Any advice on how to factor a gas fireplace into a Wrightsoft Manual J model? 

Seems like it would reduce the required heat from the central gas forced air system in that room. But not quite sure how to include this in the model. 

Any advice is appreciated. This is my second Manual J model.

Bachi

Ultimate Home Performance

Views: 374

Reply to This

Replies to This Discussion

I would not include it.  Given that it is likely much less efficient than the gas furnace, you don't want to count on the occupants using it when the outside temperature approaches the design temperature.  However, if it is atmospherically vented, you will need to include the flue in the air leakage model.

Dave

Most fireplaces a just a hole that lets heated/cooled air out chimney.  If the heated hole(fireplace) is use much just add more CFM to vent rate.   Most fireplaces are for looks and not a  real way to heat the building (eye candy).   I find a open fireplace is negative 5%  Eff.     

I agree, that fireplaces are for looks and not heat.  There are those who insist on having a fireplace, especially gas, where the vent is always open.  The fireplace needs to be covered with insulation to stop heat/cooling loss.  Fireplace Fashion makes an insulated, magnetic fireplace cover to be used when the fireplace is not in use.  This stops ;the air flow in and out of the chimney, thus stopping any heat or cooling lost dollars.   More information can be found at fireplacefashion.com.

Wrightsoft has an option to include a fireplace in a zone.  I would use that option since it complies with the Manual J instructions.  If you use some other method (hole or heating source) you should make sure your method complies with Manual J.

What kind of gas fire place?  Gas logs... in "generic brick fireplace" with dampers that are left open?  Or a sealed combustion fireplace insert?  With a pilot or pilotless?

If you've got a high performance envelop - and an efficient sealed gas insert.... they can do quite well in heating one end of the house.... and not be a massive air leak.  We have two...in our house.. and it tests at 2.8ACH50.

If the units are cheap - and don't seal up... treat them as a brick fireplace with damper stuck open.

I put a 2 Inch foam cover and painted it black and dropped the heat loss by 3/4.  You can not use it a fire place till remove the cover.  Most cast iron damper are so bent I can not close.   Just say NO to fireplaces and put in the 90%  heating system.   Over 1/2 the high CO probems I go to are with fireplaces 

Sealed combustion fireplace insert. No pilot. I believe it can be hooked up to a room thermostat. 

some can get up to 92% with PVC vent.   Some use 24 volt thermostat that can be +- 2 dead band with heating thermostat

When you model,  add a small additional area  -- say less than 10 sq inch of for possible air leaks...(that should be real high)... be safe and model the fireplace at 60%... efficient.  It really should be used just occasionally not as the primary heat source... 

With an insert - it really isn't the driver for your heat loss in the house.

ACCA Manual J does not consider any heating (BTU gain to a room) from a fireplace.  Manual J only allocates infiltration to the home caused by the fireplace's construction quality.

I think that was part of his concern.  Its a sealed combustion unit.  So the infiltration that might be used for an ordinary fireplace is going to be off the chart.  If its a new home with high end sealed combustion fireplace, correctly installed per manufacturers design... the infiltration might be closer to that of a tankless hot water heater.

A.  The point is that ACCA Manual J does not model for the Btu gain from fireplaces.

B.  Fireplaces are a part of the infiltration load in ACCA Manual J.  You have a choice as to construction quality - Tight, Semi-Tight, Average, Semi-Loose and Loose.  It is all spelled out in the actual Manual J manual published by ACCA.

RSS

Forum Discussions

Latest Activity

Energy Home Pros posted a blog post

What Kind Of Hacks Help Saving Money And Energy For Your Homes?

There are so many insulation contractors out there who state that they can only help their…See More
5 hours ago
Bryan Gabriel liked Bob Krell's discussion What Do You Do When You Find Suspected Mold?
12 hours ago
Home Energy Magazine posted a blog post

Degree Days Shuffle

A 2015 study, “Impacts of global warming…See More
13 hours ago
Efficiency First California posted blog posts
14 hours ago
Steve Schmidt replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"@David: No, it does not have this feature. Apparently machine learning doesn't work that way."
15 hours ago
Dana Fischer replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"Thanks to Laura Martel for prompting me to submit feedback. ;) Similar to Dan Phillips, I installed…"
15 hours ago
Blake Reid commented on Blake Reid's blog post Heating Houses in Hawaii (pt. 1)
"Yes, all of that.  The next part (stay tuned for part 2) will be about my hunt for a decent…"
17 hours ago
John Krochmalny's blog post was featured

Tell me again: Exactly where do I place that vapor barrier again?

There may be much confusion as to where vapor barriers are placed in building systems. Some people…See More
20 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service