Last week I was doing a rough-in w/air handler installed duct test.  I taped all the supply boots and installed the fan to the return grill just as always. When I set up the manometer, I noticed a pressure reading of 135Pa, this without the fan being turned on.  If I disconnected the hose from the manometer, pressure fell to zero.  Assuming I had done something to cause this I checked and rechecked everything, even installed fresh batteries.  Finally, I moved the hose to another supply boot, this resulted in a proper reading so I went ahead with the test.

Does anyone have any idea what was going on to give such a reading?  Let me know if you need more information.  Thanks for help solving this perplexing question.

Views: 373

Reply to This

Replies to This Discussion

Hard to see how there could be +135 in one supply duct without at least some positive reading everywhere else. Maybe someone accidentally (?) tied a bath fan into that duct.......

No power to the house at time of testing.

someone stepping on the hose?

No.

I would tend to agree with Glen, as a blocked tube will clock up rather fast.  If there is still a pin hole I suspect the pressure would stabilize at some point, although I'm not going to test it.  It could have been a kink somewhere that unfolded when you moved the hoses.  If it was a positive pressure the block was on the input.  If negative it would have been on the reference, DG700 at least.

Bud

I just submitted this to the Energy Conservatory.  If I get something useful back from them, I'll post it here.

As promised, I asked the folks at The Energy Conservatory about my funky duct test results.  Paul Morin, a Technical Sales Specialist suggested that such a situation could occur if the hose is stopped up or perhaps was up against insulation in the supply boot.  He went on to say; "You can simulate a pressure this high by putting your finger over an open tap on the DG-700 gauge.  It is harder to reproduce a pressure that high with a long length of hose attached, but you would see pressures that high if some debris is plugging the hose.  You also will see pressures that high if the hose is pinched, stepped on or if there is water in the hose."  

I believe that the end of the metal probe must have been up against the boot insulation, probably when I taped the hose  to secure it. The resulting restriction of air caused the errant reading.

Thanks to everyone who offered a suggestion.  

Something else to look out for.  If you use the metal probe to punch through the plastic tape you can actually punch a hole in the plastic tape which will cover the end of the probe.  I've had this happen to me and it caused some temporary confusion.

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler 7 hours ago. 2 Replies

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco 13 hours ago. 1 Reply

Fixing a water heater?

Started by John Shillito in Best Practices. Last reply by Eric Kjelshus on Friday. 21 Replies

Latest Activity

Profile IconAndrew McDowell, Randy Kinnison, Breanna Detwiler and 8 more joined Home Energy Pros Forum
4 hours ago
David Butler replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"theoretically, let's say you perfectly isolate the HPWH from a heat source. The HPWH's…"
6 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Interesting idea. Commercial roof on a slope! Typical density for roofing spray foam is 2.5 to 3.0…"
7 hours ago
Summer Redman added a discussion to the group Job Board
Thumbnail

Hiring 2 Training Specialists in Champaign-Urbana, Illinois

The Applied Research Institute (ARI) at the University of Illinois at Urbana-Champaign is seeking…See More
8 hours ago
Summer Redman joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
8 hours ago
Stacie Bagnasco replied to Evan Mills's discussion Dirty solar panels
"This is a great idea. I clicked on your discussion because it made me remember that I forgot to get…"
13 hours ago
Kirsten Richnavsky posted an event
Thumbnail

rCloud - The Future of Testing at Your Office or Home

October 18, 2017 from 2pm to 3pm
Integrating rCloud as an essential part of your RESNET QA process.Retrotec’s rCloud app is here,…See More
13 hours ago
Ed Whitaker replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"Brad,   I agree with the comments and would add a couple of thoughts. 1st,  any time you…"
14 hours ago

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service