Does anyone have an inexpensive method to "clock" a combustion furnace to estimate BTU output similar to Natural gas, but for propane, kerosene, or oil? I work in the Weatherization Assistance Program and often the nameplates are missing from existing furnaces. Without BTU output it is tough to do an accurate computer model of the home. Thanks!

Views: 499

Reply to This

Replies to This Discussion

For natural gas, run only the furnace for a given time, mark the dial difference on the meter and multiply the gas used by the heat multiplier for your gas supplier. This will give you a ball park estimate.

For propane, you can look at the burner orfice size.  there are charts that give the btu rating for the orfice size. then multiply by the numbers of burners.  will give approx output.  LP orfices are usually slightly smaller btu than Nat. ones.

Follow the link

http://www.joppaglass.com/burner/lowp_chrt.html

Thanks for all the comments plus the link. I think based on them I have enough information forfollks in the field to get close enough to the correct size furnaces for modeling the houses thanks all.

Ernst,

You mentioned oil, but the replies seem to all be for gas, unless I didn't read correctly.  For oil you can look for the nozzle size.  Sometimes it is notes on the service tag or in the manual, if still around.  In some cases you might be able to call the service company as they may have that noted for their HDD fuel calculations or service work. 

Bud

Thanks, I did find that out. In weatherization we deal with some really old furnaces, so sometimes getting a ballpark furnace size is the best we can do but the nozzle sizes for oil seem to be pretty specific.

For the oil burning furnaces, you should check the pump pressure. Older furnaces run at 100psi, and newer ones run at 140psi. When the pressure is higher, you need to cross reference the nozzle size to get proper Btu ratings. Plenty of reference materials are located on the Beckett website.

For propane figure about 20-25k per burner rated input. Varies some form unit to unit but 22k is typical.

Thanks Bob, we'll go woithout. It should be close enough without having to factor in pressures and temps, etc and  complicate the process too much.

I'll apologies in advance for drifting here a bit, but your "close enough" comment threw me back to my beginning in this business (05) when I questioned every number we use.  The idea of pinning down the performance of a home to the last tiny detail is laughable when we consider just how many of our inputs are "close enough" numbers.  From insulation values, HDD, window performance, and air leakage (to name a few), we guess and we guess and then carry our calculations out to two decimal places (or the computer does).  I think my tape measure is the only real source of accurate information :).

I enjoyed the comment

Bud

RSS

Forum Discussions

Psychrometric Chart Training

Started by John Krochmalny in Training 2 hours ago. 0 Replies

Too many Heat Pump Water Heaters in a basement?

Started by Brad Cook in General Forum. Last reply by Michael Duclos 7 hours ago. 10 Replies

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler on Monday. 2 Replies

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco on Monday. 1 Reply

Latest Activity

John Krochmalny posted a discussion

Psychrometric Chart Training

Looking through the various areas of this site, I didn't see too much information or training on…See More
2 hours ago
Profile IconMike Malek, Avery T. Phillips and Sarah Burger joined Home Energy Pros Forum
3 hours ago
Dannie Jackson's blog post was featured

Core Heat And Other Concepts

  In some places the use of solar heated liquids from hot water solar panels are used to provide…See More
7 hours ago
Michael Duclos replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"I’ve been looking into Sanden for a multi-family PH near Laconia, NH, ASHRAE 99.6% temp is…"
7 hours ago
Profile IconTroy Spindler, Mike Berg, Andrew McDowell and 4 more joined Home Energy Pros Forum
yesterday
David Butler replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"theoretically, let's say you perfectly isolate the HPWH from a heat source. The HPWH's…"
yesterday
David Butler replied to David Butler's discussion How would you insulate this roof?
"Interesting idea. Commercial roof on a slope! Typical density for roofing spray foam is 2.5 to 3.0…"
Monday
Summer Redman added a discussion to the group Job Board
Thumbnail

Hiring 2 Training Specialists in Champaign-Urbana, Illinois

The Applied Research Institute (ARI) at the University of Illinois at Urbana-Champaign is seeking…See More
Monday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service