Greetings.  This is my first post/question - many more to follow, I'm sure. 

I live in a rental house that has radiant floor heat and a heat recovery ventilator that pulls warm, moist air out of the baths, kitchen, and laundry room and blows outdoor air warmed through the heat exchanger into the living spaces of the house. 

The  fan started making a high pitched noise this week, so I called and they sent out a service guy (plumber).  The air exchange unit is located in the attic against a south facing wall.  The attic is not heated, but the attic is included within the building envelope (insulation against the roof). 

The plumber, after a bit of effort, pulled out the central core of the exchanger - it looks like a pentagon or hexagon prism with zig-zag filter around the perimeter (not the fan or fan motor).  It was frozen - obviously moisture had gotten in and then the cold make up air froze it.  It's been well under freezing here for several weeks.  The plumber said the ice was restricting the airflow causing the fan motor to work harder.

The plumber changed two small rectangular air filters where the ductwork enters the HRV, put everything back together, turned the fan on, and the sound was gone.  He said the system would be fine. After he left, I checked the air blowing into the house, and it felt like air conditioning - which I really don't need in the dead of winter.

My concern:  When the ice melts, and the water sits within the HRV, will I have a mold problem?

The system looks like it has a light to show that it is frosted up and might auto shut off, but obviously that didn't work. 

Thoughts?  Should I pull the ice core out and let it thaw and dry and reinsert it?  I can live without the air circulation for a couple of days.

Many thanks.

Views: 5305

Reply to This

Replies to This Discussion

It really becomes a what house, what occupancy, what climate question. I like ERVs, but it really depends. What do you want to do with latent heat, expell, keep out, or keep in? You might want both cores, switching between summer and winter.

I'm not sure it makes à huge difference unless the house is crazy tight. The issue is how yoh want/need to manage moisture.

RSS

Latest Activity

Jonathan Beers posted a discussion

MGE hiring for my job

I'm retiring next spring, and MGE is hiring:…See More
17 hours ago
Summer Reyes's blog post was featured

Equipment We Use: Detecting Water With Infrared Cameras

You know water is somewhere on the property, you can smell the mildew, but can't determine the…See More
19 hours ago
Profile IconGlenn Hourahan and Joseph Frasier joined Home Energy Pros Forum
19 hours ago
Alfredo Baccari added a discussion to the group Job Board
Thumbnail

HERS or/and BPI Energy Inspector in SF Bay Area (SAN JOSE, CA).

ELEM3NTS is a leading energy efficient consulting company specializing in residential homes. We…See More
20 hours ago
Alfredo Baccari joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
21 hours ago
David Byrnes's blog post was featured

Strategies for Hiring and Interviewing for Home Performance Professionals

Hire slow and fire fast.  It’s a phrase that experienced managers and human resources professionals…See More
23 hours ago
Dara Bowser replied to Don Fugler's discussion joining ducts in the group HVAC
"Good to hear you have clean dryer ducts Don. The dryer duct issues that we run into are…"
yesterday
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"David, If the IMC mandates metal dryer duct and prohibits metal screws, they must be accepting…"
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service