I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 3975

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Latest Activity

Stuart Langley liked David Byrnes's blog post Strategies for Hiring and Interviewing for Home Performance Professionals
3 hours ago
Kevin Miller replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Visual inspection can only confirm the presence of mold, not the absence.   That said,…"
6 hours ago
Armand C Magnelli replied to Don Fugler's discussion joining ducts in the group HVAC
"I often suggest pop-rivets as an alternative to sheet metal screws for both clothes dryer duct work…"
7 hours ago
Kevin Miller replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Sampling would be primarily to verify 'Condition 1' or 'Normal Fungal Ecology'…"
7 hours ago
Daniel Cullen joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
7 hours ago
Daniel Cullen replied to Bob Krell's discussion What Do You Do When You Find Suspected Mold? in the group Healthy Indoors (IAQ)
"Can anyone tell me exactly HOW mold sampling impacts the mold remediation process or protocol? Why…"
7 hours ago
Daniel Cullen joined Bob Krell's group
Thumbnail

Healthy Indoors (IAQ)

The Healthy Indoors group is focused on indoor air quality (IAQ), mold, moisture control, radon,…See More
7 hours ago
Debra Little's video was featured

Robert Bean, Iain Walker, indoor environmental quality experts

Robert and Iain discuss home indoor health & environmental quality. Design for human factors; thermal comfort, air quality, sound, odor...kitchen exhaust, th...
8 hours ago

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service