Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 401

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Latest Activity

Lucyna de Barbaro liked David Eggleton's group 1000 Home Challenge
3 hours ago
Steven Lefler's photo was featured
4 hours ago
Brad Cook replied to Dav Camras's discussion Low Leakage home with cathedral ceiling
"It is all about the dewpoint. Think of the roof system as a big box. Air can circulate in, out and…"
6 hours ago
David Butler replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"@Dav, 240-volt circuits are dedicated to a single appliance so circuit monitoring with CT's…"
22 hours ago
Dav Camras replied to Dav Camras's discussion Experience with new energy monitoring tools such as Curb, Sense, Nerio and Smapee
"I have been thinking about putting it on my own home as you suggest, and was wondering which, if…"
22 hours ago
Profile IconGrady Harper, Christina Savage, gregory sutliff and 1 more joined Home Energy Pros Forum
23 hours ago
Doug Mullins added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door equipment for sale

I have 5 ea Retrotec 6000 blower door fans - $3500.00 ea1 3000 series fan with WiFi -…See More
yesterday
Jon Finewood joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service