Does anyone have an inexpensive method to "clock" a combustion furnace to estimate BTU output similar to Natural gas, but for propane, kerosene, or oil? I work in the Weatherization Assistance Program and often the nameplates are missing from existing furnaces. Without BTU output it is tough to do an accurate computer model of the home. Thanks!

Views: 501

Reply to This

Replies to This Discussion

For natural gas, run only the furnace for a given time, mark the dial difference on the meter and multiply the gas used by the heat multiplier for your gas supplier. This will give you a ball park estimate.

For propane, you can look at the burner orfice size.  there are charts that give the btu rating for the orfice size. then multiply by the numbers of burners.  will give approx output.  LP orfices are usually slightly smaller btu than Nat. ones.

Follow the link

http://www.joppaglass.com/burner/lowp_chrt.html

Thanks for all the comments plus the link. I think based on them I have enough information forfollks in the field to get close enough to the correct size furnaces for modeling the houses thanks all.

Ernst,

You mentioned oil, but the replies seem to all be for gas, unless I didn't read correctly.  For oil you can look for the nozzle size.  Sometimes it is notes on the service tag or in the manual, if still around.  In some cases you might be able to call the service company as they may have that noted for their HDD fuel calculations or service work. 

Bud

Thanks, I did find that out. In weatherization we deal with some really old furnaces, so sometimes getting a ballpark furnace size is the best we can do but the nozzle sizes for oil seem to be pretty specific.

For the oil burning furnaces, you should check the pump pressure. Older furnaces run at 100psi, and newer ones run at 140psi. When the pressure is higher, you need to cross reference the nozzle size to get proper Btu ratings. Plenty of reference materials are located on the Beckett website.

For propane figure about 20-25k per burner rated input. Varies some form unit to unit but 22k is typical.

Thanks Bob, we'll go woithout. It should be close enough without having to factor in pressures and temps, etc and  complicate the process too much.

I'll apologies in advance for drifting here a bit, but your "close enough" comment threw me back to my beginning in this business (05) when I questioned every number we use.  The idea of pinning down the performance of a home to the last tiny detail is laughable when we consider just how many of our inputs are "close enough" numbers.  From insulation values, HDD, window performance, and air leakage (to name a few), we guess and we guess and then carry our calculations out to two decimal places (or the computer does).  I think my tape measure is the only real source of accurate information :).

I enjoyed the comment

Bud

RSS

Latest Activity

Dara Bowser replied to Don Fugler's discussion joining ducts in the group HVAC
"Good to hear you have clean dryer ducts Don. The dryer duct issues that we run into are…"
5 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"David, If the IMC mandates metal dryer duct and prohibits metal screws, they must be accepting…"
7 hours ago
David Butler replied to Don Fugler's discussion joining ducts in the group HVAC
"I never checked that before. Checking now... Section M1502.4.2 of the International Residential…"
7 hours ago
Joseph Frasier is now a member of Home Energy Pros Forum
7 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"Brendan, Thanks for that response. Because of your warning, I just went down to the basement and…"
11 hours ago
Brendan Reid replied to Don Fugler's discussion joining ducts in the group HVAC
"Hi Don, Summary: DRYER VENT: screws bad idea, possibly prohibited by code. METAL DUCT: must be…"
11 hours ago
Profile IconBrendan Reid and David Butler joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
11 hours ago
Profile IconSean Wiens and David Butler joined Chris Laumer-Giddens's group
Thumbnail

Energy Efficient Design

Energy efficiency starts at the drafting table...How architects and designers can help buildings…See More
20 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service