On a recent Quality Assurance site visit, I found a gas-fired water heater with a "Vent-rite Spill Alarm" installed on the flue. The contractor noted that worst-case spillage and draft failed in this home both on the test-in and test-out. I had heard of folks using these alarms, but had yet to see one installed until now. 

Ideally, the contrator would've been able to correct the venting situation and get the unit to pass its CAZ tests. The homeowner was reluctant to put in a new tankless water heater since the unit is less than 2 years old. So, it looks like the contractor fell back on the combination of a Carbon Monoxide alarm and Spillage alarm to monitor the situation until the homeowner is ready to install a direct vented water heater.

I am putting this out on the forums to find out what experiences people have had with these detectors? One concern the homeowner raised was regarding battery life - i.e. if its battery dies how will she know if it is working. A bigger concern from my perspective is whether they can be relied upon to accurately detect spillage over the lifespan of the water heater (in this case that could be 10 years). Any resources or experiences people have with these devices would be very much appreciated.

Tags: backdraft, gas-fired, heater, spillage, water

Views: 828

Reply to This

Replies to This Discussion

Sorry, no experience with the spillage alarms. Though from product description found elsewhere it should have a test/reset button so homeowner can check that it is still functioning. 

I once had a client who had installed a draft inducer fan on the vent pipe that was wired to operate when burner was on.  It seemed to work OK as an interim measure. BTW, I cannot see the chimney end of the vent pipe in your posted photo, but sounds like you saying that the venting cannot be raised to get the elbow off of the draft hood. Correct?

Does not appear to have Code Compliant pitch on that Venting, does it?

RSS

Latest Activity

Jonathan Beers posted a discussion

MGE hiring for my job

I'm retiring next spring, and MGE is hiring:…See More
15 hours ago
Summer Reyes's blog post was featured

Equipment We Use: Detecting Water With Infrared Cameras

You know water is somewhere on the property, you can smell the mildew, but can't determine the…See More
17 hours ago
Profile IconGlenn Hourahan and Joseph Frasier joined Home Energy Pros Forum
17 hours ago
Alfredo Baccari added a discussion to the group Job Board
Thumbnail

HERS or/and BPI Energy Inspector in SF Bay Area (SAN JOSE, CA).

ELEM3NTS is a leading energy efficient consulting company specializing in residential homes. We…See More
18 hours ago
Alfredo Baccari joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
19 hours ago
David Byrnes's blog post was featured

Strategies for Hiring and Interviewing for Home Performance Professionals

Hire slow and fire fast.  It’s a phrase that experienced managers and human resources professionals…See More
21 hours ago
Dara Bowser replied to Don Fugler's discussion joining ducts in the group HVAC
"Good to hear you have clean dryer ducts Don. The dryer duct issues that we run into are…"
yesterday
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"David, If the IMC mandates metal dryer duct and prohibits metal screws, they must be accepting…"
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service