I am not an energy Rater .. I am an architect

I am curious if any "Home Energy Pros" make an effort to locate the Neutral Pressure Plane (NPP) of a house that is being blower door tested?

Views: 4876

Reply to This

Replies to This Discussion

I just found a formula for approximating the house depressurization of an exhaust fan:

depressurization ≈ 50 x (CFMfan/CFM50)1/0.65

This roughly agrees with my test results.

In the link provided, Straube uses a variation of the formula I posted.

Your simplified formula, which BSC teaches in their "summer camps" (see page four on this PPT link)

http://www.buildingscienceconsulting.com/presentations/documents/XV...

loses 2% accuracy for each 10°F delta-T.

So, even with your example of 16' total stack height and 35° delta-T (total pressure differential of 4.04 Pa), if you got a reading of exactly half total delta-P at the floor, that would put the NPP at 8.62' up rather than 8'. You could say that a 7½" error is OK, but at a 70° delta-T that error increases to 1¼" feet which is significant.

Hi Robert,

I checked the link and they do use the same formula.  I see they are referencing the NPP, but it applies to any height.  In their example they are starting with a assumed NPP in the middle, not always the case.

As for accuracy, I haven't had time to review your equation, but plus or minus a foot is a lot more accurate than cracking a window open and feeling how much air is entering or exiting.  That is what they explained in my auditing class.  In any case, the accuracy we need is dependent upon what we are looking for.  A high, middle, or low, location tells us how balanced or unbalanced our leakage is.  If the location then changes a lot or a little when a window is opened we can next estimate how much total leakage we have.  And last, if we have no stack effect to play with on a given day we can use the exhaust fans to see where one then two place the NPP.

Thanks for the input,

Bud

Robert, assuming both equations came from similar sources, I was wondering what additional assumption they made to bring it down to Pa = 0.0067 x H x▲t

Just playing with the numbers it seems they assumed a very low ▲t or at least that is what I get working your equation backwards.  If the .0067 were adjusted a bit, then the plus and minus error might be better centered around some average outside temperature, thus a smaller error.

Bud

If you assume 35° delta-T and about 2,000' elevation (atmospheric  pressure of about 13.7 psi), then the simplified formula, using 0.0067 as the constant and delta-T°F, roughly approximates the curve of the accurate formula.

It's a very rough, quick and dirty, approximation of stack effect pressure.

As someone said, the easiest way to check for neutral pressure plane is with a smoke stick on a calm day. Crack a casement window or door, run the smoke up the small crack. Does the smoke come in or go out? Sometimes you see the NPP within the height of that window or door. If it is all "in" on the first floor, go upstairs and do this again. If flow is all "in" as high as windows go on the top floor, then the NPP is very close to the top floor ceiling.

I have done hundreds of neutral pressure plane tests with sensitive manometers but the technique described above will be almost as accurate and much faster.

Don

Hi Don, it sounds like you attended the same auditing class I did :).  But the back of the hand method lacks a professional look and isn't accurate enough to judge how much the NPP moves with a given amount of added leakage area or exhaust venting.  We have the tools so I like to use them.

You mention using your manometer to locate the NPP, may I ask how you used it?

Robert, I have no problem using the better formula, I just like to understand how these come about.  And even here in Maine, elevation does vary.

With the numbers we gather and calculations we do, there is a balance between accuracy and consistency.  Since accuracy is not always possible, at least being consistent gives us a reference.

Bud

The NPP testing that I did was in the early eighties. We simply measured the cross-wall pressures through any wall orifice or opening we could find, and then graphed the pressure differences against height to find the P=0 intersection. On a calm day, the NPP levels on all four sides of a house were within a metre of each other. On windy days, there was little or no consistency or repeatability. These were primarily two storey houses with a full basement, and lots of basement leakage. The NPP was in the top half of the first floor for many of the houses. Older houses usually had it higher on the second floor. If you can discern differences of a meter or so in the NPP in your added leakage area tests, then my prediction is that it is calm enough to do it accurately with a smoke pencil.

But then, I like using the garbage bag airflow test and find it almost as repeatable as a flowhood.

Don 

Don, I always chuckle when I have spotted a cold draft pouring in with my IR camera and then I catch myself testing it with the back of my hand. 

Thanks for the explanation, essentially the same.

Bud

John-

Not somthing I try to locate but it I think it could be done witout too much trouble. With a gauge and some tubing a guy could go to different parts of the home (lowest point to highest and anything in between) and just take a house with reference to the outside pressure reading. When you record zero with the gauge configured this way you may find your nuetral pressure plane. Haven't verified this but I think it would work.

 

You could do that, but you'd have to drill a lot of holes through the envelope, since you have to compare interior pressure to outside pressure at the same height (without opening windows which will change the NPP height).

Bud, CMHC tested the flow vs. pressure performance of a Saskatchewan loop back in 1987. The report is likely still around but essentially the looping just reduced the flow rate compared to a straight inlet, by introducing a 180 degree turn. The test results did not bear out the theoretical advantages of a column of cold air sitting in the vertical tube.

As well, cracking a window to test for neutral pressure plane does not unduly change the NPP location, based on the experience we had testing. In a particularly tight house, where even such a small opening might be critical, you could send out a metal capillary tube through the weatherstripping or tape the crack when doing the test. Windows and doors are really the only NPP measurement access points that you have.

Don

RSS

Latest Activity

Brett Little posted events
yesterday
Ben Thompson replied to Stuart Perkin's discussion TrueFlow in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Stephen. Do you still have a Trueflow that you would sell? Ben Thompson,…"
Friday
Ben Thompson replied to Landon's discussion WANTED: Blower door complete set Retrotec or Minneapolis in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Landon. I have a Minneapolis blower door set-up that I would like to sell. It's in…"
Friday
Ben Thompson added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted: TrueFlow plate

Seeking an Energy Conservatory TrueFlow plate (grid) in good condition. Ben Thompson.…See More
Friday
Scott Partlo replied to Jerry Needham's discussion Closed cell on roof deck to prevent mold.
"You say that 2" of closed cell foam is applied OVER the roof deck.  Where exactly was the…"
Friday
ayazfudugo1 replied to Tom Smith's discussion Are Energy Efficient Windows worth the investment?
"For both new and existing homes, Energy efficient windows are an important consideration Heat…"
Friday
Profile IconTodd Williams and Haley Keegan joined Diane Chojnowski's group
Thumbnail

Hall of Shame

In this group, members share an array of images from the field, showing the kinds of issues…See More
Friday
Todd Williams liked Diane Chojnowski's group Hall of Shame
Friday
Home Energy Magazine posted a blog post
Thursday
Leona Zoey posted a blog post

Landlords Are Your Friends

While it may be easy to forget given their apparent position of power over you, landlords usually…See More
Thursday
Haley Keegan joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
Thursday
Donald Hester replied to Jerry Needham's discussion Closed cell on roof deck to prevent mold.
"For the roof shingle issue that is an unfortunate issue with many home inspectors that have been…"
Thursday
Profile IconJason Green, Dennis Smith, Alex Ortega and 2 more joined Home Energy Pros Forum
Thursday
tedkidd replied to Quinn Korzeniecki's discussion BPI CEO Larry Zarker's Review of "The Home Comfort Book" in Healthy Indoors Magazine in the group Building Performance Institute (BPI)
"...free chapters of book available here - http://bit.ly/HPchapterlist"
Thursday
tedkidd liked Quinn Korzeniecki's discussion BPI CEO Larry Zarker's Review of "The Home Comfort Book" in Healthy Indoors Magazine
Thursday
William Collins's video was featured

Foam Kits vs. Spray Sealants Gun

How does the Foam Kit stack up to the Spray Sealants Gun when it comes to simplicity? When you integrate the Spray Sealants Gun to a 16lb Canister, you creat...
Thursday
Scott Becnel added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Brand new DucTester at a discount

Brand new DucTester at a discountI have a brand new 300 DucTester system from Retrotec for sale at…See More
Wednesday
Scott Becnel joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Wednesday
Lucyna de Barbaro liked Home Energy Magazine's blog post AeroBarrier: The Silver Bullet to Zero Energy Affordability, by Paul Springer
Wednesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service