I'm opening a separate discussion under a new thread as this one: http://homeenergypros.lbl.gov/forum/topics/locating-the-neutral-pre...  was getting overly congested and this topic deserves its own space.

Homes need to be tight to be energy efficient, but then comes the question of how to provide the necessary fresh air that we and our houses need.  Robert Riversong (above thread and several others) has posted some great information on passive vents and the economics of simple exhaust venting that I think offers a good alternative to expensive H/ERV installations.  However, I feel there needs to be a better understanding of just how static venting works.

Most of us in the energy business have read about, used, or advised on using some form of passive venting for replacement air that involves a form of air trap.  Robert posted his version and mentioned the "Saskatoon Loop" as methods of restricting the unwanted air flow while still providing a path for the desired air flow.  I have looked at the "duct ending in a bucket" and the "loop up at the bottom" cold air traps in the past and concluded they are not exactly what they appear to be.  Essentially they modify the height and resistance of the flow path, but otherwise do not act as an air block.

 

Since the explanation of the above can be long, I have put together a simple statement that I feel conveys the guidance we need when designing and installing passive vents, at least some of the guidance.

"For any fresh air vent duct passing from inside a home to the outside (under natural pressures), the effective pressure from end to end of that duct is the stack effect pressure (wrto) at the height of:

1.  the outside opening when the duct is filled with inside temperature air.

2.  the inside opening when the duct is filled with outside temperature air.

3.  the penetration through the envelope when outside is filled with outside air and the inside is filled with inside air."

I haven't reviewed this for summer conditions, but I believe the statement will hold.

When any kind of winding path is filled with the same air as is around it, it might as well be a straight shot, if the structure allows.  Alternatively, if a straight shot is not possible, a winding path will not alter the effective air flow, other than adding a bit more resistance.

The bottom line is, passive venting should follow and use the internal pressures within a home, positive, negative, and that somewhat elusive NPP.

John is very good at challenging or explaining many of my statement and he creates great artwork, so I'll post this and see what we get for input from all.

Bud

Views: 10292

Reply to This

Replies to This Discussion

The coefficient is based on standard pressure, not temperature. And that formula is for delta-P inside to out, not absolute pressure.

The atmospheric pressure is the weight of the column of air on the earth's surface. That column remains the same mass whether it expands from heat or cools and contracts.

But the HVAC industry, uses standard pressure and temperature to determine air flow volume.

I think I found what I was looking for

Standard Temperature is zero degrees Celsius

Standard Pressure is pressure at sea level

Attached is a snip-it from Straube's textbook.

the formula does return Delta P if Delta H and Temperatures are known

it can also be used to solve for Delta H if Delta P and Temps are known

 

I used the formula to estimate the Delta Vertical  Isobar Spacing for Delta T

{Isobar = a line connecting points of equal atmospheric pressure}

Delta Isobar (Pa) Spacing ( Inches) = Delta T (Farenheit) x 0.0066

 

So...at sea level and 32 degrees F

Isobar Spacing  would be 3.14 inches

If the air in an example house is 68 F.. then Delta T = 36 F

Delta Isobar spacing = 36 x 0.0066 = 0.24 inches

Isobar spacing inside the house = 3.14 + 0.24 = 3.38 inches

The US Standard Atmosphere is based on a standard temperature of 59°F (the average air temperature at the earth's surface). http://en.wikipedia.org/wiki/U.S._Standard_Atmosphere

There are many other "standard" temperatures and pressures used by various organizations:

http://en.wikipedia.org/wiki/Standard_conditions_for_temperature_an...

Robert, I noticed that there are several "standards"

which standard (temperature) do you think Straube  is referring to?

The full SI formula for stack effect delta-P is:

ΔP =0.0342 x H x A x (1/TO - 1/TI), with A = atmospheric pressure

To get Straube's conversion factor of 3465, he's multiplying 0.0342 times 101,325, so he's using that as the standard atmospheric pressure.

NIST seems to use 68°F as the standard for gas flow. But you'll have to ask Straube which is the "new normal" for him.

RSS

Forum Discussions

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler yesterday. 15 Replies

Psychrometric Chart Training

Started by John Krochmalny in Training. Last reply by Mahendra Shah yesterday. 1 Reply

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco on Monday. 1 Reply

Latest Activity

tedkidd replied to Bob Blanchette's discussion Tankless Water Heaters... has their time finally come?
"Yeah. Gas water…"
19 hours ago
Eric Kjelshus replied to Bob Blanchette's discussion Tankless Water Heaters... has their time finally come?
"With super cheap natural gas prices now, still worth going all electric?  Tankless needs a lot…"
20 hours ago
Stuart Langley liked Chris Clay's photo
yesterday
David Butler replied to David Butler's discussion How would you insulate this roof?
"Stuart, I wasn't considering the copula windows... yes, those would indeed need to be…"
yesterday
Stuart Langley replied to David Butler's discussion How would you insulate this roof?
"Well, @David Butler, you have seen the property more accurately than I have, but my impression of…"
yesterday
David Butler replied to David Butler's discussion How would you insulate this roof?
"@ Stuart,I don't think there's any concern about impact of 4" build-up on elevation…"
yesterday
Stuart Langley replied to David Butler's discussion How would you insulate this roof?
"So this building has a few issues with air leaks and air leaks have so much to do with discomfort…"
yesterday
Stuart Langley replied to David Butler's discussion How would you insulate this roof?
"John Hatfield has the right idea here for a new roof deck. Polyiso boards always need a good stout…"
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service