Is any one familiar with the Peak Energy Saver from www.peakenergytech.com  The unit is intended to store energy from motors used in the home and then supply the stored energy back to the home, thus reducing consumption.  Clames to reduce energy consumption between 10% and 25%.   Fact or Fiction, does any one know?   

Thanks PJ Stevens 

Views: 1431

Reply to This

Replies to This Discussion

Thanks Bob.  This providing me a quick uptake on the whole issue...greatly appreciated!

You're welcome Fred. Good luck to you.

Power factor correction is old, well established technnlogy which is widely used across industry and larger electricity power users. However this technology is used to reduce wasted power measuured as Kvar to bring KVA closer to KW and is not well known industry wide to be used for the above application. Further information can be seen at http://www.streamline-power.com/power_factor_correction.html
Therefore there would need to be authoritative offical independent research conducted for reliable information.

Power Factor Correction is ONLY worth considering for electricity users who are penalized (billed) for inadequate power factor by the utility. All others are billed for kW, not KVA, so it is a complete waste of money for all others to fall prey to scammers hawking power factor correction devices to homeowners and typical commercial customers.

Unfortuantely that is not the whole picture. Granted billing is in KW however improving power factor in an industrial/commercial environment will have a saving as motors will now be operating optimally hence be more efficent so last longer with less maintenance.

Because also KVA is closer to KW then any voltage optimisiation equipment will also make more savings.

Horsefeathers!

Improving a building or plant's power factor does NOTHING for individual motors. I sincerely hope you are not hawking your views for personal gain.

I like your phrase horsefeathers though here in the UK we may say rockin' horse dung!.... joking aside though I can only vouch for how industrial 3phase sites are billed here, the US may be different billing. So installing PFC equipment will (a) reduce the Kvar known as the reactive charge (b) potentially reduce the availability or capacity charge and (c) reduce the load on the transformer, the I2R losses or load losses. Potentially also reduce line losses but that will depend where the capacitors are placed.

Well, I work with the conservation guys at a big local electric utility. One of them told me, by way of agreeing that residential power factor correction is a complete scam, that out of their 400,000 (yes - four hundred thousand) electric customers, only FOUR are on power factor billing.

I imagine those four are large industrial sites, such as paper mills, with access to engineers to evaluate and implement alternatives.

4 out of 400K? All 4 are most likely large industrial customers with 3 phase power. There is absolutely no reason for any residential customer to be concerned about this. I've never seen/heard of any time of PF charge on single phase power.

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by Walter Money 27 minutes ago. 10 Replies

Psychrometric Chart Training

Started by John Krochmalny in Training yesterday. 0 Replies

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco on Monday. 1 Reply

Latest Activity

Walter Money replied to David Butler's discussion How would you insulate this roof?
"Gentlemen, and ladies, So, as I read this, I see a perfectly good roof that works in serious…"
27 minutes ago
tedkidd replied to Bob Blanchette's discussion Tankless Water Heaters... has their time finally come?
"Those are DIY install prices - not that cost is relevant now. If the goal is to go carbon free,…"
29 minutes ago
Profile IconAndy Piercefield, Paigh Bumgarner, Blake Reid and 4 more joined Home Energy Pros Forum
1 hour ago
Marc Tannenbaum's blog post was featured

3 Issues HVAC contractors Should Know About Impacting Customer Comfort and Health

There is an epidemic of people suffering in many of the 100 million homes across the U.S.  Many of…See More
1 hour ago
Stanley Layman replied to Bob Blanchette's discussion Tankless Water Heaters... has their time finally come?
"A tankless water heater can be a bit pricey. Tankless water heaters can range from $300 to $1100 or…"
2 hours ago
John Hatfield replied to David Butler's discussion How would you insulate this roof?
"David I think the finish edge application is critical but several un-knows exist. Such as how far…"
17 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"@Kevin, that article is behind a pay wall. Here's the original posted on Allison's…"
18 hours ago
Kevin Miller replied to David Butler's discussion How would you insulate this roof?
"Good question.  I don't know the answer.   I'd love to know whether there…"
18 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service