I am not an energy Rater .. I am an architect

I am curious if any "Home Energy Pros" make an effort to locate the Neutral Pressure Plane (NPP) of a house that is being blower door tested?

Views: 4875

Reply to This

Replies to This Discussion

Yes, the same amount of air must be replacing what is exhausting, which is why the fans are programmed to run about 1/3 time.

Can one fan make the entire house negative? Yes, but only if the house is tight enough. Apparently, as I and John Straube have been saying, 2ACH50 is "tight enough".

The day we did the blower door test was 24° outside, and the baseline delta-P was -2.2 Pa at the front door (1st floor), so the 2nd storey ceiling pressure should have been approximately +2.2 Pa or 4.4 Pa total stack effect pressure.

With one bathroom fan running, the manometer delta-P increased to -4 Pa, which should have brought the ceiling pressure to perhaps 0.4 Pa. With both bath fans running, the downstairs delta-P was -8.6.

Robert,

on the day of the test...what was the temperature inside the house?

Was the woodstove operating?

also... can you explain in more detail the woodstove and...

"a 4" inlet in the first floor for direct-coupled woodstove combustion air"?

 

I don't know much/anything about woodstoves...

Is your stove and chimney an airtight "system" with respect to the interior of the house?

does the combustion air inlet connect directly into the stove or is there an opening near the stove?

 

Is there a damper to close off the combustion air when the stove is not being used?

I assume the inside temperature was close to the thermostat setpoint of 68°.

I don't think you can do a blower test with a woodstove running, as -50 Pa is likely to overwhelm the chimney draft (about 42 Pa at 300° flue temperature) and cause backdrafting, even with a supposedly "air-tight" stove.

The new EPA-certified woodstove had an option for direct-coupling of combustion air supply to the firebox of the stove (as a number of them do now), but I don't believe it was connected to the 4" PVC intake pipe under the slab (that terminates in the bottom block of the chimney as an air plenum). The intake duct and cast-iron cleanout door were sealed for the test.

There is no damper in the combustion air system, since normally it would lead directly into the "air-tight" woodstove and be, effectively, a sealed combustion unit, isolated from the interior airspace. There is, however, one of my "patented" inverted U-traps:

The one weakness in this system, with a concrete block chimney (which I believe is far more durable and safe than Metalbestos) is that the cast iron cleanout door is not well sealed and should have a gasket. But it's at the lowest point of the house (most negative stack effect pressure) and the normal chimney draft pressure (at room temperature) would be 8-10 Pa, which would partially balance the house negative pressure.

There's no "reply" button for me on Robert's post with the inverted U-trap photo, but here's a question. I can't tell if you're saying you connected the woodstove to the outside air duct, or not. Also, your post refers to a block chimney but I don't see it. Curious about these details for future reference.

David,

The woodstove was not direct-coupled at the time of the blower door test but was later connected to the air intake in this house.

Here's the air plenum and combustion air duct termination in the base of the block chimney:

In homes which were entirely wood heated (plus passive solar) with no central heating system, and in which the wood stove would be running much of the winter, I have close-coupled the stoves to a nearby floor or wall register which provided outdoor make-up air. This had the advantage of avoiding cold air being drawn in from elsewhere across the floor to the wood stove, thereby creating drafts, and also allowing the woodstove to depressurize the house to act as a non-electric whole house exhaust "fan" and draw fresh air in through the remainder of the air inlets.

Otherwise, fresh air was provided by the intermittent use of bath and kitchen exhaust fans. In one house, I connected a dehumidistat to the bath exhaust fan, and in another there was an indoor composting toilet which had a low-speed fan that drew indoor air over the compost pile and exhausted through the roof, which provided continuous ventilation.

Robert, thanks for posting the photos...I am still having trouble visualizing how the intake pipe and the stove communicate...do you have a photo of the stove?

They communicate by Tweet, of course ;-)

where does the other pipe below the chimney go?

Ah! The other mystery pipe?

You can just see it at the bottom plate below the U-trap. I ran two 4" PVC pipes under the slab to the chimney pad, since two 4" pipes are roughly the same cross-sectional area as the 6" flue pipe (equal intake and exhaust).

But, when we got the wood stove, the direct-couple kit had just a 4" round intake connector, so I capped off one of the two pipes at both ends. I guess it makes sense that 4" of cold air can supply 6" of hot, expanded air.

Robert,

When you create a thermal air trap as shown, how do you calculate the pressure benefits of the trap?

Bud

Bud, I'm not sure exactly what you mean by "pressure benefits", but I did discuss this somewhat on the previous page.

It's a common practice among HVAC professionals in cold climates, and sometimes called a Saskatoon Loop.

It's similar to the common rule of thumb in roof ventilation that a minimum 3' head between intake and exhaust vents is necessary in order to get any appreciable air flow - but in reverse.

Any negative chimney effect will inhibit cold air back flow into the conditioned space unless there is so much envelope leakage that a strong negative pressure is created at the point of combustion air entry.

This thread has me lost.  Dianne is going to have to work on a better way to string these posts.

Anyway, if a vent goes directly through the envelope there is (with temperature and location) a pressure between the inside and outside to move the air.  If either inside or outside vent pipe goes up or down, that pressure is altered by the difference in the weight of the air in the pipe vs the air around the pipe.  Once I understand where the openings on your inverted loop are, I will be able to estimate what its benefits are.

Bud

PS, I have my doubts about the saskatoon loop??

RSS

Latest Activity

Brett Little posted events
yesterday
Ben Thompson replied to Stuart Perkin's discussion TrueFlow in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Stephen. Do you still have a Trueflow that you would sell? Ben Thompson,…"
yesterday
Ben Thompson replied to Landon's discussion WANTED: Blower door complete set Retrotec or Minneapolis in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Landon. I have a Minneapolis blower door set-up that I would like to sell. It's in…"
yesterday
Ben Thompson added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted: TrueFlow plate

Seeking an Energy Conservatory TrueFlow plate (grid) in good condition. Ben Thompson.…See More
Friday
Scott Partlo replied to Jerry Needham's discussion Closed cell on roof deck to prevent mold.
"You say that 2" of closed cell foam is applied OVER the roof deck.  Where exactly was the…"
Friday
ayazfudugo1 replied to Tom Smith's discussion Are Energy Efficient Windows worth the investment?
"For both new and existing homes, Energy efficient windows are an important consideration Heat…"
Friday
Profile IconTodd Williams and Haley Keegan joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
Friday
Todd Williams liked Diane Chojnowski's group Hall of Shame
Friday
Home Energy Magazine posted a blog post
Thursday
Leona Zoey posted a blog post

Landlords Are Your Friends

While it may be easy to forget given their apparent position of power over you, landlords usually…See More
Thursday
Haley Keegan joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
Thursday
Donald Hester replied to Jerry Needham's discussion Closed cell on roof deck to prevent mold.
"For the roof shingle issue that is an unfortunate issue with many home inspectors that have been…"
Thursday
Profile IconJason Green, Dennis Smith, Alex Ortega and 2 more joined Home Energy Pros Forum
Thursday
tedkidd replied to Quinn Korzeniecki's discussion BPI CEO Larry Zarker's Review of "The Home Comfort Book" in Healthy Indoors Magazine in the group Building Performance Institute (BPI)
"...free chapters of book available here - http://bit.ly/HPchapterlist"
Thursday
tedkidd liked Quinn Korzeniecki's discussion BPI CEO Larry Zarker's Review of "The Home Comfort Book" in Healthy Indoors Magazine
Thursday
William Collins's video was featured

Foam Kits vs. Spray Sealants Gun

How does the Foam Kit stack up to the Spray Sealants Gun when it comes to simplicity? When you integrate the Spray Sealants Gun to a 16lb Canister, you creat...
Thursday
Scott Becnel added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Brand new DucTester at a discount

Brand new DucTester at a discountI have a brand new 300 DucTester system from Retrotec for sale at…See More
Wednesday
Scott Becnel joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Wednesday
Lucyna de Barbaro liked Home Energy Magazine's blog post AeroBarrier: The Silver Bullet to Zero Energy Affordability, by Paul Springer
Wednesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service