Got Data? How much leaking electricity is there in HVAC systems?

I poked around when shopping for fuel-firedboilers and couldn't find anything official.  Ran across estimates ranging from a few watts to 30 watts.  Anyone have data or pointers to data?  A lot of effort has been spent on understanding "leaking electricity" from appliances, but what about HVAC? Seems like a sleeper to me.

Views: 195

Reply to This

Replies to This Discussion

This is what I have from some of our Baseload auditing:
Compressor Crankcase Heater in AC: 40 W
Zone Dampers on Air Handler: 30 W
Thermostat transformer: 4W
And... of course the 't-stat fan setting set to "on" always' which can be:
Airhandler fans on 24/7 (@400-600W)
500W x 24 hours x 365 days x .001kW/W = 4,380 kWh/yr @$.16 = $701 per year
Tamasin:

You are really making every opportunity to hammer home that "fan on" issue :-).

Regarding the math, I usually skip a term by going straight to 8760 hr/yr...sounds much more impressive :-). Anything multiplied by that number is a bunch :-)

And $0.16/kWh !! I'm crying the blues at $0.14 in NV!

Can not be said too often!
Can't tell you anything about boilers, but I could look up measured data for my own ECM furnace if that helps. If memory serves it was on the order of 10 watts total. I believe Scott Pigg of the Energy Center of Wisconsin has data for furnaces, but probably not boilers - he might have published the furnace standby in his Home Energy Magazine article of Nov/Dec 2003.

You might try posting this question on "The Wall" at HeatingHelp.com. This is Dan Holohan's web site, and some experienced hydronic contractors often give prompt answers to questions.

Alan Meier sent me to the Australian Standby Power study linked here: http://standby.lbl.gov/docs.html several years ago, but I don't recall if boilers were measured. Great study because it measured a lot of hard-wired sleepers, as you called them.

If you find good data please publish it - inquiring geeks want to know!

Upstate NY is coming in at $.17/kWh

Steve Waclo said:

Tamasin:

You are really making every opportunity to hammer home that "fan on" issue :-).

Regarding the math, I usually skip a term by going straight to 8760 hr/yr...sounds much more impressive :-). Anything multiplied by that number is a bunch :-)

And $0.16/kWh !! I'm crying the blues at $0.14 in NV!

Can not be said too often!

Mark:

 

"Upstate NY is coming in at $.17/kWh"

Does the meter reader wear a Lone Range mask on his rounds :-)??

Spent the coldest winter ever in Corning back in 99-00 and noticed how the state seemed to load up utility bills with surcharges. Corning Glass was booming at the time, but pity folks who had to pay the heating costs when things declined there later.Understand CG is now coming back.

The only electrical stand by losses I believe would be from the control transformer. If there is no call for heat.



Steve Waclo said:

Mark:

 

"Upstate NY is coming in at $.17/kWh"

Does the meter reader wear a Lone Range mask on his rounds :-)??

Spent the coldest winter ever in Corning back in 99-00 and noticed how the state seemed to load up utility bills with surcharges. Corning Glass was booming at the time, but pity folks who had to pay the heating costs when things declined there later.Understand CG is now coming back.

 

They wear a mask, but it ain't Lone Ranger or Robin Hood!

Actually just about HALF of the electric cost (I'm in Central Hudson territory) is fees and transmission charges. You 'only' pay about $.08-.09/kWh for the electricity, the rest is delivery.

Just got some measurements from one boiler.

 

Heating mode: 936W

Circ pump and air handler: 396

Circ pump only: 216W

Cooldown (internal fan): 120W

All "off": 3.6W

If it's leaking, while it certainly does affect efficiency, wouldn't this nevertheless already have been calculated?

If not, then a 14 seer pump is not a 14 seer.

If I may chime in, the newer hydronic boilers, (Viessmann Vitodens 200 being one I have personally installed, but others as well), often do cause an unexpected electrical consumption jump -at least the first time you install one. In our case, the internal blower fan and internal circulator (an ECM based Grundfos just the same), drew over 130 Watts over our previous baseline. The heating efficiency was admirable and worth it, but we paid no mind to the electrical consumption until we got the bill. I installed a Kill-A-Watt meter at the power supply unit for a season and it recorded over 600 kWH for a ten month period. This does not include the secondary circulator for the heating loop. We average about 18 cents per kWH here in Boston, BTW.

These are net boiler numbers. Our first month was double this but we found the culprit: When the boiler fired it created the tell-tale condensing boiler plume. The plume in turn activated the IR/Motion Detector on our outdoor flood lights... live and learn.

Tamasin illustrates the much larger parasitic losses of moving air. All that mass of low specific heat vs. water, it is not an efficient delivery method. The Btu per Watt ratio is rather low.

RSS

Forum Discussions

Efficiency of furnace

Started by Jignesh in General Forum. Last reply by Jim Hensen 12 hours ago. 5 Replies

2005 EPAct tax credit

Started by Mandy Leazenby in General Forum. Last reply by Sean Lintow Sr on Thursday. 3 Replies

Best brands for furnace

Started by Jignesh in General Forum on Tuesday. 0 Replies

ROCIS recommendations for Ducted Range Hoods

Started by Diane Chojnowski in General Forum. Last reply by Tony Baptist on Tuesday. 8 Replies

Latest Activity

Todd Abercrombie liked Barbara Smith's video
9 hours ago
Jim Hensen replied to Jignesh's discussion Efficiency of furnace
"Great question - what the efficiency rating means is one of the most common questions we we asked.…"
12 hours ago
Michael Schettine's blog post was featured

Framing production combined with air sealing

Building Tighter Homes with Gasketed FramingIf you follow our blog, you know that we talk quite a…See More
yesterday
Profile IconMichael E and Jason Dion joined Home Energy Pros Forum
yesterday
Jason Dion joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
yesterday
Jason Dion joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
yesterday
Jason Dion joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Jason Dion joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
yesterday
Jason Dion joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
yesterday
Jason Dion joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
yesterday
Jason Dion joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
yesterday
Brad Cook replied to Jignesh's discussion Efficiency of furnace
"NO combustion based heating system can ever be 100% efficient, according to the Second Law of…"
Thursday
Brian Robinson commented on Barbara Smith's video
Thumbnail

How to get top performance from your furnace, air conditioner or heat pump

"So glad you highlighted the importance of air sealing & insulating the home form the bottom to…"
Thursday
Brian Robinson replied to Jignesh's discussion Efficiency of furnace
"You also may also want to account for the distribution losses as you move the heat from the…"
Thursday
Michael Schettine posted a blog post

Framing production combined with air sealing

Building Tighter Homes with Gasketed FramingIf you follow our blog, you know that we talk quite a…See More
Thursday
David Butler replied to Jignesh's discussion Efficiency of furnace
"Adding to Sean's comment... The reason a 90%+ furnace uses a PVC flue (as opposed to metal) is…"
Thursday
Barbara Smith's video was featured

How to get top performance from your furnace, air conditioner or heat pump

Video produced as part of our Minnesota heating and cooling system study. Seventhwave
Thursday
DesignTech posted photos
Thursday
Sean Lintow Sr replied to Mandy Leazenby's discussion 2005 EPAct tax credit
"And there we go, it got a retroactive extension till 12.31.2017 now"
Thursday
Barbara Smith commented on Barbara Smith's video
Thumbnail

Building a Green Veterans network

"Thanks Hannah!  I corrected the link. Please try again."
Wednesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service