What sort of leakage reduction could I expect if I try to plug all these tiny gaps?

This is a typical cathedral ceiling around these parts, 2x6 tongue and groove over 4x beams. In this image we're looking at a big valley rafter running diagonally in front, with a beam in the background at right. There are a couple of can lights and a couple of skylights in there too. This is after about 30 minutes with the door running and a 20 degree delta T. All of the beams have strips of trim, about 3/8" x 1", nailed on with brads. Lots of air comes out from behind that trim, where boards end. Relatively little comes out in the field, apparently because there's poly sheeting behind the 2x6.

It would be possible to pull each piece of trim with a flat bar, pull the nails, caulk behind it, drill a hole into each joint, inject more caulk in hopes of sealing the tongue/groove, and renail the trim. Some of this stuff is 16 feet in the air above the grand piano, really hard to get at. 

Ever done a test-in, test-out on leakage like this? Did you get big results? This house is well around 2 CFM50 per square foot, so it needs a major reduction.

Views: 197

Attachments:

Reply to This

Replies to This Discussion

I have sealed this before. IMO, it would be easier to run two beads of caulk on each side of trim rather than removing the trim piece. Unfortunately I didn't individually test the measure when I did the job, so I am not sure how much that contributed.

Hi David,

I've worked above expensive furnishings and either everything has to be moved or protected.  Drop that flat bar and no one is going to be happy.  Thus, I might consider the back door approach.  Do everything else and what is left is some base amount plus that ceiling.  If you can isolate that room in any way, some zone pressure readings might help identify how much is coming from where.  Again, even if you can't read that space, maybe you can read others.  Divide and conquer.

Bud

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler 3 hours ago. 34 Replies

Psychrometric Chart Training

Started by John Krochmalny in Training. Last reply by Mahendra Shah on Friday. 1 Reply

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco Oct 16. 1 Reply

Latest Activity

David Butler replied to David Butler's discussion How would you insulate this roof?
"Sean Lintow proposed rails and clips (re: first comment in this discussion), but in the context of…"
3 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"I missed where the suggestion for rails came in. The plywood would not need any rails. 4+ inches is…"
7 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"I'm a little confused about the necessity and purpose of using support rails if working on…"
8 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"If you insulate master bedroom and family room from below, you definitely need more R-value than…"
8 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Brad, I was only talking about using EPS between the ridges, if necessary, to conform to bolts.…"
8 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"It kind of depends on the PIC. Not all insulation is made the same. Here in VT (and all of New…"
8 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Filling those shallow valleys with rigid foam not only prevents primary foam panels from…"
9 hours ago
Brad Cook replied to David Butler's discussion How would you insulate this roof?
"Bill, you just posted a number of responses in different areas of the thread. I will try to respond…"
13 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service