When doing a blower door test, do you ever use long term average? Why or why not?

Digital pressure and flow gauges have an option for time averaging, such as 1, 5 or 10 seconds, long term or a manual time average option.

Under what circumstances would you use the long term average and why?

Views: 284

Reply to This

Replies to This Discussion

When the wind is breezy, I use long term averaging. The more the pressure jumps around due to breezes, the longer the term that I use. Even then, I mentally average the readings. This is after I have taken steps to shield the end of the outside hose from the wind.

Wind is caused by a difference in air pressure so the change in air pressure from the wind, or a passing truck, is reflected in the change in the readings of a digital pressure gauge. Keep in mind that 1 pascal is a tiny change of pressure. I find that the best way to get a stable baseline is to insert a "T" fitting into the reference tube and connect 2 reference tubes. Place 1 tube on 1 side of the house and the other tube on the opposite side of the house. Be sure that the tube nearest the blower door is at least 5' (preferably more) from the fan. If the fan needs to be installed where it is blowing into an enclosed porch or mud room (not a good choice unless there is no better alternative) make sure the tube is outside of the porch.

Hi Kim,

Wind is probably the most frequent reason for using the time averaging with our manometers, but there is another that we need to be careful with.  Manometers are unique in that they ignore barometric pressures.  Place your refer tube out the front door and walk your manometer (long tube) upstairs or into the basement and even though the top to bottom pressure may vary (on a cold day) by 50 pascals or more our manometers will register very little.  When the temperature of our tubes and the air inside is the same as in the house, any changes in elevation are canceled out.  However, if those tubes just came out of an ice cold vehicle, or a hot one, and have not fully acclimated, our readings will drift.  In this case, before we start averaging we need to allow those tubes to become room temperature.  The section of tube that goes outside needs to acclimate as well.

Bud

I never use any setting but "long term" average. Any other setting will always give you a less accurate average reading. Under the "long term" setting the manometer automatically calculates a mathematically continuous average. That means that you can "hold " the reading after "any" length of time and it will give the average for all of the seconds that you had the meter running.

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler 10 hours ago. 34 Replies

Psychrometric Chart Training

Started by John Krochmalny in Training. Last reply by Mahendra Shah on Friday. 1 Reply

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco Oct 16. 1 Reply

Latest Activity

Profile IconCharles Buell, Robert Cowell, Alice Quinn and 1 more joined Home Energy Pros Forum
2 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Sean Lintow proposed rails and clips (re: first comment in this discussion), but in the context of…"
10 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"I missed where the suggestion for rails came in. The plywood would not need any rails. 4+ inches is…"
14 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"I'm a little confused about the necessity and purpose of using support rails if working on…"
15 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"If you insulate master bedroom and family room from below, you definitely need more R-value than…"
15 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Brad, I was only talking about using EPS between the ridges, if necessary, to conform to bolts.…"
15 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"It kind of depends on the PIC. Not all insulation is made the same. Here in VT (and all of New…"
15 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Filling those shallow valleys with rigid foam not only prevents primary foam panels from…"
15 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service