Posted on wrong thing first time.  Have cust who claims to have condensation on ceiling in summer time.  has 2 ac... has approx 3,000 sf two story built 1978 mst br is only room with cathedral ceiling.  said the condensation started after they installed ridge vent.  says ceilings are 2 by 6.  i am thinking of removing the dry wall and spray foaming the ceiling and replacing the drywall causing an unvented ceiling.

any thoughts.

Jerry Needham

Views: 451

Reply to This

Replies to This Discussion

Is it the cathedral ceiling that's sweating? Is the condensation on or adjacent to supply vents?

David

Not sure if there are any supply vents in the ceiling.  I am scheduled for an energy audit on June 18th and will know a lot more about the house at that point.  Just trying to get ahead of the curve prior to getting to the house.

Spray closed cell foam and get rid of soffit venting.

Problem fixed! Adding soffit vents just allowed hot moist air to hit, I assume, an underinsulated and non air sealed space. Doubt they actually vented the space with baffels all the way up the cavity to a vented ridge cap. Is there a vented ridge cap?  As the cool air got passed the drywall it just condensed on the nearest surface.

Bet there is a tone of mold on the back side of that drywall. Proceed with caution. Good luck!

Thanks for the reply Daniel.  I have worked with several jobs where we did as you suggest and all seem to be good.  I like the concept of the un-vented foam filled cathedral ceiling.  Cust says no issues with the condensation prior to adding the ridge vent. I know that the moisture hitting the warm ceiling in the summer goes against my training.  I am still going to look at the possibility of too much AC capacity with 2 AC in a 2,600 sf house.  One on first floor and one on second floor.  Lots of un-answered questions at this time.

The problem was probably there before, it just wasn't as apparent - sure rain isn't getting in through said ridge also? Love hot roof systems especially when you have so little room for traditional means - just make sure it is closed cell & I would also test out with a blower door to make sure they got it sealed / installed properly

Sounds like u opened the hornets nest! I would say a 2600 sq ft home shouldn't need more than 2tons a/c depending where u are at. More tonnage can cause issues. Especially makes it difficult for the system to pull moisture out of the air of it is short cycling. I would suggest a duct test to see how leaky the system is. Highly recommend if any ducts are in unconditioned space. Areoseal might be a good option if the leakage is high. I don't really like the stuff but it is a great option

Looks like a leaking ridge vent

Condensation on ceiling occurs when the attic space above is poorly ventilated or insulated. The traps heat in the attic, which then warns the ceiling. When the cool air from your living space rises due to humidity in your home then it comes in contact to the warm surface of the ceiling and condensation forms. To fix this condensation issue in ceiling by following these of the three below mentioned tips

  • First, you have to do attic ventilation

  • Then after you should do attic insulation

  • And last you should fix or try to reduce humidity in living spaces.

If you are looking for the professional Heating, Ventilation & Cooling (HVAC) experts then you could contact us at White Mechanical, Inc.

Jerry,

;Have you opened the cathedral ceiling?  

Try using ceiling fan to move / mix air temps / gradients

RSS

Forum Discussions

Indoor Air Quality Monitors and Meters

Started by Rob Madden in General Forum. Last reply by Al Tibbs 17 hours ago. 13 Replies

70 unit building rehab

Started by Jerry Needham in Multifamily. Last reply by Sean Lintow Sr on Saturday. 2 Replies

Linda Wigington Leadership Award Nominations

Started by Diane Chojnowski in General Forum. Last reply by Diane Chojnowski on Friday. 1 Reply

Latest Activity

Laurie DiDonato posted an event

RESNET HERS Rater Hybrid Training (Classroom Section in NH) at Online/ Classroom Component in Manchester, NH

April 29, 2019 at 9am to May 24, 2019 at 5pm
Online Component: NEW- On-Demand Training Modules (with Live Office Hours) Office Hours: April…See More
13 hours ago
Emily Ambrose posted a blog post

City Pages: What They Are & How to Use Them Right

Recently, we have been talking a lot about…See More
17 hours ago
Al Tibbs replied to Rob Madden's discussion Indoor Air Quality Monitors and Meters
"I would take a look at Gray Wolf products. They are the best I have used. I have tried most over…"
17 hours ago
Tommie John added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door and Duct Blaster!

Hey everyone, I have some great items for sale a Minneapolis blower door with dg-700. I also have a…See More
18 hours ago
Tommie John joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
18 hours ago
Kelly Caplenas posted a blog post

Technology and Customer Service

I read this line in a Forbes article … "Time and technology wait for no one, and customer loyalty…See More
19 hours ago
Diane Chojnowski posted a discussion

EERE Request for Information Concerning Efficient & Flexible Building Loads

The DOE Building Technologies Office has issued a Request for Information to solicit feedback from…See More
19 hours ago

© 2019   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service