I am curious/concerned about advising a tight house (addition) with a cathedral ceiling. I understand that normally, one should keep a 1-2" gap in the rafter bay above the insulation as an air gap. But, if the construction is tight, to achieve a low ACH50 or 1-2, what is the point?How is air (moisture) going to escape if the enclosure, including the roof sheeting, is sealed tight? Also interestingly, the plans did not include any mandatory ventilation for this 780 sqft addition in So. Cal. by the ocean. 

Thank you. 

Dav  

Tags: Tight, control, enclosure, moisture

Views: 216

Reply to This

Replies to This Discussion

It depends, are they going with a hot roof system? If so no air gap is required

The reason for the gap is because even with super low leakage numbers, you still have leakage & the reason the bays get ventilated is to eliminate condensation issues with the sheathing

Most places will not require "ventilation" for additions as they assume the house has it already & it is not a mandatory no matter what if you do X you must put Y in like smoke detectors / carbon monoxide

I agree with Sean, that the main concern is condensation, and in northern climates frost accumulation in the attic.  In southern CA, I am sure those are not a big considerations. You should still have some low attic venting, but it is not as critical.  

Paul

With a vented cathedral ceiling, getting a tight envelope is difficult, but not impossible. Various products are available to maintain the vent gap, some of which are easier than others to air seal.

It's easier, and I believe better, to go with an unvented assembly, in which case the insulation must be fully in contact with the roof, and depending on climate zone, some portion must be air impermeable (less in milder climates, more in colder climates). The purpose is to prevent house moisture from coming in contact a cold roof.

House moisture is removed by spot exhaust in kitchen & baths. Whole house ventilation has a different purpose.

I'm not familiar with California Title 24 requirements for unvented roofs but here's a link to the IRC Chapter that covers that detail (scroll down to Section R806.5): IRC Chapter 8

It is all about the dewpoint. Think of the roof system as a big box. Air can circulate in, out and around the inside of that box. If you could possibly air seal the entire inside plane, and install a durable, continuous and effective vapor barrier over the entire inside plane, you still have the other 5 sides where air and/or moisture can enter (or leave) the box. When the outside temperature falls by a significant amount (as when it is cold enough for snow in the South), you are most likely to hit the dewpoint on those 5 sides. When that condensation pools up in the air permeable insulation, it will be difficult for that water to get out of there unless there is a reasonable connection for air to move in and out. By the time the water eventually gets out, it could promote the growth of fungi, such as wood rot. That is why we ventilate roofs. If there is enough air and vapor impermeable insulation on the roof deck, then the temperature inside the box should stay above the dewpoint and ventilation is not needed (or desired).

I would refer you to this document by Building Science Corp., which tackles the issue of ventilation in cathedral or flat roofs. You don't need to ventilate, but you need to carefully design the assembly.

https://buildingscience.com/documents/insights/bsi-043-dont-be-dense

"Why such a difference between walls and roofs? Walls in most older houses can dry out to the exterior because they rarely have exterior vapor barriers. Roofs have either roof membranes or asphalt shingles that are exterior vapor barriers, and they can’t dry out to the exterior unless the roof assembly is vented to the exterior. We have developed ways of dealing with unvented roof assemblies and insulation, but dense packing them is not one of them. I’ll talk more about the alternative ways later. Walls have “wiggle” room. We don’t have to be perfect because some drying can occur to the outside. We do not typically have the same “wiggle” room with unvented roofs."

RSS

Latest Activity

Jenna Bader's event was featured
Thumbnail

Zero Net Energy Virtual Conference, Jan. 25 & 26, 2018 at Online Webinar via Zoom, Facebook Live, and YouTube Live

January 25, 2018 to January 26, 2018
Devoted to the All-Electric, Solar-Powered Building TypeA FREE On-Line Conference using Zoom: …See More
13 minutes ago
Profile IconThom Phillips and jeff greenberg joined Home Energy Pros Forum
15 minutes ago
jeff greenberg replied to mark avila's discussion Aeroseal Homeseal Pro unit for sale?
"Mark: My client has one for sale. very lightly used but huge discount.   Where are you…"
19 hours ago
Jenna Bader posted events
Friday
Sean Lintow Sr replied to mark avila's discussion Aeroseal Homeseal Pro unit for sale?
"As I recall you have to be a Aeroseal listed "distributor" aka installer to get the…"
Friday
Paul Raymer posted an event

Radon Protections in New Homes at On line

January 30, 2018 from 1pm to 2pm
Radon-resistant construction is becoming a focal point in the high performance building industry.…See More
Thursday
mark avila posted a discussion

Aeroseal Homeseal Pro unit for sale?

Hello,We may be in the market to purchase a used machine should someone have one for sale.Cordially,See More
Thursday
Robert Zockoff liked Tray Biasiolli's discussion Two-stage furnace, control at furnace or thermostat?
Thursday
Profile IconKevin Jacks, Christine Elovecky and Bryan McIntyre joined Home Energy Pros Forum
Thursday
Kevin Jacks liked Diane Chojnowski's group Job Board
Thursday
Scott Doyle liked David Butler's discussion RESNET gets serious about modeling platform consistency
Thursday
Quinn Korzeniecki posted an event

BPI Retreat at HPC New York 2018 at Saratoga Springs, NY

February 12, 2018 from 12pm to 4pm
BPI will be hosting a retreat for BPI GoldStar Contractors, Test Centers, Proctors, and Certified…See More
Thursday
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

BPI to Host Retreat for Stakeholders on February 12th

BPI will be hosting a retreat for BPI GoldStar Contractors, Test Centers, Proctors, and Certified…See More
Thursday
Rhett Major posted an event
Thumbnail

Building Analyst - Energy Auditor Class at Conservation Consultants, Inc.

February 26, 2018 at 8am to March 2, 2018 at 5pm
Building Analyst - Energy Auditor class for BPI Certification, using Saturn Resources On-line…See More
Thursday
Barbara Smith's video was featured

ACEEE Report: How to Talk About Home Energy Upgrades

How can home energy assessments lead to more energy efficiency upgrades? Using a behavioral science approach to answer this question, we conducted an online ...
Thursday
Profile IconMichael W. Ford and Rob Vehring joined Home Energy Pros Forum
Wednesday
Luke Yang is now a member of Home Energy Pros Forum
Tuesday
KRicket Smith-Gary commented on Efficiency First California's blog post Is Health The Future of Home Performance?
"While discussing health benefits for various retrofits and new construction, please also keep in…"
Jan 15
KRicket Smith-Gary liked Efficiency First California's blog post Is Health The Future of Home Performance?
Jan 15
goodtidings comfort is now a member of Home Energy Pros Forum
Jan 15

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service