discussion to the group Job Board
Thumbnail

Hiring 2 Training Specialists in Champaign-Urbana, Illinois

The Applied Research Institute (ARI) at the University of Illinois at Urbana-Champaign is seeking…See More
9 hours ago
Summer Redman joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
9 hours ago
Stacie Bagnasco replied to Evan Mills's discussion Dirty solar panels
"This is a great idea. I clicked on your discussion because it made me remember that I forgot to get…"
14 hours ago
Kirsten Richnavsky posted an event
Thumbnail

rCloud - The Future of Testing at Your Office or Home

October 18, 2017 from 2pm to 3pm
Integrating rCloud as an essential part of your RESNET QA process.Retrotec’s rCloud app is here,…See More
14 hours ago
Ed Whitaker replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"Brad,   I agree with the comments and would add a couple of thoughts. 1st,  any time you…"
15 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service