I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 3974

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Forum Discussions

What made this chimney fall down?

Started by Eric Kjelshus in General Forum. Last reply by Eric Kjelshus on Tuesday. 7 Replies

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by Dave Taylor Nov 11. 61 Replies

Manual J (SD) for custom, luxury homes

Started by Dav Camras in HVAC. Last reply by Dav Camras Nov 10. 3 Replies

Quantitative methods for residential zoning

Started by Brett in HVAC. Last reply by David Butler Nov 9. 1 Reply

Home Energy Pros and #MeToo

Started by Mike Rogers in General Forum. Last reply by Mike Rogers Nov 9. 3 Replies

Latest Activity

Don Fugler added a discussion to the group HVAC
Thumbnail

joining ducts

A question came up on exhaust duct connections. I have always considered screws necessary for…See More
34 minutes ago
Don Fugler joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
42 minutes ago
Profile IconSonny Roncancio and Chester Energy & Policy joined Home Energy Pros Forum
21 hours ago
Ryan Moore updated an event
Thumbnail

LEED for Homes Green Rater Training at Fort Collins, CO

December 7, 2017 to December 8, 2017
Green Insight will host this 2-day training in Fort Collins, CO December 7-8,…See More
yesterday
Rodney Bailey liked Rodney Bailey's discussion Energy audit equipment for sale.
yesterday
tedkidd liked Mike Rogers's blog post Focusing on payback to motivate customers?
Thursday
Home Energy Magazine's blog post was featured
Wednesday
Home Energy Magazine posted a blog post
Wednesday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service