I am not an energy Rater .. I am an architect

I am curious if any "Home Energy Pros" make an effort to locate the Neutral Pressure Plane (NPP) of a house that is being blower door tested?

Views: 4977

Reply to This

Replies to This Discussion

Yes, the same amount of air must be replacing what is exhausting, which is why the fans are programmed to run about 1/3 time.

Can one fan make the entire house negative? Yes, but only if the house is tight enough. Apparently, as I and John Straube have been saying, 2ACH50 is "tight enough".

The day we did the blower door test was 24° outside, and the baseline delta-P was -2.2 Pa at the front door (1st floor), so the 2nd storey ceiling pressure should have been approximately +2.2 Pa or 4.4 Pa total stack effect pressure.

With one bathroom fan running, the manometer delta-P increased to -4 Pa, which should have brought the ceiling pressure to perhaps 0.4 Pa. With both bath fans running, the downstairs delta-P was -8.6.

Robert,

on the day of the test...what was the temperature inside the house?

Was the woodstove operating?

also... can you explain in more detail the woodstove and...

"a 4" inlet in the first floor for direct-coupled woodstove combustion air"?

 

I don't know much/anything about woodstoves...

Is your stove and chimney an airtight "system" with respect to the interior of the house?

does the combustion air inlet connect directly into the stove or is there an opening near the stove?

 

Is there a damper to close off the combustion air when the stove is not being used?

I assume the inside temperature was close to the thermostat setpoint of 68°.

I don't think you can do a blower test with a woodstove running, as -50 Pa is likely to overwhelm the chimney draft (about 42 Pa at 300° flue temperature) and cause backdrafting, even with a supposedly "air-tight" stove.

The new EPA-certified woodstove had an option for direct-coupling of combustion air supply to the firebox of the stove (as a number of them do now), but I don't believe it was connected to the 4" PVC intake pipe under the slab (that terminates in the bottom block of the chimney as an air plenum). The intake duct and cast-iron cleanout door were sealed for the test.

There is no damper in the combustion air system, since normally it would lead directly into the "air-tight" woodstove and be, effectively, a sealed combustion unit, isolated from the interior airspace. There is, however, one of my "patented" inverted U-traps:

The one weakness in this system, with a concrete block chimney (which I believe is far more durable and safe than Metalbestos) is that the cast iron cleanout door is not well sealed and should have a gasket. But it's at the lowest point of the house (most negative stack effect pressure) and the normal chimney draft pressure (at room temperature) would be 8-10 Pa, which would partially balance the house negative pressure.

There's no "reply" button for me on Robert's post with the inverted U-trap photo, but here's a question. I can't tell if you're saying you connected the woodstove to the outside air duct, or not. Also, your post refers to a block chimney but I don't see it. Curious about these details for future reference.

David,

The woodstove was not direct-coupled at the time of the blower door test but was later connected to the air intake in this house.

Here's the air plenum and combustion air duct termination in the base of the block chimney:

In homes which were entirely wood heated (plus passive solar) with no central heating system, and in which the wood stove would be running much of the winter, I have close-coupled the stoves to a nearby floor or wall register which provided outdoor make-up air. This had the advantage of avoiding cold air being drawn in from elsewhere across the floor to the wood stove, thereby creating drafts, and also allowing the woodstove to depressurize the house to act as a non-electric whole house exhaust "fan" and draw fresh air in through the remainder of the air inlets.

Otherwise, fresh air was provided by the intermittent use of bath and kitchen exhaust fans. In one house, I connected a dehumidistat to the bath exhaust fan, and in another there was an indoor composting toilet which had a low-speed fan that drew indoor air over the compost pile and exhausted through the roof, which provided continuous ventilation.

Robert, thanks for posting the photos...I am still having trouble visualizing how the intake pipe and the stove communicate...do you have a photo of the stove?

They communicate by Tweet, of course ;-)

where does the other pipe below the chimney go?

Ah! The other mystery pipe?

You can just see it at the bottom plate below the U-trap. I ran two 4" PVC pipes under the slab to the chimney pad, since two 4" pipes are roughly the same cross-sectional area as the 6" flue pipe (equal intake and exhaust).

But, when we got the wood stove, the direct-couple kit had just a 4" round intake connector, so I capped off one of the two pipes at both ends. I guess it makes sense that 4" of cold air can supply 6" of hot, expanded air.

Robert,

When you create a thermal air trap as shown, how do you calculate the pressure benefits of the trap?

Bud

Bud, I'm not sure exactly what you mean by "pressure benefits", but I did discuss this somewhat on the previous page.

It's a common practice among HVAC professionals in cold climates, and sometimes called a Saskatoon Loop.

It's similar to the common rule of thumb in roof ventilation that a minimum 3' head between intake and exhaust vents is necessary in order to get any appreciable air flow - but in reverse.

Any negative chimney effect will inhibit cold air back flow into the conditioned space unless there is so much envelope leakage that a strong negative pressure is created at the point of combustion air entry.

This thread has me lost.  Dianne is going to have to work on a better way to string these posts.

Anyway, if a vent goes directly through the envelope there is (with temperature and location) a pressure between the inside and outside to move the air.  If either inside or outside vent pipe goes up or down, that pressure is altered by the difference in the weight of the air in the pipe vs the air around the pipe.  Once I understand where the openings on your inverted loop are, I will be able to estimate what its benefits are.

Bud

PS, I have my doubts about the saskatoon loop??

RSS

Forum Discussions

Mini split air conditioners and ceiling fans

Started by Beverly Lerch in General Forum. Last reply by Daniel Baur-McGuire yesterday. 4 Replies

DIY Filter Solution for an Evaporative Cooler, anyone?

Started by Leslie Jackson in HVAC. Last reply by Daniel Baur-McGuire yesterday. 6 Replies

VERY TIGHT HOME WITH OVER SIZED AC

Started by Jerry Needham in BPI. Last reply by Tim O'Brien yesterday. 5 Replies

Apply now for the Jon Siemen Memorial Scholarship!

Started by Diane Chojnowski in General Forum. Last reply by Quinn Korzeniecki on Thursday. 1 Reply

Log home roof insulation

Started by Bob Reuther in Best Practices. Last reply by Bob Reuther Aug 7. 10 Replies

Latest Activity

Profile Iconyanky fogel, Kathleen Krebs, Nicholas Rubenstein and 3 more joined Home Energy Pros Forum
7 hours ago
yanky fogel liked Home Energy Magazine's video
12 hours ago
Franco Oyuela commented on Shawn Weeks's blog post How Homeowners Can Keep Electricity Costs Down in Summer Months
"Cutting back on air conditioning is also good for the environment because it reduces carbon…"
16 hours ago
Seventhwave posted events
16 hours ago
Franco Oyuela commented on John White's blog post Top Reasons to Consider Seasonal HVAC Maintenance
"They say an ounce of prevention is worth a pound of cure, and when it comes to HVAC units, this…"
16 hours ago
Diane Chojnowski's video was featured

1950s Home Retrofit to Super Efficient Passive House - Urban Green Building

This 1950s Montreal house was retrofitted to become a super efficient passive house by adding a 16 inch thick layer of cellulose insulation to the exterior. Maison Ozalée's builder, Richard Price from Construction Le Tournesol, also used triple…
20 hours ago
Diane Chojnowski posted a video

1950s Home Retrofit to Super Efficient Passive House - Urban Green Building

This 1950s Montreal house was retrofitted to become a super efficient passive house by adding a 16 inch thick layer of cellulose insulation to the exterior. ...
20 hours ago
Profile IconSara Melucci, Hayden Sloan and Jediah Krajcik joined Home Energy Pros Forum
yesterday
Daniel Baur-McGuire replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Running a ceiling fan actually heats up air. Allison Bailes has some great articles on it.  I…"
yesterday
Daniel Baur-McGuire replied to Leslie Jackson's discussion DIY Filter Solution for an Evaporative Cooler, anyone?
"Where are the supply runs located? Look to make sure supply runs are sealed. I would second having…"
yesterday
Tim O'Brien replied to Jerry Needham's discussion VERY TIGHT HOME WITH OVER SIZED AC
"New build may not have been "dry" before finished and occupied. Residual moisture from…"
yesterday
Daniel Baur-McGuire replied to Jerry Needham's discussion VERY TIGHT HOME WITH OVER SIZED AC
"Oversized A/C systems wont pull out enough moisture from the conditioned air. I would check to make…"
yesterday
Efficiency First California's blog post was featured
yesterday
Laurie DiDonato posted a blog post

HERS Rater Training Discount ($200) Ends August 20th!

Online: September 17-28th (Times TBA)Classroom: October 1-5th in Manchester, NHFull fee: $2595…See More
yesterday
Profile IconNorthWest AeroBarrier and david beckwith joined Home Energy Pros Forum
Friday
John White posted a blog post
Friday
Efficiency First California posted a blog post
Friday
Franco Oyuela commented on Fresh Air Duct Cleaning's blog post Moving in to a new home and why you should get a Duct Cleaning
"There is no evidence to suggest that clean ducts leads to better overall health. However, it should…"
Friday
Franco Oyuela replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Using a ceiling fan as part of a team to bring your maximum home cooling comfort. Adding a ceiling…"
Friday
Beverly Lerch replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Thank you.  Good information about the ceiling fans."
Thursday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service