I am not an energy Rater .. I am an architect

I am curious if any "Home Energy Pros" make an effort to locate the Neutral Pressure Plane (NPP) of a house that is being blower door tested?

Views: 4856

Reply to This

Replies to This Discussion

Robert, LOL, simplicity is a must.  One thing I have learned in energy auditing is KISS.

Paul Morin gave me this version and John Brooks dug up John Straube's version at http://www.buildingscience.com/documents/digests/bsd-014-air-flow-c...

The "H" is whatever height you select and since we don't know from the start where the NPP is, just use the floor to ceiling.  What we want is the pressure per foot so we could actually use 1.  I just like to walk readers through just how simple stack effect really is and the many ways we can benefit from understanding it.

I will give your version a try as well.


And for another version.....

Here are a couple of Illustrations (in-progress) that I am adapting from John Klote's paper.


One example is for a single opening

the other example is for two openings

For estimating the height of the NPP ....

Temperature and Season don't make a big difference.

It is the Size and vertical distance between Significant openings that matter most.

The delta-T has a significant impact on the actual pressure difference inside to out (or from floor to ceiling), but not on the location of the NPP. 

Nice illustrations. But why would you open the doors and windows on a 35° day?    ;-)

fair enough...I would not suggest opening the windows when it's 35 outside

 ...the openings could also be not-so-big ventilation ports

here is a snipit from the Klote paper

the study is concerned with smoke movement ...but applies to general stack effect

Robert, where would you estimate the NPP to be in your Warren, VT house?

Are the silver rectangles in the attached photo your Air Inlets?

Are you running the exhaust fan 24/7 ?


Yes the rectangles just under the eaves are the Airlet 100 passive air inlets (there are seven all together, plus a 6" round inlet in the air-sealed laundry room for dryer makeup air and a 4" inlet in the first floor for direct-coupled woodstove combustion air).

There are also two bath exhaust fans (one on each floor) with the ducts dropping 3' before exiting the sidewalls to prevent cold air thermo-siphoning, and a kitchen range hood with a similar down-and-out anti-siphon duct. Both the dryer make up inlet and the woodstove combustion air inlet have similar cold air traps.

There are no upstairs ceiling penetrations other than masonry chimney and plumbing vent - both well air-sealed. The attic hatch is above the thermal/air envelope in the gable wall.

The house tested to 2.13 ACH50 (460 CFM50) with the air inlets taped. That shows an effective leakage area (@ 4 Pa) of 11 square inches, which increases to only 13 square inches when tested with the inlets open - so I don't think they contribute to much passive leakage when the exhaust fans are not running.

I had set the bath fans to run approximately one hour out of three to provide a little more than the ASHRAE 62.2 minimum, and flow tested them for actual CFM (94 CFM for the 110 fan and 74 CFM for the 80).

Since the downstairs has more mechanical openings (including the chimney cleanout door), I would guess that the NPP is somewhat below the first floor ceiling (particularly given 8' ceilings on the 1st floor and 7' ceilings on the 2nd) when no exhaust fans are running, and at the upstairs ceiling when one or more fans are running (baseline ΔP was 2.2 Pa, 4 Pa with one fan running and 8.6 Pa with both bath fans running).

With the static NPP likely below the downstairs air inlets, there's probably little or no flow between lower and upper passive inlets without either fan pressure or some wind pressure. I also installed a sweep on the door at the top of the stairs to pneumatically isolate the two floors.

Robert, thanks for all the detail

How did you calculate "effective leakage area" ?

(I found a ballpark formula of CFM-50 divided by18)

Why do you think "ELA" only increased 2 sq in (13-11)....

after you opened up 7 openings of approx 5 sq in (net free area) each?

CFM50/18 is a ballpark approximation of natural leakage (or more accurately normalized leakage), but the conversion factor (typically 20) depends on the climate zone, height of building, degree of shielding, and "leakiness factor" - as determined by LBNL studies http://www.homeenergy.org/show/article/id/1015.

The formula I use to determine ELA (in SF) is

ELA50 = CFM50/(2400 x √(50/248.88))

ELA4 = (CFM50/NL conversion factor)/(2400 x √(4/248.88))

[ELA @ 4 Pa is the standard]

or generically

ELA(sf) = CFM/(2400√(Pa/248.88))

Pa/248.88 = inches water column

The CFM50 went up from 460 to 570 with the Airlets open (24% increase), but when that is converted to ELA at a normalized 4 Pa, it amounts to an 18% increase.

I suspect that's because the combination of the foam dust filter and the mylar reed valve in the Airlet is sufficiently restrictive that it presents less net free area than a simple measurement would show.

With both bath fans running (168 CFM measured flow), I was getting between 6 and 8 CFM per Airlet for a total of about 50 CFM (which was very close to the 62.2 target of 47), which amounted to 30% of the exhaust flow. Including the laundry room inlet and chimney leakage, I measured about 80 CFM, or 47% of exhaust flow - with the remainder from envelope leakage.


Robert, you mentioned "cold air thermo-siphoning"

can you explain how this "works" ?

what is cold air thermo-siphoning?

and how does dropping the duct 3 feet prevent it?

why 3 feet ?

Air increases in density about 2% for every 10°F drop in temperature, so any duct with an outside termination at the same height or higher than the inside termination will allow the denser (winter) cold air to displace the warmer air and thermosiphon into the conditioned space (slowed, but not likely stopped by mechanical dampers, which sometimes get stuck open).

This is a potential problem when exhaust fans terminate through the roof, but even when they terminate at a wall on the same elevation as the fan. It's also a potential problem when inlet ducts come either straight in or in and down.

Indoor air at 70°/40%RH with outside air at 0°F/50%RH will produce a buoyancy (or downward cold air displacement pressure) of 0.0117 pcf. At the same conditions, a 3' chimney would create an upward stack effect pressure of 0.034 psf.

If you calculate actual duct air volume buoyancy vs duct stack effect pressure, they balance out at 3' of duct or "chimney" height.

Whoops! I've got to come up with another rationale for the 3' drop.

Air buoyancy and stack effect are the same thing, so they'll be the same regardless of "chimney" height. I was using two different formulas, with buoyancy based on wet air density and stack effect on dry air density, but the difference is not significant (moist air is actually less dense than dry air).

Any 3' "chimney at a 70° delta-T will create a 1.63 Pa stack pressure, which is the equivalent of the stagnation pressure of a 3.65 mph wind. But I don't know that tells us anything useful.

It's just an old rule of thumb that I learned many years ago and it makes sense to me, so I've used it for 20 years.

So, About a dozen "intentional openings" not including doors and windows

Let's say it is pretty darn cold outside (0 F)

What happens when one bathroom exhaust fan is activated?

and 94 CFM is pushed out of the house

doesn't 94 CFM also enter the house?

Is One exhaust fan powerful enough to raise the NPP all the way to the 2nd floor ceiling?

Can one bathroom exhaust fan make the entire house "negative" (WRTO)?


Latest Activity

Landon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase

WANTED: Blower door complete set Retrotec or Minneapolis

Hi all,I'm looking for a blower door system complete, ready to go. Preferably used, unless you have…See More
7 hours ago
Landon joined allen p tanner's group

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
7 hours ago
ABAA posted an event

ABAA 2018 Conference and TradeShow at Salt Palace Convention Center

May 8, 2018 to May 9, 2018
7th Annual Air Barrier Association of America’s conference and trade show.May 8-9, 2018 at the Salt…See More
8 hours ago
Michael R. Johnson liked Bruce Sullivan's blog post Solving Energy Poverty: Energy Efficient Homes for Those Who Need Them Most
9 hours ago
Home Energy Magazine posted a blog post
10 hours ago
Diane Chojnowski posted a discussion

ACEEE Fact Sheet: The Impact of Federal Energy Efficiency Programs

Federal energy efficiency programs have played a key role in reducing energy use and saving…See More
11 hours ago
Profile IconLandon, Lloyd Elam, Jeremiah Doty and 3 more joined Home Energy Pros Forum
11 hours ago
Khaliquzzaman Katchi liked Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge
11 hours ago
Mick Lane replied to Steve Eberly's discussion Infrared camera recommendations for general contractor use
"The real question is what are you going to do with the camera.  Does it need to take pictures…"
12 hours ago
Lloyd Elam commented on Home Energy Magazine's blog post How We Turned Our House into a Giant Foam Box, Part I — Wall Insulation By Wen Lee
"Can't wait to see what your blower door number will be...."
12 hours ago
Danny Gough replied to Jeremy Begley's discussion Manual S for Water Furnace Equipment in the group HVAC
"Well said David Butler. One more thing I would add is if you have some flexibility with the loop…"
14 hours ago
Leslie Jackson posted a blog post
20 hours ago
Steve Eberly posted a discussion

Infrared camera recommendations for general contractor use

Hi, I believe I have searched and found little recent discussion on recommendations for IR…See More
22 hours ago
Jeremiah Doty commented on Jeremiah Doty's blog post A list of 7 important questions to ask potential Contractor's BEFORE hiring them!
"To read more of our helpful Blog's visit us at https://www.jandmservices.us/blog/"
Jeremiah Doty posted a blog post

A list of 7 important questions to ask potential Contractor's BEFORE hiring them!

A list of 7 important questions to ask a Contractor Before Hiring Them.1) First and foremost when…See More
Todd Williams liked Diane Deyerler's event Energy OutWest Conference
Khaliquzzaman Katchi replied to Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I am prepared to pay $200 and I will pay the shipping to Canada."
Brad Cook replied to Brad Cook's discussion When is a fuel history confidential and why?
"Personally, I just don't see what is so personal about how much fuel your home uses, in…"
Barbara Smith liked Diane Chojnowski's video
Al Tibbs replied to Khaliquzzaman Katchi's discussion Retrotec DM-2 Pressure Gauge in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a DM2 Mark II in VERY GOOD to Excellent Condition. I will sell for $300."


  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service