On a recent Quality Assurance site visit, I found a gas-fired water heater with a "Vent-rite Spill Alarm" installed on the flue. The contractor noted that worst-case spillage and draft failed in this home both on the test-in and test-out. I had heard of folks using these alarms, but had yet to see one installed until now. 

Ideally, the contrator would've been able to correct the venting situation and get the unit to pass its CAZ tests. The homeowner was reluctant to put in a new tankless water heater since the unit is less than 2 years old. So, it looks like the contractor fell back on the combination of a Carbon Monoxide alarm and Spillage alarm to monitor the situation until the homeowner is ready to install a direct vented water heater.

I am putting this out on the forums to find out what experiences people have had with these detectors? One concern the homeowner raised was regarding battery life - i.e. if its battery dies how will she know if it is working. A bigger concern from my perspective is whether they can be relied upon to accurately detect spillage over the lifespan of the water heater (in this case that could be 10 years). Any resources or experiences people have with these devices would be very much appreciated.

Tags: backdraft, gas-fired, heater, spillage, water

Views: 892

Reply to This

Replies to This Discussion

Sorry, no experience with the spillage alarms. Though from product description found elsewhere it should have a test/reset button so homeowner can check that it is still functioning. 

I once had a client who had installed a draft inducer fan on the vent pipe that was wired to operate when burner was on.  It seemed to work OK as an interim measure. BTW, I cannot see the chimney end of the vent pipe in your posted photo, but sounds like you saying that the venting cannot be raised to get the elbow off of the draft hood. Correct?

Does not appear to have Code Compliant pitch on that Venting, does it?

RSS

Latest Activity

Brett Little posted a discussion

Deer Haven Tour: Architect's residence goes LEED zero energy ready with warm modernism design

Join Evan behind the scenes for a tour of his personal residence that he designed to LEED (pending…See More
1 hour ago
Brett Little replied to Brett Little's discussion Do ductless systems do better on the HERS?
"Sounds fair but will anyone see it? Maybe this can get promoted?  In our webinar about ducted…"
1 hour ago
Energy Circle's event was featured
Thumbnail

FREE WEBINAR - The Contractors Blueprint: Boosting Market Share for a New or Existing Service - Critical Steps for Reaching your Audience at Crowdcast

November 14, 2018 from 5pm to 6pm
This training is specifically for HVAC, Home Performance, Solar or Insulation contractors that are…See More
2 hours ago
Diane Chojnowski added a discussion to the group News & Announcements
Thumbnail

Home Depot Rebates for Members

ATTENTION CONTRACTORS:  We are pleased to announce that HPC has worked with our partners, …See More
3 hours ago
Mark Buhler is now a member of Home Energy Pros Forum
3 hours ago
Harry Silver posted a discussion

Electricity demand response to changing electricity prices

Hello,I've been looking at electricity demand response to changing electricity prices within a…See More
12 hours ago
Robin Henry replied to Robin Henry's discussion Starting Business And I Need Auditing Equipment in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Thank you Mark but I have assembled most of the large purchases I need at this point. For anybody…"
yesterday
David Butler replied to Brett Little's discussion Do ductless systems do better on the HERS?
"Hi Brett, since the archive discussion you linked is locked to new posts, I think the best way to…"
yesterday

© 2018   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service