Hi,

After installing a Cree CR6 insert, does the canister still needs to be boxed out to keep insulation from covering the fixture?

Thanks

Paul

Views: 576

Reply to This

Replies to This Discussion

Hi Paul.

Certainly an issue with all cans that could use a good answer.  Unfortunately, we are most often left to our own thinking for guidance.  Here are my thoughts.

If it is possible to re-install a bulb with a higher wattage, then the higher wattage rules must remain in place along with the wattage warning.  If the modification is basically permanent, (no Edison socket), then the new bulb potential wattage can be considered.  Remember, I'm not the authority, these are just thoughts and here is the last sentence on one of Cree's warranty statements:

"Any changes or modifications not expressly approved by the party responsible for compliance could void the user’s authority to operate the equipment."  This was from a PDF under Vantage Controls.com from this search: http://www.google.com/#q=Cree+CR6+insert&hl=en&prmd=imvns&a...

Exactly what that means I couldn't say, but there are two authorities I look to, local AHJ, and UL.  I didn't see any reference to UL, but if your packaging has such that would be good.  As for the local AHJ, they rule and should always be contacted when looking for approval not specifically granted elsewhere.

As for boxing any can light, it is often discussed, but I have never seen a universally approved approach that would be accepted by all authorities.  Lacking specific UL approval or someone else's signature on the dotted line to take the responsibility off of your shoulders, I would not box, but replace with a new AT/IC can.

Bud

i bought severa of the Cree CR6 bulbs and have put soem in my own home as substitute bulbs in AT/IC fixtures.  They have been in for at elast 5 years now.    before we put these in the fixtures had halogenbulbs in them.  we sprayed the fixtures with open cell foam from the attic when we first installed them in 1996.  so far no problems with the halogens or the LED's.  not scientific, but factual.

when i told my supplier this, he said Cree does not reccomend this, and will not warantee bulbs installed this way.   i have since been using TenMat domes on recessed lights, then spraying foam on the domes.  we had one failure where the fixture had an incondescent bulb with the adjustable 'eyeball' trim ring.  in that case airlfow is restricted by the trim ring and the bulbs overheated.  the fixtures shut off.  i replaced the incandescents with LED screw in bulbs and all is well. 

in my case, we are specifying creating an airspace in the attic around any recessed fixture, then using spray foam to seal the outer surface of that space. 

Hi Pat, although my post above kind of says not to box, I also compare boxing to installing a can in a first floor ceiling or in a drop area over a kitchen sink.  In those cases, the can is still enclosed, but in a cavity that provides more area to dissipate the heat.  Since I have seen no restrictions for cans in a joist cavity, I would assume a similar generous space with a box should be acceptable.  At least this is the argument I use when talking to local code officials, if one is ok why not the other.

Bud

Sorry about all the typo's.  not my forte`  check with TenMat on this, but those covers are made for this application.  they are made of rock wool, so they will not burn and are good protection for the foam.  they are also easily installed. 

 

 

Typo's are certainly not an issue in these days.

The key to any cover is having had UL test that specific light with that cover or possibly having UL approve that cover for any and all lights, which I don't think they would do.  One cover I looked at had a list of several cans they had tested it with and it was thus approved for those and only those cans.  In any event, I haven't heard of this being an issue, but would not want to be the last one in line when they were looking to blame someone.

Bud

RSS

Forum Discussions

Think of the house as a really big duct

Started by Frank Spevak in HVAC. Last reply by Franco Oyuela 17 hours ago. 1 Reply

What's the Most Profitable HVAC Job for Your Company?

Started by Wayne Melancon in HVAC. Last reply by Franco Oyuela 18 hours ago. 4 Replies

Mini split installation location

Started by Jan Green in HVAC. Last reply by David Butler yesterday. 1 Reply

Mini split air conditioners and ceiling fans

Started by Beverly Lerch in General Forum. Last reply by David Butler yesterday. 11 Replies

Latest Activity

John White replied to Jerry Needham's discussion Condensation on ceiling and walls of master bedroom
"Condensation on ceiling occurs when the attic space above is poorly ventilated or insulated. The…"
5 hours ago
Joshua P Murphy is now a member of Home Energy Pros Forum
15 hours ago
Franco Oyuela replied to Frank Spevak's discussion Think of the house as a really big duct
"THANKS for the information. Ducted mini splits offer hidden benefits."
17 hours ago
Franco Oyuela replied to Wayne Melancon's discussion What's the Most Profitable HVAC Job for Your Company?
"Get into commercial, it's more money!"
18 hours ago
David Byrnes's video was featured

Why One Room Is Hotter Than Others

Ever wonder if your air conditioner is working right because one room never gets a cool or warm as others? Do you need a bigger air conditioner to fix a room...
yesterday
Profile IconEric MacCallum, Adam Morgan and Caolan Hutchens joined Home Energy Pros Forum
yesterday
David Butler replied to Jan Green's discussion Mini split installation location
"Really hard to advise without knowing the layout. But you're asking good questions. Any chance…"
yesterday
Jan Green posted a discussion

Mini split installation location

Reaching out to the experts today to ask about location of installation of a mini split.  I'm a…See More
yesterday
David Butler replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Among the various opinions expressed here, I offer a few 'truths'... Ceiling fans are…"
yesterday
Walter Ahlgrim replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"This is one of thouse topic where you ask 10 people and get 12 different opinions. I will give you…"
yesterday
Brett Little's event was featured
Thumbnail

Full Circle Urban Forestry: Introducing Urban Wood Opportunities - Free CE Webinar at Webinar Online

October 17, 2018 from 12pm to 1:15pm
Many common urban tree removal practices in the United States view felled urban trees as costly…See More
yesterday
Beverly Lerch replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Now I am confused.  Everyone has a different opinion.  "
yesterday
Joseph Novella replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"Don't use the fans! They generate heat and mix the stratified high warm air with the low cool…"
yesterday
John White replied to Beverly Lerch's discussion Mini split air conditioners and ceiling fans
"If you are using air conditioning, a ceiling fan will allow you to raise the thermostat setting…"
Monday
John White posted a blog post
Monday
Profile IconDana Launius and Susan Dee Cummins joined Home Energy Pros Forum
Sunday
Linda Wigington liked Don Fugler's discussion Depressurization/make-up air issues
Sunday
Profile IconCourteney Hazard, Erin Kelly, Megan Bailey and 3 more joined Home Energy Pros Forum
Friday
Kent Browning replied to Julie Saporito's discussion Tankless water heating and existing gas lines
"First the problems - increased CO due to poor combustion, flue condensation delayed ignition, etc.…"
Friday
Brett Little posted an event
Thumbnail

Full Circle Urban Forestry: Introducing Urban Wood Opportunities - Free CE Webinar at Webinar Online

October 17, 2018 from 12pm to 1:15pm
Many common urban tree removal practices in the United States view felled urban trees as costly…See More
Friday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service