I recently measured disappointing bath fan flows at a project - both being below our program minimum of 50cfm. The builder had the installer come back to have a look and found nothing obvious but he did get a couple of new fan motors and swapped them out and also double checked that the damper flap wasn't stuck. There was a slight improvement to both but it was not enough, still both below 50.

These fans were routed - with a short run of duct - to soffit terminations which allowed us to look up inside and check for blockages but none were seen. 

Then the weirdness: I checked the flow coming from the terminations and both were about 90cfm, yet still only about 45 inside. How can this be? I've never seen this before, but that's because I never test at the outside. 

I hate to bash brands but these were Broan fans which I rarely see used around here. Most all of my contractors use Panasonics.

Views: 239

Reply to This

Replies to This Discussion

In my opinion venting into any soffit is a bad idea, it usually requires a sharp bend to get into the soffit, and reduces insulation value where it crosses the top plate. (significantly)  Better going through the sidewall or box/gable, nice straight run with an extra damper thrown in that doesn't put back pressure on vent pipe.  Additionally the hood damper seals much tighter (typically) then the inline damper that is provided with fan.

In my northeast climate (zone 5 & 6) adding damp air to roof edge in 0deg weather is asking for icing issues.

Never had issues getting fans up to needed CFM when running through wall.  Usually issue is related to air envelope tightness where the fan struggles due to lack of fresh air intake.  This can be detected by opening the bathroom window (or any window) while testing to see if it affects flow rate. (I've seen that it does)

RSS

Forum Discussions

Indoor Air Quality Monitors and Meters

Started by Rob Madden in General Forum. Last reply by Al Tibbs 2 hours ago. 13 Replies

70 unit building rehab

Started by Jerry Needham in Multifamily. Last reply by Sean Lintow Sr on Saturday. 2 Replies

Linda Wigington Leadership Award Nominations

Started by Diane Chojnowski in General Forum. Last reply by Diane Chojnowski on Friday. 1 Reply

Latest Activity

Emily Ambrose posted a blog post

City Pages: What They Are & How to Use Them Right

Recently, we have been talking a lot about…See More
2 hours ago
Al Tibbs replied to Rob Madden's discussion Indoor Air Quality Monitors and Meters
"I would take a look at Gray Wolf products. They are the best I have used. I have tried most over…"
2 hours ago
Tommie John added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door and Duct Blaster!

Hey everyone, I have some great items for sale a Minneapolis blower door with dg-700. I also have a…See More
2 hours ago
Tommie John joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
3 hours ago
Kelly Caplenas posted a blog post

Technology and Customer Service

I read this line in a Forbes article … "Time and technology wait for no one, and customer loyalty…See More
4 hours ago
Diane Chojnowski posted a discussion

EERE Request for Information Concerning Efficient & Flexible Building Loads

The DOE Building Technologies Office has issued a Request for Information to solicit feedback from…See More
4 hours ago
Profile IconSteve Nations, MKR, Kathy Rubel and 2 more joined Home Energy Pros Forum
19 hours ago

© 2019   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service