We are looking at getting a portable AC unit. Is it possible to vent the heated exhaust air into a fireplace that will exit up and out the chimney. Or would I have to run the 5" flexible exhaust vent up and out the top of the chimney? The chimney is about 20' in length so was wondering if it would be a stretch for the exhaust pump to move air that distance. But seeing how hot air likes to rise, that might be a benefit. Thanks in advance.

Views: 343

Reply to This

Replies to This Discussion

just not much air flow.  5" pipe at .1 in water  is just 40 CFM  If bring it up to a inch water still just 1/3 ton at most.   Most AC unit in free air 2 ton system are in the 8,000 CFM range at very little SP .01 or less and still 15' spit.    I took a small 1/10 hp 240 volt motor out and put 24 inch pipe up 10 feet so to get hot air out of a closed in area, put back a one HP  to over come the SP.  ITs been working with out a compressor change for 8 years before 6 weeks till the compressor burned out with high heat. Heat kills.   Can you bump up the pipe size or out the side? to lower the drag?  

What is the portable AC unit model information?What kind of fireplace is it?

RSS

Latest Activity

Dara Bowser replied to Don Fugler's discussion joining ducts in the group HVAC
"Good to hear you have clean dryer ducts Don. The dryer duct issues that we run into are…"
14 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"David, If the IMC mandates metal dryer duct and prohibits metal screws, they must be accepting…"
15 hours ago
David Butler replied to Don Fugler's discussion joining ducts in the group HVAC
"I never checked that before. Checking now... Section M1502.4.2 of the International Residential…"
15 hours ago
Joseph Frasier is now a member of Home Energy Pros Forum
15 hours ago
Don Fugler replied to Don Fugler's discussion joining ducts in the group HVAC
"Brendan, Thanks for that response. Because of your warning, I just went down to the basement and…"
19 hours ago
Brendan Reid replied to Don Fugler's discussion joining ducts in the group HVAC
"Hi Don, Summary: DRYER VENT: screws bad idea, possibly prohibited by code. METAL DUCT: must be…"
20 hours ago
Profile IconBrendan Reid and David Butler joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
20 hours ago
Profile IconSean Wiens and David Butler joined Chris Laumer-Giddens's group
Thumbnail

Energy Efficient Design

Energy efficiency starts at the drafting table...How architects and designers can help buildings…See More
yesterday

Photos

  • Add Photos
  • View All

© 2017   Created by Home Performance Coalition (HPC)   Powered by

Badges  |  Report an Issue  |  Terms of Service