We are seeing this more and more... 9" of insulation flush on the bottom of a 12" or 14" floor joist cavity.  No contact with conditioned floor, enclosed and ventilated crawlspace.  They typically have 3" to 5" air gap above the insulation.  From underside it appears to be grade 2 and possibly grade 1!   Does any one know how poor these really perform?

Views: 740

Reply to This

Replies to This Discussion

Hi Kent,

Cutting corners is a practice many have perfected.  But that air gap above the insulation may not be all that bad.  Emphasis on "may", as there are other details that need to be done correctly.  Joseph Lstiburek did a good article on this, attached below.

What's your climate zone and what does enclosed means if it is also ventilated.  Is the crawl floor covered and sealed?  If it truly needs to be a vented crawl space that floor above needs to be covered from below with an air barrier.  What else is in the crawlspace?

http://www.buildingscience.com/documents/insights/bsi-064-bobby-dar...

Bud

Thanks for the feedback Bud! 

We are in Climate zone 4 - marine & radon zone 1. It's a foundation wall with venting 1/150.  Crawl is covered with 6 mil visqene with good overlaps & sealed.   Insulation is open to crawl with no rigid on the bottom side.  These homes do get frequent 10- 20 mph winds.  2-3 weeks of freezing and 2-3 weeks of high temperatures - moderate temperatures otherwise.

Lstiburek's article implies there isn't too much loss unless exposed to wind and big temperature swings. 

First, to clarify, we are discussing a short basement, ie a crawlspace??  Your reference to 1/150 for venting I would normally apply to attics.  Not sure that number is applicable to a below the house crawlspace, minimal stack effect and limited high/low locations for vents.

In a humid climate I probably would not vent a crawlspace.  Seal it up and insulate the foundation walls and make it part of the conditioned space.  This avoids summer humid air entering and finding a cold surface to condense on.  But, if they go with a vented crawlspace, then the crawl ceiling needs more than exposed fiberglass.  If the house is air conditioned, that same humid air will end up condensing on the bottom of the floor, right through the insulation.  Exactly what needs to go there is debatable.

But your original question is about how effective the insulation is in this configuration.  Joe covers it in his paper, the limited air flow.  In a warm over cold configuration, convection is naturally suppressed.  Depending upon the location of those vents and the amount of air flow the loss of r-value will be limited.  But, there are better ways of insulating these locations.

And, as for the radon, they should at least have a passive system installed ready to be upgraded to active if needed.

Bud

Thanks Bud.  Yes these are short foundation walls and access under is usually an issue.  Unvented & enclosed crawlspaces have been tried here (Pacific Northwest) with conflicting results and the consensus is to stick with vented crawlspaces.  The passive radon system is required and also ready to be made active if deemed necessary.

I appreciate Lstiburek's article and it makes some sense but I'd like to hear from actual results.  The beer reflection gives me hesitation, as that has often resulted in breaking out in handcuffs.  Logic and alcohol are not good mixes!

I think if it were my house I'd have the insulators get the insulation in contact with the subfloor...basically -  just fill the cavity.

Haven't seen anyone in this area do the rigid foam on the underside yet- probably too moderate of a climate to make it cost effective.

One of the distinctions Joe makes about the gap above (which I agree with) is a "warmer floor".  Floors are hard to heat because of the natural stratification above.  Leaving the gap allows for some heat loss into that space and a slightly warmer floor.  But, that cavity should be as sealed as possible.  For simplicity and for less overall heat loss, filling the cavity might be best, especially since you are not in an extremely cold climate.  I'm just sure how to evaluate the moisture flow.

As for Joe's humor, that is his writing style, his experience is extensive.  As for some having tried the sealed and unvented approach, I would suspect they did not condition the resulting space below, a must.  If fully conditioned, it would be no different from a conditioned basement. 

Best,

Bud

RSS

Latest Activity

John Redmond added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Flir I7 Infrared Camera (Barely Used)

I have been away from this site for a while, so my apologies if this is supposed to be posted…See More
21 minutes ago
John Redmond joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
24 minutes ago
Hannah Wood liked Quinn Korzeniecki's discussion Application Period for 2018 Energy Auditor (EA) and Quality Control Inspector (QCI) Pilots Now Open
2 hours ago
Quinn Korzeniecki posted a discussion

Application Period for 2018 Energy Auditor (EA) and Quality Control Inspector (QCI) Pilots Now Open

We need you!Applications are now being accepted to participate in the 2018 Energy Auditor (EA) and…See More
2 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Application Period for 2018 Energy Auditor (EA) and Quality Control Inspector (QCI) Pilots Now Open

We need you!Applications are now being accepted to participate in the 2018 Energy Auditor (EA) and…See More
2 hours ago
David Butler replied to Chris Bellanca's discussion Overheating garage
"Easy... insulate the attic ceiling. I'm not sure how much good it would do to air seal a…"
2 hours ago
Chris Bellanca posted a discussion

Overheating garage

Hi all, I'm looking for potential solutions to a problem at a client's house.  The south facing 2…See More
4 hours ago
Landon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Brand new retrotec blower door system $3000

Hi, I’ve got a brand new blower door system from retrotec that I got 2 months ago, and never got…See More
4 hours ago
John Redmond posted discussions
5 hours ago
David Holtzclaw replied to David Holtzclaw's discussion GSHP for domestic hot water
"Thanks John & Bill. Bill your experience is one reason why I wanted a larger heat pump with…"
7 hours ago
John White posted photos
17 hours ago
Diane Chojnowski posted events
yesterday
Rob commented on Bob Krell's group Healthy Indoors (IAQ)
"Hello, Has anyone tried custom filtering of window AC units? Specifically concerned with…"
yesterday
Michael Dunseith's 2 photos were featured
yesterday
Franco Oyuela commented on Perry Ning's blog post Warnings About Portable Air Conditioners
"Here are the top five benefits of owning a portable air conditioner: 1. Low Price – All…"
yesterday
Daniel Baur-McGuire commented on Kurt Shafer's status
"Whole house fans are a scam if you use air conditioning. Seriously "
yesterday
Daniel Baur-McGuire commented on Michael Dunseith's photo
Thumbnail

NYC DEPT OF BUILDINGS TR8 ENVELOPE TESTING

"Looks fun. How did you connect all the fans together or did you adjust the flows manually? The…"
yesterday
Daniel Baur-McGuire replied to Bob Reuther's discussion log home roof insulation
"I would look to stop air from penetrating the ceiling. I would guess hot air is able to rise…"
yesterday
Jay Lillien posted a blog post

How Changing Temps Affect Your Home’s Windows

In Colorado, there’s a time-honored saying:“If you don’t like the weather, just wait a few minutes……See More
Tuesday
Matt Peiris replied to H.O. Electric's discussion Stop Drinking Bottled Water! in the group News & Announcements
"Cities like Los Angeles now use chlorine AND chloramine to treat their water. While chlorine can be…"
Tuesday

Photos

  • Add Photos
  • View All

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service