When replacing outdoor unit, is it necessary to also replace the indoor unit?????

When replacing the outdoor unit, should the indoor unit also be replaced? most of the people have this question in their mind....please share your reviews...

Thank You Guys!!!!

Tags: fernando, hills, hvac, san, services, valley, woodland

Views: 417

Reply to This

Replies to This Discussion

Are you referring to the furnace or the evaporation coil?

Aaren  Assuming you are talking about a new condensing unit for an AC there are a few of good answers.

1) Yes if the old indoor coil is from a low efficiency unit and was designed for the same size unit as the new outdoor unit. That is the only way you are going to get the rated efficiency from the new unit

2) No if the old indoor coil is clean and is say from a 4 ton unit, but you are putting in a 2 or 2.5 ton outdoor unit. If you also change the metering device to a properly sized TXV then you can come up with a really sweet efficient AC.

3) Better yet, if the only problem is the compressor of the old 4 ton unit, put in a new 2 or 2.5 ton compressor and a new properly sized TXV.

Yes it works 

Be sure to check/clean the indoor coil before reusing. Many coils have been in the system for years and are clogged up with dirt. Other than that it's just tubes and fins.

If you do the smaller condenser while keeping large coil, check airflow. You may need to adjust speed or replace blower motor to get correct CFM.

Also note that you won't be eligible for any rebates unless the coil is changed.

What about issues of refrigerant incompatibility? 

Refrigerant is all gone once system is opened up. There is ongoing debate about oil compatibility.

Hopefully Bob was saying the refrigerant was recovered not: "all gone" into the atmosphere.

If you have a R22 unit any replacements will have to be R22 equipment. If you are replacing everything you will be putting in R-410A and the refrigerant oils are not compatable. The old oil will need to be cleaned from the lineset unless you replace it too. Don't mix the oils -- gunk will result.

I have taken  a 5 ton coil Air handler and 3 tons of duct work and sealed the home and added R and went back with a 2.5 ton AC system keep the old but in good shape coil and air handler end up with a 15.3 EER with a 15.5 SEER unit.  I used the old line set  and flushed with r-11 flush and lots of presser - nitrogen.  Then Vack to 300 Mic.  Its works well for 3 yr  but is not ARI

RSS

Forum Discussions

What made this chimney fall down?

Started by Eric Kjelshus in General Forum. Last reply by Eric Kjelshus on Tuesday. 7 Replies

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by Dave Taylor on Sunday. 61 Replies

Manual J (SD) for custom, luxury homes

Started by Dav Camras in HVAC. Last reply by Dav Camras Nov 10. 3 Replies

Quantitative methods for residential zoning

Started by Brett in HVAC. Last reply by David Butler Nov 9. 1 Reply

Home Energy Pros and #MeToo

Started by Mike Rogers in General Forum. Last reply by Mike Rogers Nov 9. 3 Replies

Latest Activity

Profile IconSonny Roncancio and Chester Energy & Policy joined Home Energy Pros Forum
4 hours ago
Ryan Moore updated an event
Thumbnail

LEED for Homes Green Rater Training at Fort Collins, CO

December 7, 2017 to December 8, 2017
Green Insight will host this 2-day training in Fort Collins, CO December 7-8,…See More
23 hours ago
Rodney Bailey liked Rodney Bailey's discussion Energy audit equipment for sale.
yesterday
tedkidd liked Mike Rogers's blog post Focusing on payback to motivate customers?
yesterday
Home Energy Magazine's blog post was featured
Wednesday
Home Energy Magazine posted a blog post
Wednesday
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Rebates and Incentives: Illinois

Curious about home performance incentives and rebates available in your area? Check out this BPI…See More
Wednesday
Profile IconStacey Cordeiro and Melissa Ames joined Home Energy Pros Forum
Wednesday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service