I've encountered an install of 6" duct directly connected to the outside through the rim joist and covered by a simple mess screen on the end.  The other end has been placed next to the gas furnace as make-up air.  The cold air just pours in whether the furnace is active or not.  There is a clear need for make-up air as the CAZ is very small and the DHW and furnace are next within a couple of feet of each other.  Any advice on a simple mechanical option to better regulate this situation.  (The DHW is natural draft and the furnace is power-assist.  They are commonly vented.)   

Views: 370

Reply to This

Replies to This Discussion

Let it be known common venting of power draft and natural draft appliances is against code in many jurisdictions. Are the DWH and Furnace in conditioned or unconditioned space?

The units are in a conditioned laundry area, 16'X11'X7.5'  The DHW is 36K btu & furnace 45K btu. (Dryer is electric.)

Hi Jerry, your classic can of worms.

Each of us must decide where we will draw the line, that line where we can be blamed for making conditions worse and this is one.  Any improvements on air sealing could affect that CAZ, therefore, IMO, I advise the problems need to be fixed FIRST, before I will continue with an audit.  I usually catch these with a pre-audit visit, but that's my routine.

Here is some of what you face and I'm not a pro on HVAC as Maine prohibits auditors from doing anything beyond the specified CAZ test. 

1.  Venting as Bob mentioned needs to meet code.

2.  Replacement air also needs to meet code, such as vent area, high and low vents, and outside clearance.  A 6" duct is way too small.

3.  Any mechanical solutions need to be approved for that use, no shoe strings and cloths pins.

A common recommendation is a cold air trap with a bucket or a 180° turn in the incoming duct.  The short explanation is, they don't do as advertised and neither would bring the venting up to code.

Most burner units, and you have two, have combustion air kits that can draw air directly from the outside.  There are also powered dampers which open and close as needed and prevent the burner from coming on if they fail.  Whether either of these could be used to solve the problem and meet the codes would need to be determined.

Again, this is my opinion and perhaps others will chime in with some code requirements, beyond my scope.

Bud

Picture of uncontrolled make-up air duct next to furnace.

 

Attachments:

Glad they used insulated duct for the fresh air intake ;)

Have you considered sectioning off the water heater and furnace from the rest of the laundry area? Make the that unconditioned space. How about a vent between the laundry area and the rest of the house effectively increasing the size of the laundry room and eliminating the need for make up air?

Be sure to check local codes before making a final choice. As Bud said this may be a HVAC contractors issue, although I probably wouldn't call the one that stuck in the 6" flex for fresh air...

RSS

Forum Discussions

Too many Heat Pump Water Heaters in a basement?

Started by Brad Cook in General Forum. Last reply by David Butler 16 hours ago. 9 Replies

How would you insulate this roof?

Started by David Butler in General Forum. Last reply by David Butler 17 hours ago. 2 Replies

Dirty solar panels

Started by Evan Mills in General Forum. Last reply by Stacie Bagnasco 23 hours ago. 1 Reply

Fixing a water heater?

Started by John Shillito in Best Practices. Last reply by Eric Kjelshus on Friday. 21 Replies

Latest Activity

Profile IconAndrew McDowell, Randy Kinnison, Breanna Detwiler and 8 more joined Home Energy Pros Forum
14 hours ago
David Butler replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"theoretically, let's say you perfectly isolate the HPWH from a heat source. The HPWH's…"
16 hours ago
David Butler replied to David Butler's discussion How would you insulate this roof?
"Interesting idea. Commercial roof on a slope! Typical density for roofing spray foam is 2.5 to 3.0…"
17 hours ago
Summer Redman added a discussion to the group Job Board
Thumbnail

Hiring 2 Training Specialists in Champaign-Urbana, Illinois

The Applied Research Institute (ARI) at the University of Illinois at Urbana-Champaign is seeking…See More
18 hours ago
Summer Redman joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
18 hours ago
Stacie Bagnasco replied to Evan Mills's discussion Dirty solar panels
"This is a great idea. I clicked on your discussion because it made me remember that I forgot to get…"
23 hours ago
Kirsten Richnavsky posted an event
Thumbnail

rCloud - The Future of Testing at Your Office or Home

October 18, 2017 from 2pm to 3pm
Integrating rCloud as an essential part of your RESNET QA process.Retrotec’s rCloud app is here,…See More
23 hours ago
Ed Whitaker replied to Brad Cook's discussion Too many Heat Pump Water Heaters in a basement?
"Brad,   I agree with the comments and would add a couple of thoughts. 1st,  any time you…"
yesterday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)  

Badges  |  Report an Issue  |  Terms of Service